Default Any Comments on Breaker Panel

This breaker panel was installed in a home I inspected last week.
Notice the 120v 100 amp main. Any comments?
Also some circuits are AL.

Thanks.
Attached Thumbnails
any-comments-breaker-panel-p1070737.jpg   any-comments-breaker-panel-p1070738.jpg   any-comments-breaker-panel-p1070739.jpg   any-comments-breaker-panel-p1070740.jpg  



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080

Last edited by mbenerowski; 7/9/10 at 11:21 PM.. Reason: wrong pics
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/10/10, 12:09 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Any Comments on Breaker Panel

AL needs paste and to be connected to AL approved devises etc,so if it is in the branch circuits I defer to Electrician myself.

Notice your pic shows white at ground and 2 different sized conductors double tapped.

What is connected to that knuckle off the feeder?(sorry can't tell.)(looks like they ran it to a sidecar for a A/C unit) Am I right?
Need better labeling.

Do not see much Romex so hope that is not extension cord.

Also observe two of the double breakers are in the off position.Do you know why?

Ran two conductors through one BX connector at the panel.(Is that a bare black conductor and extension cord ?)

OK on second look I swear it looks as if they cut the conductor off the closed 15 amp double breaker.

Stopping there because looking at wiring pics makes my eyes blurry.

Last edited by belliott; 7/10/10 at 12:16 AM..
Reply With Quote
  #3  
Old 7/10/10, 5:49 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Any Comments on Breaker Panel

Be a lot easier to see and accurately describe something if the photos were oriented. Do you not have photo software that can flip the photos. I really hate tilting my head sideways to look at photos, it may not go back straight one day.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #4  
Old 7/10/10, 6:24 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Any Comments on Breaker Panel

They mount them sideways in Canada Doug.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 7/10/10, 7:07 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any Comments on Breaker Panel

Not sure about the Canadian electrical code but there are some issues under the NEC. I see other 2 pole breakers so I don't know what you mean by 120 volt, 100 amp main. Back-fed mains require a clip or screw to keep them from pulling out. There are multiple conductors under the ground lug in photo #4.
Reply With Quote
  #6  
Old 7/10/10, 7:16 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Any Comments on Breaker Panel

There is also a double tapped 15 A breaker on the bottom row and the lug near the right side is not likely rated for more than 1 conductor.

And as Robert said, It looks like a 120/240 V panel with no hold down for the 100 main.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 7/10/10, 9:46 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Any Comments on Breaker Panel

Just took another quick look and see the breakers were tripped when the cover was pulled off.
Hope you remembered to reset them.
Reply With Quote
  #8  
Old 7/10/10, 10:32 AM
mbenerowski mbenerowski is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Toronto, On
Posts: 59
Default Re: Any Comments on Breaker Panel

The home has 2 stoves one AC unit and a dryer. My concern is that no other subpanels were observed in the home or carport. Not sure what this knuckel is feeding, and if this connection is safe. The knuckel is not feeding to AC unit. Everything was operating in the home and the double pole 20amp was in the off position from the start. My concern is with the knuckel. Can you do this connection? and with no subpanel attched?



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Reply With Quote
  #9  
Old 7/10/10, 10:50 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Any Comments on Breaker Panel

Allowed if done the right way.

Breaker is on in picture before cover removal by the way.
Reply With Quote
  #10  
Old 7/10/10, 11:44 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any Comments on Breaker Panel

That "knuckel" as some call it, looks like a split bolt connection to extend a service conductor that was cut too short. If any of the reds are also in that splice I can't tell.
Reply With Quote
  #11  
Old 7/10/10, 12:33 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Any Comments on Breaker Panel

just an observation, there are two red wires coming off the black wire at the split bolt.

Not determining where this stuff goes, you may have missed a significant issue.

I see someone using two wires of lower capacity to feed a single circuit somewhere. The two wires are trying to produce the sum of the required amperage capacity by double tapping.

This is a circuit without over current protection as well!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 7/10/10, 12:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any Comments on Breaker Panel

Let's start with some information:

1-Is the 100 amp CB the service disconnect?
2-Are the red conductors connected to anything?
3-Is the rigid conduit a service raceway?
Reply With Quote
  #13  
Old 7/10/10, 3:34 PM
mbenerowski mbenerowski is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Toronto, On
Posts: 59
Default Re: Any Comments on Breaker Panel

1-Yes
2- Yes - Split bolt connection
3- Yes - and I can't trace the wires out the top mast head or at any visible location on the raceway.



Quote:
Originally Posted by Robert Meier View Post
Let's start with some information:

1-Is the 100 amp CB the service disconnect?
2-Are the red conductors connected to anything?
3-Is the rigid conduit a service raceway?



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/10/10, 3:46 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any Comments on Breaker Panel

Quote:
Originally Posted by mbenerowski View Post
3- Yes - and I can't trace the wires out the top mast head or at any visible location on the raceway.
The conduit should go into the meter base and then from the meter base to the weatherhead. Are you saying you cannot see any of this conduit?
Reply With Quote
  #15  
Old 7/10/10, 4:26 PM
mbenerowski mbenerowski is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Toronto, On
Posts: 59
Default Re: Any Comments on Breaker Panel

Quote:
Originally Posted by Jim Port View Post
The conduit should go into the meter base and then from the meter base to the weatherhead. Are you saying you cannot see any of this conduit?
Yes, I can see the meter and conduit. A stone facing has been applied throughout the home and the raceway is only 1/2 visible. Ok my point is that these two red wires enter the raceway off the split bolt connection. I can't visually trace where these two red wires go (maybe behind the stone facing). There are no sub panels in the garage or anywhere on the property. Is this standard instalation? I have a funny feeling about this installation, however Im not any electrican. I know about the double taps (15amp breaker/ and 3 taps on panel grounding connection) and flux on the AL wiring. My question is that these red wires are live, and they go somewhere.

P.s. the AC unit does not have a disconect switch on the exterior.

I called out an electrician but just wanted some extra info.

Hence this post.
Attached Thumbnails
any-comments-breaker-panel-p1070674.jpg   any-comments-breaker-panel-p1070612.jpg   any-comments-breaker-panel-p1070740.jpg  



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
High Magnetic circuit breaker to fit Homeline 200 amp panel Unregistered AskNACHI.org Inspection Questions Forum 0 11/24/09 2:50 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Old panel configuration for comments dnice Electrical Inspections 8 9/9/07 1:35 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM