Default Another Square D Breaker Question

Home built in 1990, no modifications, etc.

Breakers are all type HOM Square D. Load center is an I-T-E Siemens brand.

Are these breakers allowed in a Siemens box?

(Searched the BB but am in need of a quick response, sorry but thanks!)



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
  #2  
Old 10/16/09, 4:06 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Another Square D Breaker Question

Did you read the label in the box? When a manufacturer restricts use to his breakers, that is where he publishes it?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 10/16/09, 4:22 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Another Square D Breaker Question

Quote:
Originally Posted by jbushart View Post
Did you read the label in the box? When a manufacturer restricts use to his breakers, that is where he publishes it?
Yes. Note reads: .... designed for use with only I-T-E type QP, QT, QPF, QPH, QPHF, and HQP circuit breakers. All others will void warranty.

So, probably a dumb question, aside from the warranty issue, are HOM Square D breakers allowed?

(Yeah, this seems like a dumb question as I write it but maybe allowable alternates can now be used...)



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 10/16/09, 4:25 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Another Square D Breaker Question

Square D does not manufacture Classified Circuit Breakers

PDF



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #5  
Old 10/16/09, 4:38 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Another Square D Breaker Question

Thanks, now after reading that, would you write up the panel as I described? Sorry, long day and a bit cross eyed right now



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #6  
Old 10/16/09, 5:26 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Square D Breaker Question

Robert this was posted before, Square D 1-pole HOM 115 thru 150 and 2-pole HOM 215 thru 250 are compatible with ITE Siemens.

Gary
Reply With Quote
  #7  
Old 10/16/09, 5:27 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Another Square D Breaker Question

I've been out for a bit.

I simply state that the panel has breakers installed that are not on the list marked on the label and include a photo of the label.

Refer it out to a qualified electrician and let him sort it out.

If you want to do some more digging call ITE and ask them.

At this time Square D breakers are only listed for use in their panels.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #8  
Old 10/16/09, 6:15 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Another Square D Breaker Question

Thanks Mike and Gary (Gary, Thx for the email too)



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
AC Unit Maximum Breaker jchamp Inspecting HVAC Systems 17 11/28/10 1:10 AM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 3:57 PM
Square D breaker handle with holes for ties? kshepard Electrical Inspections 10 12/20/06 9:39 PM


All times are GMT -4. The time now is 2:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts