Default Another amazing installation.........

Supposedly this was done by a licensed electrician and sign off by the City inspector. ( this was a flip) # 14-2 wire out of the main service panel through a weather head, tied into 2 awg AL triplex , only 8 feet off the ground running through the back yard then re-attached to #14-2 and run through a pipe into the garage. This cannot be right ! Right?
The #14-2 w / ground was typical interior rated NM (Romex) . Also, this # 14 wire was protected by a 20 amp breaker in the panel.

How would you word this in a report , besides just saying that it was FUBAR and recommending eval by a qualified electrical contractor?
Attached Thumbnails
another-amazing-installation-wiring-garage-1.jpg   another-amazing-installation-wiring-garage-2.jpg   another-amazing-installation-wiring-garage-3.jpg  



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #2  
Old 4/6/08, 6:40 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another amazing installation.........

It is really hard to tell from the picture but the branch circuit supplying the garage seems to be as high as the service drop so in one is bad the other is bad.

20 amps on a #14 is bad but other than that there is nothing wrong with the installation. It is okay to upsize a conductor but it is wrong to down size one.
Reply With Quote
  #3  
Old 4/6/08, 6:52 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 230
Default Re: Another amazing installation.........

Thanks Mike. Actually the service drop is quite a bit higher, hard to tell from the pic though. So , is it ok for the #14 wire to be exposed to the elements like that? And should the point where the wire enters the garage also run through a weather head?



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #4  
Old 4/6/08, 7:23 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another amazing installation.........

Quote:
Originally Posted by rslocum
Thanks Mike. Actually the service drop is quite a bit higher, hard to tell from the pic though.
Quote:
Originally Posted by rslocum

So , is it ok for the #14 wire to be exposed to the elements like that?
That could be debatable as they are supposed to be sunlight resistant


Quote:
Originally Posted by rslocum
And should the point where the wire enters the garage also run through a weather head?
Yes or something equivalent
Reply With Quote
  #5  
Old 4/6/08, 7:26 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 230
Default Re: Another amazing installation.........

Thanks Mike ! Appeciate the help as always.



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #6  
Old 4/12/08, 10:35 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another amazing installation.........

If 14/2 is NM-B than the exposed wire is thhn/thwn and is good per code.
20 amp breaker is not to code. Must be 15 amp.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Grounded conductors cduphily Electrical Inspections 144 11/16/08 10:28 PM
Siding installation and electrical service equipment jtedesco1 Exterior Inspections 1 12/16/07 4:59 PM
Question about improper installation cbell1 Exterior Inspections 3 10/24/07 9:13 PM
Bonding wire installation requirements ?? rnewman1 Electrical Inspections 7 7/31/06 2:31 PM
Window installation jmichalski Exterior Inspections 17 1/24/06 9:42 PM


All times are GMT -4. The time now is 2:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts