Default Any code violation here?

1yr warranty inspection,

Is it allowed to have 14.2 amps (measured) of permanent light fixtures on a 15 amp circuit that also has some wall outlets on it?

This involves kitchen, dining, breakfast nook and hallway lights and also the outlets in the front living room where lamps could be plugged in later.

Homeowner trips the breaker when using a (10 amp measured) vacuum cleaner. Breaker is labeled "kitchen lights".


Just poor wiring/labeling practice or is this a code violation?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #2  
Old 11/22/08, 5:00 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any code violation here?

In a dwelling, that's legal. Inconvenient as can be, but legal.
Reply With Quote
  #3  
Old 11/22/08, 5:01 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: Any code violation here?

It's pretty much poor practice. The lighting isn't considered a continuous load, so it doesn't fall into the 80% FLA category. Check with the town's local codes, they may have a limit on the number of outlets (inc lighting) on one circuit. In my town they have a limit of 8.

Jeff
Reply With Quote
  #4  
Old 11/22/08, 8:43 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any code violation here?

Quote:
Originally Posted by bking View Post
1yr warranty inspection,

Is it allowed to have 14.2 amps (measured) of permanent light fixtures on a 15 amp circuit that also has some wall outlets on it?

This involves kitchen, dining, breakfast nook and hallway lights and also the outlets in the front living room where lamps could be plugged in later.

Homeowner trips the breaker when using a (10 amp measured) vacuum cleaner. Breaker is labeled "kitchen lights".


Just poor wiring/labeling practice or is this a code violation?
Hello,
In any situation like this were CODE is a major point you will want to call in some Sparkys.

The other posters are correct, but they give no advice for you.


Hmm, how do you know there are 14.2 amps on that circuit? Did you tell anyone?

If you are not doing a complete code HI then you have no need for the info you provided , and I hope you did not put it in your report......

If you did , then that makes you a top of the line electrical consultant....

Last edited by tallen; 11/22/08 at 8:52 PM..
Reply With Quote
  #5  
Old 11/22/08, 8:53 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any code violation here?

Quote:
Homeowner trips the breaker when using a (10 amp measured) vacuum cleaner. Breaker is labeled "kitchen lights".
Measured by what? Are you a licenced and qualified electrician?

Bla bla bla.............. them Lawer type as-s wipes can go on forever.....
Reply With Quote
  #6  
Old 11/22/08, 9:38 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,789
Default Re: Any code violation here?

Correct me if I am wrong, but did your post state that the kitchen is on a 15 amp breaker????



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #7  
Old 11/22/08, 10:09 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default Re: Any code violation here?

Quote:
Originally Posted by wsiegel View Post
Correct me if I am wrong, but did your post state that the kitchen is on a 15 amp breaker????

kitchen lights etc....

Would have been too easy if it were the kitchen counter outlets.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #8  
Old 11/22/08, 10:12 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default Re: Any code violation here?

Quote:
Originally Posted by tallen View Post
Measured by what? Are you a licenced and qualified electrician?

Bla bla bla.............. them Lawer type as-s wipes can go on forever.....

Not to worry, many of us ask questions on here that go much deeper than inspection SOP's and report writing. No harm in learning or contributing knowledge beyond the scope.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #9  
Old 11/23/08, 2:26 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any code violation here?

Bruce .,

The sistuation you are describing it is legit set up however it kinda poor pratice to do that.

I know it can get out of hand but some case in some of the homes some of the contractors go by few diffrent way .,, Bare minuim NEC code requirement { that typically a cheapest route to run the conductors } and med or top of line which it mean more than minuim code requirement.

Merci,Marc
Reply With Quote
  #10  
Old 11/26/08, 2:38 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 327
Default Re: Any code violation here?

Hey Bruce, I am curious how you picked that up. Did the owner's statement tip you off to look for a problem, or did you find it on your own?
Reply With Quote
  #11  
Old 11/26/08, 10:54 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default Re: Any code violation here?

Owner discovered the issue, I was doing a 1 year warranty inspection and took the time to make a few extra checks to see if the problem appeared to be an immediate fire hazard or if the circuit was loaded beyond max with just the lights.

I always try to accomodate the client on these 1 year inspections, they always have some inside information about the house that is interesting. This is not something I usually look for and do not recommend anyone start checking current draw without experience with doing so. I didn't even stay in a holiday inn all year but could.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage/house fire door Steven C. Meyer General Inspection Discussion 15 2/5/08 8:06 AM
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM


All times are GMT -4. The time now is 9:31 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts