Default Another version of the kitchen bar wall outlet

Check out this one, picture taken while standing in the walkway between the kitchen and breakfast nook. Sink faucet is visible at other side of the bar.

Outlet is about 12 inches below the underside of the bar and about 27 inches above the floor.


Does this outlet serve the kitchen countertop?
Or does it only serve the bar top?
Or does it serve neither?
Attached Thumbnails
another-version-kitchen-bar-wall-outlet-january-11-2009-004.jpg  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 1/11/09, 11:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Another version of the kitchen bar wall outlet

The "bar top" is a counter top.

Assuming the counter top does not project 6 or more inches past the wall, this receptacle serves the counter top and would require GFCI protection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/11/09, 11:25 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is online now
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,421
Default Re: Another version of the kitchen bar wall outlet

Serves countertop and yes for GFCI. Bruce, what's the other outlet? cable, phone?



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 1/11/09, 11:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another version of the kitchen bar wall outlet

Yeah, if it's within the dimensional limits that it would be considered as a receptacle serving the countertop (no greater than 6" overhang, no lower than 12"), it does require GFCI protection.

When I see colors mis-matched like that cable jack is (ivory or light almond device with a white cover), it makes me look at stuff extra hard. That's the sign of a handy man.
Reply With Quote
  #5  
Old 1/12/09, 12:08 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Another version of the kitchen bar wall outlet


Nah ...I won't say it.
Reply With Quote
  #6  
Old 1/12/09, 12:17 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Another version of the kitchen bar wall outlet

The bar extends about 12 inches past the wall.

Yes, that is a TV outlet



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 1/12/09, 12:55 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Another version of the kitchen bar wall outlet

I think it's fine. If someone's dumb enough to plug a TV into that outlet, they deserve to die.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 1/12/09, 11:28 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Another version of the kitchen bar wall outlet

Quote:
Originally Posted by bking View Post
The bar extends about 12 inches past the wall.
Then the receptacle does not technically serve the counter top, and does not require GFCI protection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 1/12/09, 3:21 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,857
Default Re: Another version of the kitchen bar wall outlet

Quote:
Originally Posted by jfunderburk View Post
I think it's fine. If someone's dumb enough to plug a TV into that outlet, they deserve to die.

Joe, is that a narrative you use often?
Reply With Quote
  #10  
Old 1/14/09, 6:25 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Another version of the kitchen bar wall outlet

Bruce,

They look to be 12 inch tiles on the passover portion so if the wall is framed with 2X4's and then sheetrocked that outta leave about 6 inches (or less) on the receptacle side (the measurable 'overhang' area).

I'd go with a GFCI recommended upgrade if it isn't as it (from the pics) certainly could 'serve the counter top area'...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #11  
Old 1/14/09, 7:02 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Another version of the kitchen bar wall outlet

This outlet does have GFCI protection....



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #12  
Old 1/14/09, 7:04 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Another version of the kitchen bar wall outlet

WHEW!!

Glad that's over...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Termites in a kitchen wall rbibler Thermal Imaging, Infrared Cameras & Energy Audits 19 11/17/08 11:12 PM
Moisture Management mcyr Exterior Inspections 15 9/8/08 1:11 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 6:25 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 11:48 AM