I was looking forward to seeing good panel terminations when I removed the cover and saw the 4 conductors terminated in this 200 A subpanel. But very quickly I saw that the neutrals and grounds were all terminated (in pairs) on the bonded neutral bar and nothing on the ground terminals at all !! Somebody obviously missed the point entirely - Go figure !
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#2
|
|||
|
|||
|
That looks like the service panel. If so, the grounds and nuetrals should be on the same bar, just not under the same screw.
|
|
#3
|
||||
|
||||
|
Please Note:
bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#4
|
|||
|
|||
|
Quote:
However, on second thought, the conductors feeding this panel were not fed by a breaker in the outdoor service panel, rather from a second (bottom ) set of lugs on the main bus. Frank P. Newman Emerald City Inspections, LLC Dublin, GA Last edited by fnewman; 8/12/08 at 10:07 PM.. |
![]() |