#1
|
||||
|
||||
|
Check out this one, picture taken while standing in the walkway between the kitchen and breakfast nook. Sink faucet is visible at other side of the bar.
Outlet is about 12 inches below the underside of the bar and about 27 inches above the floor. Does this outlet serve the kitchen countertop? Or does it only serve the bar top? Or does it serve neither? B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#2
|
||||
|
||||
|
The "bar top" is a counter top.
Assuming the counter top does not project 6 or more inches past the wall, this receptacle serves the counter top and would require GFCI protection. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Serves countertop and yes for GFCI. Bruce, what's the other outlet? cable, phone?
Robert Newland Tyrone, GA 30290 NACHI05101290 http://www.CertifiedHI.com http://www.HomeInspectorTyroneGa.com Home Inspection Reports Powered by: HomeGauge eServices |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yeah, if it's within the dimensional limits that it would be considered as a receptacle serving the countertop (no greater than 6" overhang, no lower than 12"), it does require GFCI protection.
When I see colors mis-matched like that cable jack is (ivory or light almond device with a white cover), it makes me look at stuff extra hard. That's the sign of a handy man. |
|
#5
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Nah ...I won't say it. |
|
#6
|
||||
|
||||
|
The bar extends about 12 inches past the wall.
Yes, that is a TV outlet B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#7
|
||||
|
||||
|
I think it's fine. If someone's dumb enough to plug a TV into that outlet, they deserve to die.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
||||
|
||||
|
Then the receptacle does not technically serve the counter top, and does not require GFCI protection.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Quote:
Joe, is that a narrative you use often? |
|
#10
|
||||
|
||||
|
Bruce,
They look to be 12 inch tiles on the passover portion so if the wall is framed with 2X4's and then sheetrocked that outta leave about 6 inches (or less) on the receptacle side (the measurable 'overhang' area). I'd go with a GFCI recommended upgrade if it isn't as it (from the pics) certainly could 'serve the counter top area'... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#11
|
||||
|
||||
|
This outlet does have GFCI protection....
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#12
|
||||
|
||||
|
WHEW!!
Glad that's over... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Termites in a kitchen wall | rbibler | Thermal Imaging, Infrared Cameras & Energy Audits | 19 | 11/17/08 11:12 PM |
| Moisture Management | mcyr | Exterior Inspections | 15 | 9/8/08 1:11 PM |
| VIDEO--Bowed Basement Wall, Cracks etc | john bubber | Structural Inspections | 75 | 7/21/08 6:25 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 2:26 AM |
| Newbie here with a slab "standards" question | Robert Young, #3 | Structural Inspections | 17 | 4/10/07 11:48 AM |