Default Anything wrong with this?

Anything wrong with this???

50 amp bridged breaker (electric range I believe) with appropriately sized conductors. However, one is copper and the other is aluminum.

I can only assume that the copper distribution wire was short (or had to be replaced) so they spliced a short pigtail to ONE side with aluminum stranded. Again, can only assume that they used Aluminum because that is what they had in the truck?????

Can't think of any reason this would be called out but wanted to get a second opinion before submitting my report.

Any input is welcome.
Attached Thumbnails
anything-wrong-img_2580.jpg   anything-wrong-img_2581.jpg  
Reply With Quote
  #2  
Old 11/4/06, 4:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Anything wrong with this?

The CU to AL splice would be a potential point of issue. It must be an approved connector, but it almost looks like a split-bolt connector (which would not be proper).

Verification of the connection would be warranted. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 11/4/06, 5:03 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

Actually a correct CU/AL split-bolt is one of the proper methods of splicing larger AL to CU. They have a "partition" that keeps the two dissimilar conductors from coming in contact.


To me that looks like tinned, or AL clad, copper, not aluminum.
Reply With Quote
  #4  
Old 11/4/06, 5:03 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

Quote:
Originally Posted by jpope
The CU to AL splice would be a potential point of issue. It must be an approved connector, but it almost looks like a split-bolt connector (which would not be proper).

Verification of the connection would be warranted. . .
Thanks Jeff....

Why can't a split bolt connector be used if properly rated for this connection? I've seen them rated for Aluminum to Copper connections:

Split bolt connector with spacer bar Copper alloy-bodied, electro-tin plated For aluminum-to-aluminum cable Copper-to-aluminum cable Copper-to-copper cable Size= Min/Max range of equal main & tap Color: WIRE:Solid/Stra Size: SIZE:6/ 1/0

http://acmehardware.com/Electrical/M...ment-ASB1and0/

What would you consider to be a proper splice (Copalum Crimp?).

Last edited by jweinberg; 11/7/06 at 10:50 PM..
Reply With Quote
  #5  
Old 11/4/06, 5:07 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

I agree with Speedy on this----that wire is not likely aluminum----note the cloth covering?
Reply With Quote
  #6  
Old 11/4/06, 5:56 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Anything wrong with this?

Howdy,

Mind if I chime In.......

Actually older style split bolts that are copper where not designed to be CU/AL conection choices......The bridge in the middle was still copper and not voiding the copper to aluminum issue.....The ones that Speedy and I used today will be listed and labeled as AL/CU if they have that intent...and are usually silver in color ( well the ones I use are...lol...)

Many of the older split bolts that are copper colored did not allow for the mixing.......HOWEVER.....

With that said.......I do not think you should call this out because you are not able to verify the type of split bolt and the electrician is not going to come and cut off the tape to see....so it depends on the installation....

If it was a relative new change over.....we have to assume they used a AL/CU rated Split Bolt.......but being it is wrapped.....no signs of melting tape....due to possible signs of heat build up.....a condition that may occure in a situation where disimilar metals happen and resistance could lead to heat built up......sooooooo

so regardless of Alum or Copper Conductors.......since you can't see the end of the conductor to verify if it is Copper Tinned and so on......not enough of something I would call out....sorry...only my opinon.

Never said I was a GURU.......just opinionated.


lKnob & tube: 1880’s – 1930’s
lAC (armored cables) 1930’s - current
lNM (non-metallic) cloth covered:1928 – 1960’s
lNM (romex) (plastic sheathed): 1960’s - current



Copper conductors: 1880’s to current
Tinned Copper conductors: 1910’s to 1950’s
Aluminum conductors: 1960’s to current



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 11/4/06, 6:56 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

Quote:
Originally Posted by pabernathy
With that said.......I do not think you should call this out because you are not able to verify the type of split bolt
I agree Paul. Mainly becuase it is not VISIBLE.

I did not call this out but did call out the oversized breaker (50 Amp on a 10AWG copper conductor) and the scorched wire and melted insulation in other parts of the panel, while calling for a complete evaluation of the panel by a licensed electrician.

The Sparky should decide if there is a problem with the splice while he is doing his complete evaluation.

Thanks to everyone that chimed in....

Jeff
Reply With Quote
  #8  
Old 11/5/06, 12:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Anything wrong with this?

Quote:
Originally Posted by Speedy Petey
Actually a correct CU/AL split-bolt is one of the proper methods of splicing larger AL to CU. They have a "partition" that keeps the two dissimilar conductors from coming in contact.
Good point. I rarely see that type and forgot that they exist.

Quote:
To me that looks like tinned, or AL clad, copper, not aluminum.
Looking again at the photo, I agree.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 11/7/06, 9:04 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

Quote:
Originally Posted by cbuell
I agree with Speedy on this----that wire is not likely aluminum----note the cloth covering?
Quote:
Originally Posted by Speedy Petey
To me that looks like tinned, or AL clad, copper, not aluminum.
Quote:
Originally Posted by jpope
Looking again at the photo, I agree.
Thanks guys....

Since you can't see the tips of the conductor, what clues are there that the wire is tinned copper and not aluminum?
Reply With Quote
  #10  
Old 11/7/06, 9:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Anything wrong with this?

The cloth cover is one indicator - there are also knicks on the wire that have exposed the copper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 11/7/06, 10:59 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this?

For me it just an experienced eye. Old tinned CU looks quite different that solid AL.
Also as Jeff said, the braided/rubber insulation is quite common to tinned CU.
Reply With Quote
  #12  
Old 11/7/06, 11:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Anything wrong with this?

as well it appears to be nicks that has the copper showing through... unless the color is just a bad image.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thanks Nick I just hate it when I'm wrong cbottger Misc. Discussion 0 6/9/07 3:01 PM
Messy work, but is it wrong? mtimpani Electrical 8 9/9/06 10:56 PM
What's Wrong Here? jtedesco1 HVAC 20 6/29/06 7:50 PM


All times are GMT -4. The time now is 12:37 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts