Default AMP (Tyco) Copalum connectors

Hey folks,

Has anyone seen these connectors used on aluminum wired homes? I have been asked to inspect a home with known aluminum wiring (split level) and the most cost effective solution would be to use these connectors. Any feedback as to costs, effectiveness, problems? Any input would be greatly appreciated.

Thanks,

Steven
Reply With Quote
  #2  
Old 5/3/06, 10:25 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: AMP (Tyco) Copalum connectors

You will need to have what they call, COPALUM , connectors.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #3  
Old 5/3/06, 10:26 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: AMP (Tyco) Copalum connectors

I defer these types of Inspections to an Electrician.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 5/3/06, 10:32 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: AMP (Tyco) Copalum connectors

Quote:
Originally Posted by jhagarty
I defer these types of Inspections to an Electrician.
I do the same.
Reply With Quote
  #5  
Old 5/3/06, 10:38 PM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

I refer as well, but was hoping that one of the electricians that usually post could give me their opinion on this type repair. I realize that replacement is the best alternative but do the COPALUM crimp connectors work well, or does the installation cause other problems? Just wanted some input from someone who has installed these connectors.



Steven
Reply With Quote
  #6  
Old 5/3/06, 10:43 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: AMP (Tyco) Copalum connectors

Best website I have ever seen on aluminum wiring and the use of Copalum crimps. Enjoy and share.

http://www.inspect-ny.com/aluminum.htm

Here's another one with "pictures"
http://www.alwirerepair.com/copalum_crimp_method.htm

Last edited by dedwards; 5/3/06 at 10:48 PM..
Reply With Quote
  #7  
Old 5/3/06, 10:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: AMP (Tyco) Copalum connectors

It must be done properly, therefore it should be defered to verify the integrity of the installation.

Quote:
The COPALUM crimp connector, which has been available for more than 20 years, is the only system recognized by CPSC that provides a complete and permanent repair and reduces the fire hazard in aluminum wire circuits. The COPALUM connector system attaches a copper wire to the old aluminum wires and is then crimped together with a power tool, achieving a "cold weld" between the conductors. The "cold weld" creates a permanent bond that eliminates electrical arcing or glowing connections and creates a safer electrical connection at outlets, switches, lights, circuit breakers, and panelboard terminals. The COPALUM connector repair materials and power crimping tools are only available to electricians who receive training from the manufacturer, to ensure that repairs are properly made.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 5/3/06, 11:12 PM
Steven Brewster Steven Brewster is offline
New User
 
Join Date: Aug 2005
Location: Southside, AL
Posts: 57
Please Note: Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

Thanks guys.
Reply With Quote
  #9  
Old 5/3/06, 11:34 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

I am in the minority opinion here but I think if you don't have symptoms and you don't screw with it, aluminum wire is not that big a problem. I back that up with the lack of scare stories on the news today. I think all the sloppy aluminum jobs that were doomed to fail have already failed and the others will be OK.
The fact is, if the electrican did a good job and the homeowner didn't screw with it, most of the millions of aluminum wired houses never had a problem.
Has Inspect-NY come up with any "new" stories? That article is older than some of our readers here.
Reply With Quote
  #10  
Old 5/4/06, 12:16 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: AMP (Tyco) Copalum connectors

You're the "expert" here Greg. Your opinion matters, not only to us, but the public as well.

As generalists, we are obligated (or if you prefer - "compelled") to defer these situations to the experts. When you offer this opinion to our client, you relieve us of the potential liability.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 5/4/06, 12:28 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: AMP (Tyco) Copalum connectors

Quote:
Originally Posted by jpope
You're the "expert" here Greg. Your opinion matters, not only to us, but the public as well.

As generalists, we are obligated (or if you prefer - "compelled") to defer these situations to the experts. When you offer this opinion to our client, you relieve us of the potential liability.
Compelled......I like that...

Since you have a Zinsco electrical panel with single strand aluminum branch circuit wiring "I'm Compelled" to refer this installation to a licensed electrician, blah, blah.

It is compelling Jeff......
Reply With Quote
  #12  
Old 5/4/06, 12:37 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: AMP (Tyco) Copalum connectors

Greg,
I have to agree with you. I routinely inspect homes here on the Gulf Coast of FL that are older homes that may have been had updated electrical systems more than once. I can honestly say that I have yet to find a home with aluminum wiring that has had any signs of arcing or overheating. Many of them have aluminum systems well over 30 years old and my standard response to the client is that the home has been here without incident for ____ years but also tell them what they should look for in the way of symptoms of problems. The biggest problem we run up on is insurance companies, realtors and as you said the horror stories that have been circulating for years. Many insurance companies will not take on a customer if they find out the home has aluminum wiring. I have known of several realtors that will not list a home if they find out it has aluminum wiring. Unfortunately it is hard to put the toothpaste back into the tube once the public has come to believe something. Equally difficult is when you have electricians who do not agree on the issues of AL wiring. Some will say the whole sytem should be pulled and replaced while there are others like yourself who use a more common sense approach and look at the evidence rather than the hype. Thanks for your input.
Reply With Quote
  #13  
Old 5/4/06, 12:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: AMP (Tyco) Copalum connectors

Quote:
Originally Posted by dedwards
my standard response to the client is that the home has been here without incident for ____ years. . .
I would caution HI's against using this type of statement.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 5/4/06, 3:44 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

The CPSC provided the following information as early as 1974. Use this for your reports.

May Is National Electrical Safety Month: Good News for Homeowners - Aluminum Wiring Fix ...

CPSC Invites Offerors For Aluminum Wire System Safety Standard

CPSC Safety Recommendations For Aluminum Wiring In Homes
CPSC Sets Aluminum Wire Hearings - Explore Potential Fire Hazards

"Repairing Aluminum Wiring"
Reply With Quote
  #15  
Old 5/4/06, 12:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

Like I said, most of these reports are older than a lot of our posters.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hook 2 appliance connectors together? jfunderburk Inspecting HVAC Systems 6 9/8/07 4:24 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Aluminum Connectors bsmith Electrical Inspections 9 5/9/06 12:01 PM
Crimp connectors at breakers syared Electrical Inspections 55 2/27/06 12:28 PM


All times are GMT -4. The time now is 8:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts