The 1st and 3rd photos are two 75 amp breakers with a handle connecting them. The 2nd pic is the panel.
I called it 75 amp, because 75A + 75A = 75A The appraiser told my client it's 150A. The letter from the electrician says it's a double 75A. (Still 75A right?) Last edited by jrichards; 2/26/08 at 8:32 AM.. |
|
#2
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hard to tell from your pictures. Is that third pic the service panel or a distribution panel. That box almost looks like a split system.
|
|
#3
|
||||
|
||||
|
Looks like 75 amps.
The configuration almost kinda looks like a split panel, though I saw no indication of a convenience/lighting section. Just a single double-pole breaker marked as 75A. And that's it, I suppose |
|
#4
|
||||
|
||||
|
I think you would be correct, Rule is that you call the lowest value. The main breaker is going to pop at 75 amps. Both breakers are 75 amps, and tied together.
|
|
#5
|
||||
|
||||
|
Looks like 2/0 copper at the top entrance cable. (200AMPS service) and the 75AMP breakers (labeled main) limit the lower panel to its rated max.
Must be a small house and or has gas/ fuel major appliances. Peter Doane Realty Check Inspection Service NACHI ID# 05120681
Last edited by pdoane; 2/26/08 at 12:44 PM.. |
|
#6
|
||||
|
||||
|
Peter,
I do not believe this is a split panel. If so, there would usually be a visible tie in from the lower breaker (usually bundled in a grouping of 4 2-pole at the top) and the lower section of the panel. Based on the physical configuration, I dont see room for 4 breakers at all. There are the main lugs, with bus bard and the 75 amp unit immediately beluw that area. Also, the 75 amp breaker is clearly marked as "main disconnect". You typically will never see it marked as such if there is a possibility of adding breakers at the upper section. |
|
#7
|
|||
|
|||
|
Please Note:
jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Thanks to all. I wanted to make sure I wasn't losing my last marble. |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's a 150A panel. Those 75's are wired in parallel like some Siemens and GE panels do with 200's. They use two 100's in parallel.
See how the short feeders from the main lugs are run in parallel. VERY odd setup for sure. 150A. |
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
What's a "double 75A" ???? Try again Sparky. ps- I added the quotes. |
|
#10
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is one of very old QO series breaker box and that box is 150 amp main rating let me expain a little on this one.
you see non standard arrangement on the handle because this is a paralleded connectioned breaker so it is rated at 75 amp per lug so muti by 2 result is 150 amp. you should able see the catalog #'s on the side of panel it will tell ya what size it is. Merci, Marc BTW this is not a split buss breaker box at all |
|
#11
|
||||
|
||||
|
Quote:
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#12
|
||||
|
||||
|
Okay
I learned something valuable today. Thanks, Guys! |
|
#13
|
|||
|
|||
|
Please Note:
jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
|||
|
|||
|
Please Note:
jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's one weird panel, for sure. Only the second one I've ever seen like that. I think they were called QOA1, if I'm not mistaken. A relic.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |