Is Aluminum wiring for the service entrance wires okay? I believe only single strand aluminum branch wiring is a problem, but want to confirm.
Thanks |
| Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Not a problem. I would bet that 95% of the homes I inspect are aluminum. Copper is a rarity.
Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#3
|
||||
|
||||
|
Quote:
J.Szczesny 4 Seasons Home Inspections Washington State Inspector # 711 800 5th Ave #101-385 Seattle, Wa 98104 (206)391-0285 online @ www.4seasonsinspects.com email @ info@4seasonsinspects.com toll free cal @ 866-512-9972 "For the best protection, get the right inspection" |
|
#4
|
|||
|
|||
|
Multi strand aluminum wiring is still to code if used for a dedicated 240 VAC appliance circuit.
|
|
#5
|
|||
|
|||
|
Copper is the preferred feeder wire for manufactured homes.
|
|
#6
|
|||
|
|||
|
Thanks for all of the answers.
So, if you found aluminum as feeder wire for a manufactured homes you would write it up as a defect? |
|
#7
|
||||
|
||||
|
Make sure aluminum SEC's have anti-oxidant paste installed at the lugs. Some manufacturer's use aluminum lugs, but the set screws are made out of steel. The paste helps prevent galvanic reaction between two dissimilar metals.
Stranded AL SEC's are perfectly fine and expect to find them everywhere. Scott Gilligan 215-888-4943 Infraspection Institute Level III Certified Thermographer Philadelphia Mold Inspections Philadelphia Home Inspections Philadelphia Commercial Inspections Philadelphia Licensed Home Inspector Pennsylvania - New Jersey - Delaware Infrared Thermal Imaging Inspections President The Greater Philadelphia Chapter of InterNACHI http://pa.nachi.org/greaterphiladelphia Vice President & Webmaster National Association of Commercial Building Inspectors and Thermographers |
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
While a good practice, the use of anti-oxidant paste is not required by the NEC, unless called for by the wire manufacturer.
|
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree, you shouldn't be writing this up unless you know for sure that the specific lug manufacturer requires an anti-ox compound. To the best my knowledge most actually do not require it.
|
|
#10
|
|||
|
|||
|
Aluminum is fine if sized properly. What could be a problem is the type of insulation on the wire. Where conductors enter the residence they should have a temperature rating of 90C. In other words the insulation marking should have an HH rating... THHN XHHW. The higher rating is for a better fire rating. Many older homes will not have this type of insulation, but newer construction should. There again electrical can be case sensitive according to the AHJ.
|
|
#11
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Wendy -
Aluminum stranded wire is probably the most common service entry wire in use in many areas. NO it would not be written /Just identified. |
|
#13
|
|||
|
|||
|
Quote:
For instance, certain direct burial conductors(service lateral) could be used up to the meter. If enough was left over after making the connection to the meter, we would just use the same wire to go from the meter to the indoor panel. But now that the wire has entered the building it should have a higher insulation rating. Not sure if this could ever be written up though as I am quite new to the home inspection world. |
| Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Direct burial cable used to feed a service are not for use inside the house.
|
|
#15
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Got a letter from ASHI's President today. | gromicko | General Inspection Discussion | 55 | 12/12/10 11:51 PM |
| Panel box wiring..Question | dnasser | Electrical Inspections | 8 | 10/30/10 9:17 AM |
| Top Ten Wiring Hazards Threaten Life and Property | jtedesco1 | Electrical Inspections | 3 | 9/2/08 5:15 PM |
| Top Ten Wiring Hazards | jtedesco1 | Electrical Inspections | 6 | 9/1/08 8:26 PM |
| Panel Surround / Exposed Wiring Question | thance | Electrical Inspections | 11 | 2/19/08 9:06 PM |