Default Amerage question

I have seen several different answers and got different answer from each of the licensed electricians I know. Here is the situation.

Pool sub panel is a 90 amp Cutler Hammer breaker wired with 4 AWG aluminum wiring. The type of wire is THHN2. Now from what I could get from it is that this wire is MAX rated for 75 amps of power. I know the higher temperature rated wiring can facilitate more power. But doesn't the connection point also have to be properly rated.

So is this wire good enough for a 90 amp sub panel fed from the main panel and were can this be found specifically.

Thanks in advance.
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 10/29/09, 8:55 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Amerage question

What is the protection ahead of the wire?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 10/29/09, 9:01 PM
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 573
Default Re: Amerage question

sorry don't understand the question....coming from a 200 amp cutler hammer main breaker box..
Reply With Quote
  #4  
Old 10/29/09, 9:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Amerage question

Was the wire to the sub protected at the 200 A panel?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 10/29/09, 9:04 PM
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 573
Default Re: Amerage question

yes, it was
Reply With Quote
  #6  
Old 10/29/09, 9:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Amerage question

Quote:
Originally Posted by rhensel View Post
yes, it was
By what size breaker or fuse?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #7  
Old 10/29/09, 9:07 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ampacity question

Your answer is in Table 310.16. Even using the 90 degree column #4 AL is only good for 75 amps max. Using lower rated columns would reduce this rating.

You are correct that the terminations would also affect the ampacity. AFAIK I have not seen a 90 degree termination.

Ambient temperatures and number of conductors in the raceway would also have an impact.
Reply With Quote
  #8  
Old 10/29/09, 9:11 PM
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 573
Default Re: Amerage question

It was a 90 amp breaker coming from a Cutlet Hammer 200 amp distribution panel that went about 70 feet to a cutlet hammer pool equipment sub panel...
Reply With Quote
  #9  
Old 10/29/09, 9:12 PM
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 573
Default Re: Amerage question

4/O aluminum wiring was the main incoming wires...
Reply With Quote
  #10  
Old 10/29/09, 9:16 PM
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 573
Default Re: Amerage question

Thanks Mr. Port...everywhere I looked I was right, but then a master electrician said I was wrong. This was at a re-inspection and I did not just take his "its OK' for granted. I appreciate your response and help and this is the exact reason why INACHI ROCKS!
Reply With Quote
  #11  
Old 10/29/09, 9:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Amerage question

I was on the phone but I see Mr. Port helped out.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #12  
Old 11/4/09, 5:01 PM
George P. Wells's Avatar
George P. Wells George P. Wells is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 366
Send a message via Skype™ to gwells
Default Re: Amerage question

Did the electrician explain why he believed the installation to be acceptable? 75A may not be a standard breaker size for that manufacturer. If a 90A breaker is the closest standard size, then generally it would be acceptable to protect the circuit at the next standard breaker size.

Another possibility is that building codes usually allow for variances from the code when calculations are made under the supervision of an engineer. In a situation where you a single motor load on a circuit, the manufacturer of the motor may have made calculations and published installation requirements that do not necessarily meet any local, regional or national code but the local inspectors will allow the installation based on the manufacturers specs.

As an electrical contractor, I had a few occasions where I installed equipment based on manufacturers recommendations. The local inspector would sometimes disallow the installations based on the building codes until I provided copies of the manufacturers installation specs.

Quote:
Originally Posted by rhensel View Post
Thanks Mr. Port...everywhere I looked I was right, but then a master electrician said I was wrong. This was at a re-inspection and I did not just take his "its OK' for granted.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing 4 11/26/08 2:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 8:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing 4 3/21/07 12:56 AM


All times are GMT -4. The time now is 8:04 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts