Default Another fine pool aux panel

This one powered the pool motor, outlets, pool lights, heater and hot tub.

See anything wrong???
Attached Thumbnails
another-fine-pool-aux-panel-137-171.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/9/11, 11:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Another fine pool aux panel

What size breaker is protecting the feeders? Is the neutral terminal isolated from the panel? It's difficult to determine from your picture.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 12/10/11, 7:32 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Another fine pool aux panel

30 amps

It was difficut for me to see and I was there.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 12/10/11, 7:47 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another fine pool aux panel

Looks like the breakers might be from different manufacturers. You would need a load calculation to determine if the 30 amp feeder is of adequate size. Is this at/on a separate structure? If so I see no grounding electrode conductor so I would assume that there is no grounding electrode system installed.

Reply With Quote
  #5  
Old 12/10/11, 2:49 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Another fine pool aux panel

Quote:
Originally Posted by Robert Meier View Post
Looks like the breakers might be from different manufacturers. You would need a load calculation to determine if the 30 amp feeder is of adequate size. Is this at/on a separate structure? If so I see no grounding electrode conductor so I would assume that there is no grounding electrode system installed.
What would the load requiements be to cover a....
hot tub
pool lighting
pool pump motor
Gas fired pool heater

all in one panel. I would think just the hot tub itself would do it, but out of curiosity what size breaker and wire would be needed.

This panel was on the back of the home and the ground was present, just not connected in the panel. I found it loose and lying in the grass.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 12/10/11, 4:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another fine pool aux panel

If the panel wasn't mounted to a separate structure then no GES is required. There is an insulated EGC in the feeder which is required to ground the panel.

As far as load goes, without specific nameplate ratings from the equipment you cannot answer the question as to where or not a 30 amp feeder is adequate.
Reply With Quote
  #7  
Old 12/10/11, 4:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Another fine pool aux panel

It's pretty common to find a 40 amp feed on a system with multiple pumps and lights. 30 amps may be sufficient in this case.

If the heater is electric (which is very unlikely), it would need a larger circuit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 12/10/11, 4:09 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Another fine pool aux panel

If the neutral bar is isolated and ground bar is bonded, which they both appear to be (not sure), is there actually anything wrong here?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 12/10/11, 4:32 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another fine pool aux panel

Quote:
Originally Posted by ccurrins View Post
If the neutral bar is isolated and ground bar is bonded, which they both appear to be (not sure), is there actually anything wrong here?
IMO nothing that is readily identifiable from the photo.
Reply With Quote
  #10  
Old 12/10/11, 5:22 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Another fine pool aux panel

Interesting....
The circuit for the pool lights had tripped and wouldn't reset, which was the main issue at hand. The sizing was somthing uncommon for me to see, especially with all that was on it. We will see what the next guy has to say when they come to replace the breaker or correct the issue.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #11  
Old 12/10/11, 5:29 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Another fine pool aux panel

Quote:
Originally Posted by sfogarty View Post
Interesting....
The circuit for the pool lights had tripped and wouldn't reset, which was the main issue at hand.
What caused it to trip??



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 12/10/11, 5:42 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Another fine pool aux panel

Quote:
Originally Posted by ccurrins View Post
What caused it to trip??
It was already tripped Chirs. Its not my job to guess with pool lights, but if I had to I would start with a faulty breaker.

Maybe it got too hot while running all the other stuff.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #13  
Old 12/10/11, 5:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Another fine pool aux panel

Quote:
Originally Posted by sfogarty View Post
Maybe it got too hot while running all the other stuff.
Not likely.

There's probably a ground-fault in the lighting circuit, and the breaker is doing it's job. This often happens when the seal for the pool light fails.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/10/11, 5:54 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Another fine pool aux panel

Quote:
Originally Posted by sfogarty View Post
It was already tripped Chirs. Its not my job to guess with pool lights, but if I had to I would start with a faulty breaker.

Maybe it got too hot while running all the other stuff.
You did try to reset the breaker.....not your job either.

Maybe the breaker was doing it's job.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #15  
Old 1/27/12, 3:26 PM
Isaac Quezada Isaac Quezada is offline
InterNACHI Member
 
Join Date: Jan 2012
Posts: 12
Default Re: Another fine pool aux panel

what about double taps and wrong colored wires. hot and neutral same color as some wire going into breakers. i know they arent the exact same wire, but souldnt they be different colors.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Pool Executive Charged in Drain Death jhagarty Ancillary Inspection Services & Additional Topics 1 7/23/08 11:15 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
It's time for Professional Pool Inspections Revel L. Thom Ancillary Inspection Services & Additional Topics 13 7/26/07 10:50 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts