Default Re: AMP (Tyco) Copalum connectors

I am talking to my friend the Realtor about the AL wire I have just noticed in the panel. He is telling me it is not a big deal so on and so forth. I explain that it is not my place to tell the client AL wires are not a big deal that I always recommend the services of an electrician when I find single strand AL wires.

I start to explain my findings to the buyer, as I tell her about the AL wires she explains that her sister died in a house fire caused by faulty wiring (she did not say what type of wires and I did not ask) and she did not think she wanted a house with AL wires. Not my job to sell her, no upside.
Reply With Quote
  #17  
Old 5/4/06, 7:42 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

How about the connectors (look like pigtail or blue twist on type) that you can buy at home depot for AL repair.
Why are they selling these if copalum should only be the fix?
Are these meant to be temporary?
Reply With Quote
  #18  
Old 5/4/06, 7:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: AMP (Tyco) Copalum connectors

You can purchase these at Home Depot as well. . .
Attached Thumbnails
amp-tyco-copalum-connectors-hpim6465.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #19  
Old 5/4/06, 7:57 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: AMP (Tyco) Copalum connectors




They sell these @ home depot too, doesn't mean you are a steam fitter.
Reply With Quote
  #20  
Old 5/4/06, 9:47 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: AMP (Tyco) Copalum connectors

Quote:
Originally Posted by jlybolt
How about the connectors (look like pigtail or blue twist on type) that you can buy at home depot for AL repair.
Why are they selling these if copalum should only be the fix?
Are these meant to be temporary?
James, there is a page on Alumium wiring on the new online electrical course, including a really pretty picture of one of those repair wire nuts.

Try it here

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #21  
Old 5/5/06, 12:58 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

Bob has a nice picture of a Rigid Metal Conduit with the side blown out. That doesn't mean rigid threaded pipe sucks as a wiring method. I agree 100% that the 13<sumpin> alloy wire was real easy to screw up when you installed it but if you did it right (and Harry Home Depot didn't screw with it) it is still working.
The new 88xx alloys and the new devices are probably as safe as copper but 88xx is too hard to bend for most electricians. Up one size and stiffer that copper at the same size) All that aside, f copper gets much higher I bet you start seeing Alcan on TV telling you it is fine. (I saw the road show)
Guys over at Bob's house are talking about ~$90 rolls of 12-2 Romex ... at the contractor price. That is why you had 197x "aluminum" houses.
Reply With Quote
  #22  
Old 5/5/06, 1:09 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: AMP (Tyco) Copalum connectors

Quote:
Originally Posted by Greg Fretwell
Bob has a nice picture of a Rigid Metal Conduit with the side blown out. That doesn't mean rigid threaded pipe sucks as a wiring method. I agree 100% that the 13<sumpin> alloy wire was real easy to screw up when you installed it but if you did it right (and Harry Home Depot didn't screw with it) it is still working.
.
That is the problem as I see it here in Phoenix. The homes I see AL wire in have been added on to, partially re wired and Harry Home Depot'd to death. I call out needs evaluation by an electrician.
Heck Sparky's need to eat too.
Reply With Quote
  #23  
Old 5/5/06, 2:03 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AMP (Tyco) Copalum connectors

If you see "Harry" poking around in aluminum wire, I agree 100% you should have it evaluated but I wouldn't really go too crazy if this is a clean, stock installation, showing no signs of trouble.
It is also worth reporting to your client, simply because of the perceived loss in value.
I wish saner heads could come together on some sensible recomendations on aluminum. Like I said in response to Joe. These stories are all 30 years old. Where are the fires today and why did they happen?
Homeowners should be aware but they shouldn't be shivvering in fear.
Reply With Quote
  #24  
Old 5/5/06, 8:50 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thumbs up Re: AMP (Tyco) Copalum connectors

Thanks Garry, appreciate the link. It was what I was looking for.
Reply With Quote
  #25  
Old 5/5/06, 9:05 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: AMP (Tyco) Copalum connectors

I agree in that while single aluminum SHOULD always be listed in the report and recommend it be evaluated by a local electrical contractor....it is important to be tactful in how you explain things to potential buyers...

Many people are hurt each day i am sure from falling down steps....things happen and their are known issues with Aluminum single strand wire...but you need to allow the electrical contractor to inform the buyer of this fact in more detail other than you just letting them know this.

Yes, I believe the home owner or potential buyer should be made aware of it not only for safety but because some insurance companies will not insure a home in this wiring method....seen it many times....

But I believe it should not be stated like a ticking time bomb in your repsonse to the buyer, simply state the facts, that it is present and that it should be evaluated because where the largest problems could happen the HI wont see it.....so if you notice it in the panel, and it looks fine and no signs of issues...still refer it because you can't see at the plugs....an electrician will more than likely do a sampling of the plugs and make other suggestions...

Take the liability off yourself....defer in this situation but again don't fear the people into SHOCK.....be tactful....now if you say..NO..NO...I MUST explain to them " THEY ARE GONNA DIE " you better be able to back it up with more than 30 year old potentials...



Paul W. Abernathy
Reply With Quote
  #26  
Old 5/5/06, 9:18 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: AMP (Tyco) Copalum connectors

Very well put. That is the kind of approach we use to inform and educate the customer. Often if they are present they see the AL wiring and start to panic, then the Realtor has to put their two cents in. As I stated earlier, present the facts calmly and try to bring some reality into the presentation. One of the most often things I hear is the customer saying "their father, or their uncle" told them if it had AL wiring it was going to burn down while they were all asleep in their beds. We do recommend having the system looked over and signed off on by a licensed Electrician if for no other reason than often the house is already going to require a 4 Point inspection and that is just one step closer to getting one. We always tell them to "get it in writing too" This is a good thread and I am glad the Electricians have had their input on it. Thanks.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hook 2 appliance connectors together? jfunderburk Inspecting HVAC Systems 6 9/8/07 3:24 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Aluminum Connectors bsmith Electrical Inspections 9 5/9/06 11:01 AM
Crimp connectors at breakers syared Electrical Inspections 55 2/27/06 11:28 AM


All times are GMT -4. The time now is 5:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts