Default Another 'what was he thinking'?

I was looking forward to seeing good panel terminations when I removed the cover and saw the 4 conductors terminated in this 200 A subpanel. But very quickly I saw that the neutrals and grounds were all terminated (in pairs) on the bonded neutral bar and nothing on the ground terminals at all !! Somebody obviously missed the point entirely - Go figure !
Attached Thumbnails
another-he-thinking-eci-059.jpg   another-he-thinking-eci-062.jpg  



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #2  
Old 8/12/08, 8:28 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Another 'what was he thinking'?

That looks like the service panel. If so, the grounds and nuetrals should be on the same bar, just not under the same screw.
Reply With Quote
  #3  
Old 8/12/08, 9:22 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,927
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another 'what was he thinking'?

How about this one? What's your thoughts.

another-he-thinking-img_7802.jpg

This entire system wasn't even grounded.

another-he-thinking-img_7822.jpg
Reply With Quote
  #4  
Old 8/12/08, 10:03 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: Another 'what was he thinking'?

Quote:
Originally Posted by wsiegel
That looks like the service panel. If so, the grounds and nuetrals should be on the same bar, just not under the same screw.
Nope - the service panel (although smaller) is outside, mounted next to the meter - very common around here. Otherwise there would have been no need to bring four conductors to the subpanel at all.

However, on second thought, the conductors feeding this panel were not fed by a breaker in the outdoor service panel, rather from a second (bottom ) set of lugs on the main bus.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA

Last edited by fnewman; 8/12/08 at 10:07 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What are people thinking jschwartz1 Plumbing 30 4/24/08 12:34 PM
Needed my thinking cap on this one dandersen Thermal Imaging, Infrared Cameras & Energy Audits 7 2/15/08 2:58 PM
What were they thinking?! (For cat lovers - or haters) rhumphries General Inspection Discussion 7 1/11/08 11:17 AM
Thinking of becoming a home inspector in West Virginia David Goad General Inspection Discussion 9 2/15/07 9:28 PM


All times are GMT -4. The time now is 3:20 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts