Default What amperage is this panel

The 1st and 3rd photos are two 75 amp breakers with a handle connecting them. The 2nd pic is the panel.

I called it 75 amp, because 75A + 75A = 75A
The appraiser told my client it's 150A.
The letter from the electrician says it's a double 75A. (Still 75A right?)
Attached Thumbnails
amperage-panel-close-up-main.jpg   amperage-panel-panel.jpg   amperage-panel-main-breaker.jpg  

Last edited by jrichards; 2/26/08 at 8:32 AM..
Reply With Quote
  #2  
Old 2/26/08, 7:55 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

Hard to tell from your pictures. Is that third pic the service panel or a distribution panel. That box almost looks like a split system.
Reply With Quote
  #3  
Old 2/26/08, 9:21 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: What amperage is this panel

Looks like 75 amps.

The configuration almost kinda looks like a split panel, though I saw no indication of a convenience/lighting section. Just a single double-pole breaker marked as 75A. And that's it, I suppose
Reply With Quote
  #4  
Old 2/26/08, 9:42 AM
Kenton J. Schaff's Avatar
Kenton J. Schaff Kenton J. Schaff is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Loveland, CO
Posts: 66
Default Re: What amperage is this panel

I think you would be correct, Rule is that you call the lowest value. The main breaker is going to pop at 75 amps. Both breakers are 75 amps, and tied together.
Reply With Quote
  #5  
Old 2/26/08, 12:41 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: What amperage is this panel

Looks like 2/0 copper at the top entrance cable. (200AMPS service) and the 75AMP breakers (labeled main) limit the lower panel to its rated max.

Must be a small house and or has gas/ fuel major appliances.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681

Last edited by pdoane; 2/26/08 at 12:44 PM..
Reply With Quote
  #6  
Old 2/26/08, 1:20 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: What amperage is this panel

Peter,

I do not believe this is a split panel. If so, there would usually be a visible tie in from the lower breaker (usually bundled in a grouping of 4 2-pole at the top) and the lower section of the panel. Based on the physical configuration, I dont see room for 4 breakers at all. There are the main lugs, with bus bard and the 75 amp unit immediately beluw that area.

Also, the 75 amp breaker is clearly marked as "main disconnect". You typically will never see it marked as such if there is a possibility of adding breakers at the upper section.
Reply With Quote
  #7  
Old 2/26/08, 2:34 PM
jrichards jrichards is offline
Active Poster
 
Join Date: Feb 2006
Location: Jacksonville, FL
Posts: 213
Please Note: jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

Quote:
Originally Posted by pdoane
Looks like 2/0 copper at the top entrance cable. (200AMPS service) and the 75AMP breakers (labeled main) limit the lower panel to its rated max.

Must be a small house and or has gas/ fuel major appliances.
You are so observant. It was originally a smaller home with natural gas. Now there is an addition and the natural gas service has been terminated.

Thanks to all. I wanted to make sure I wasn't losing my last marble.
Reply With Quote
  #8  
Old 2/26/08, 4:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

That's a 150A panel. Those 75's are wired in parallel like some Siemens and GE panels do with 200's. They use two 100's in parallel.
See how the short feeders from the main lugs are run in parallel.
VERY odd setup for sure.

150A.
Reply With Quote
  #9  
Old 2/26/08, 4:05 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

Quote:
Originally Posted by jrichards
The letter from the "electrician" says it's a double 75A.
WHAT?????
What's a "double 75A" ????

Try again Sparky.

ps- I added the quotes.
Reply With Quote
  #10  
Old 2/26/08, 4:10 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

This is one of very old QO series breaker box and that box is 150 amp main rating let me expain a little on this one.

you see non standard arrangement on the handle because this is a paralleded connectioned breaker so it is rated at 75 amp per lug so muti by 2 result is 150 amp.

you should able see the catalog #'s on the side of panel it will tell ya what size it is.

Merci, Marc

BTW this is not a split buss breaker box at all
Reply With Quote
  #11  
Old 2/26/08, 4:41 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: What amperage is this panel

Quote:
Originally Posted by Speedy Petey
That's a 150A panel. Those 75's are wired in parallel like some Siemens and GE panels do with 200's. They use two 100's in parallel.
See how the short feeders from the main lugs are run in parallel.
VERY odd setup for sure.

150A.
That was the answer.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 2/26/08, 5:27 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: What amperage is this panel

Okay

I learned something valuable today.

Thanks, Guys!
Reply With Quote
  #13  
Old 2/26/08, 6:48 PM
jrichards jrichards is offline
Active Poster
 
Join Date: Feb 2006
Location: Jacksonville, FL
Posts: 213
Please Note: jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

Quote:
Originally Posted by Speedy Petey
WHAT?????
What's a "double 75A" ????

Try again Sparky.

ps- I added the quotes.
That's what I wanted to know!
Reply With Quote
  #14  
Old 2/26/08, 6:52 PM
jrichards jrichards is offline
Active Poster
 
Join Date: Feb 2006
Location: Jacksonville, FL
Posts: 213
Please Note: jrichards is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

Quote:
Originally Posted by Marc Benz
This is one of very old QO series breaker box and that box is 150 amp main rating let me expain a little on this one.

you see non standard arrangement on the handle because this is a paralleded connectioned breaker so it is rated at 75 amp per lug so muti by 2 result is 150 amp.

you should able see the catalog #'s on the side of panel it will tell ya what size it is.
I couldn't see anything else on the panel. Thank you for the edumacation
Reply With Quote
  #15  
Old 2/26/08, 8:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What amperage is this panel

That's one weird panel, for sure. Only the second one I've ever seen like that. I think they were called QOA1, if I'm not mistaken. A relic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts