Default Another Sub????

I inspected a home yesterday with a 150amp main that had a 60amp breaker running to a sub in the garage. Everything looked ok in the main except for a few abandoned wires, however there was no main breaker. I have read some of paul abernathy's responses and did not realize if there are more than 6 breakers you need a main trip? Is this true in per code? or in all situations? even in Nj? Another question which I suggested further evaluation was the 60amp going to the sub in the garage had a 100amp disconnect. It had proper grounding, but shouldn't it have had a 60amp disconnect as well?

Thanks in advance!!
Chris
Reply With Quote
  #2  
Old 1/17/06, 9:35 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Another Sub????

It should take 6 throws or less to shut down a panel. Thats code.
Reply With Quote
  #3  
Old 1/17/06, 9:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Another Sub????

Quote:
Originally Posted by tallen
It should take 6 throws or less to shut down a panel. Thats code.
Not true for all panels, only the service equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 1/17/06, 9:50 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Another Sub????

Quote:
Originally Posted by Lbisurfcaster
Another question which I suggested further evaluation was the 60amp going to the sub in the garage had a 100amp disconnect. It had proper grounding, but shouldn't it have had a 60amp disconnect as well?

Thanks in advance!!
Chris
If the 60 amp breaker was feeding a 100 amp breaker, it's not a big deal. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/17/06, 9:52 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Sub????

Quote:
Originally Posted by Lbisurfcaster
I inspected a home yesterday with a 150amp main that had a 60amp breaker running to a sub in the garage. Everything looked ok in the main except for a few abandoned wires, however there was no main breaker. I have read some of paul abernathy's responses and did not realize if there are more than 6 breakers you need a main trip? Is this true in per code? or in all situations? even in Nj? Another question which I suggested further evaluation was the 60amp going to the sub in the garage had a 100amp disconnect. It had proper grounding, but shouldn't it have had a 60amp disconnect as well?

Thanks in advance!!
Chris

If there was a breaker at the main panel for this sub panel then the sub needs no disconnect at all. If the main panel is a split bus it can have up to six breakers on the main bus, one of which will shut down the second bus.
Reply With Quote
  #6  
Old 1/17/06, 9:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Sub????

You need a service disconnect. The panel it is in needs to be rated suitable for service equipment. If you are using the 6 handle rule for a service disconnect all of them have to also be rated as service equipment.

In a sub panel in a separate structure this is not service equiipment.
Reply With Quote
  #7  
Old 1/17/06, 10:52 PM
Lbisurfcaster Lbisurfcaster is offline
New User
 
Join Date: Jan 2006
Posts: 13
Please Note: Lbisurfcaster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Sub????

Thanks, everyone for the quick responses..

Chris
Reply With Quote
  #8  
Old 1/19/06, 5:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Another Sub????

Quote:
Originally Posted by Lbisurfcaster
Another question which I suggested further evaluation was the 60amp going to the sub in the garage had a 100amp disconnect. It had proper grounding, but shouldn't it have had a 60amp disconnect as well?

Thanks in advance!!
Chris

Chris,

As jeff so correctly stated.....it is not a problem but here is how you remember that....the system is only as good as it's weakest link. In this case if the wire is rated for 60A, the breaker is 60A that feeds the wire tot he 100A disconnect....then the garage disconnect can be 100A with no problem....because the concern is the wire which is protected ahead of the disconnect with the correct breaker....as you stated.



Paul W. Abernathy
Reply With Quote
  #9  
Old 1/19/06, 11:03 PM
Lbisurfcaster Lbisurfcaster is offline
New User
 
Join Date: Jan 2006
Posts: 13
Please Note: Lbisurfcaster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another Sub????

Thanks Paul.. and for everyone else's answers!

Chris
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts