Default Another Multi-wire Circuit Question

This is not my photo, I borrowed it from a colleague.
Is it true that, for this panel, the ungrounded conductors of a multi-wire circuit should not be connected to adjacent breakers 1-2 because they are on the same bus?
I thought multi-wire ungrounded conductors of the same circuit should always be connected to adjacent breakers, with a tie-bar between the breakers
Reply With Quote
  #2  
Old 3/30/07, 10:27 AM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Another Multi-wire Circuit Question

Woops, the file size of the photo was too big. It's an FPE Stablok.
Reply With Quote
  #3  
Old 3/30/07, 10:31 AM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Another Multi-wire Circuit Question

Here it is ( I think).
Attached Thumbnails
another-multi-wire-circuit-question-stab_lok_same_hot-cover-r1-.jpg.jpg
Views:	70
Size:	22.5 KB
ID:	10391  
Reply With Quote
  #4  
Old 3/31/07, 12:10 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Another Multi-wire Circuit Question

Hard to see in the photo because the breakers are all black. Keep in mind that a pair of half sized breakers will contact the same bus, and adjacent full sized breakers will contact opposite busses. The two hot wires of a multi-wire circuits must originate from opposite busses.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Easy question brepanshek Electrical Inspections 8 3/19/07 9:43 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM
Smokes on AFI circuits lprinzi Electrical Inspections 9 7/6/06 9:12 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 2:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts