Question Another Al Wiring Question

Is Aluminum wiring for the service entrance wires okay? I believe only single strand aluminum branch wiring is a problem, but want to confirm.
Thanks
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/7/11, 12:17 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Another Al Wiring Question

Not a problem. I would bet that 95% of the homes I inspect are aluminum. Copper is a rarity.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 3/7/11, 12:36 AM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Another Al Wiring Question

Quote:
Not a problem. I would bet that 95% of the homes I inspect are aluminum. Copper is a rarity.
true,true



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #4  
Old 3/7/11, 5:19 PM
John M. Walker John M. Walker is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Ocala, FL
Posts: 9
Default Re: Another Al Wiring Question

Multi strand aluminum wiring is still to code if used for a dedicated 240 VAC appliance circuit.
Reply With Quote
  #5  
Old 3/7/11, 5:20 PM
John M. Walker John M. Walker is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Ocala, FL
Posts: 9
Default Re: Another Al Wiring Question

Copper is the preferred feeder wire for manufactured homes.
Reply With Quote
  #6  
Old 3/11/11, 8:02 AM
wvaidic wvaidic is offline
InterNACHI Member
 
Join Date: Nov 2010
Location: Indialantic, FL
Posts: 10
Default Re: Another Al Wiring Question

Thanks for all of the answers.
Quote:
Originally Posted by jwalker1 View Post
Copper is the preferred feeder wire for manufactured homes.
So, if you found aluminum as feeder wire for a manufactured homes you would write it up as a defect?
Reply With Quote
  #7  
Old 3/11/11, 11:55 AM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Another Al Wiring Question

Make sure aluminum SEC's have anti-oxidant paste installed at the lugs. Some manufacturer's use aluminum lugs, but the set screws are made out of steel. The paste helps prevent galvanic reaction between two dissimilar metals.

Stranded AL SEC's are perfectly fine and expect to find them everywhere.
Reply With Quote
  #8  
Old 3/11/11, 3:03 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Al Wiring Question

While a good practice, the use of anti-oxidant paste is not required by the NEC, unless called for by the wire manufacturer.
Reply With Quote
  #9  
Old 3/11/11, 5:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Al Wiring Question

Quote:
Originally Posted by Jim Port View Post
While a good practice, the use of anti-oxidant paste is not required by the NEC, unless called for by the wire manufacturer.
I agree, you shouldn't be writing this up unless you know for sure that the specific lug manufacturer requires an anti-ox compound. To the best my knowledge most actually do not require it.
Reply With Quote
  #10  
Old 3/11/11, 8:19 PM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: Another Al Wiring Question

Aluminum is fine if sized properly. What could be a problem is the type of insulation on the wire. Where conductors enter the residence they should have a temperature rating of 90C. In other words the insulation marking should have an HH rating... THHN XHHW. The higher rating is for a better fire rating. Many older homes will not have this type of insulation, but newer construction should. There again electrical can be case sensitive according to the AHJ.
Reply With Quote
  #11  
Old 3/11/11, 11:09 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Al Wiring Question

Quote:
Originally Posted by mwolff View Post
Aluminum is fine if sized properly. What could be a problem is the type of insulation on the wire. Where conductors enter the residence they should have a temperature rating of 90C. In other words the insulation marking should have an HH rating... THHN XHHW. The higher rating is for a better fire rating. Many older homes will not have this type of insulation, but newer construction should. There again electrical can be case sensitive according to the AHJ.
Mark what do you mean about a better fire rating and insulation type?
Reply With Quote
  #12  
Old 3/12/11, 11:16 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Another Al Wiring Question

Wendy -

Aluminum stranded wire is probably the most common service entry wire in use in many areas. NO it would not be written /Just identified.
Reply With Quote
  #13  
Old 3/13/11, 12:35 AM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: Another Al Wiring Question

Quote:
Originally Posted by Robert Meier View Post
Mark what do you mean about a better fire rating and insulation type?
Not all insulation types are the same. Such as thermoplastics or rubber. The type of insulation or coating on the wire will give it a specific temp.(heat) rating. By having a higher temperature rating it would be less likely to melt down the insulation in high current situations, thus a better fire rating.
For instance, certain direct burial conductors(service lateral) could be used up to the meter. If enough was left over after making the connection to the meter, we would just use the same wire to go from the meter to the indoor panel. But now that the wire has entered the building it should have a higher insulation rating.
Not sure if this could ever be written up though as I am quite new to the home inspection world.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/13/11, 4:00 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Al Wiring Question

Direct burial cable used to feed a service are not for use inside the house.
Reply With Quote
  #15  
Old 3/13/11, 7:09 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Al Wiring Question

Quote:
Originally Posted by mwolff View Post
Not all insulation types are the same. Such as thermoplastics or rubber. The type of insulation or coating on the wire will give it a specific temp.(heat) rating. By having a higher temperature rating it would be less likely to melt down the insulation in high current situations, thus a better fire rating.
I'm not understanding this concept. If the conductor is properly sized for it's connected load why would the type of insulation make any difference?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
Panel box wiring..Question dnasser Electrical Inspections 8 10/30/10 9:17 AM
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 5:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 8:26 PM
Panel Surround / Exposed Wiring Question thance Electrical Inspections 11 2/19/08 9:06 PM