Default Anything wrong with this grounding connection?

Lead main piping connected to a copper section 8ft and then connected to Pex piping.

Thanks.
Attached Thumbnails
anything-wrong-grounding-connection-p1040659.jpg   anything-wrong-grounding-connection-p1040660.jpg  



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/8/10, 7:57 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this grounding connection?

Here's the NEC requirement for using a water pipe as a grounding electrode:

Quote:
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
If the pipe in question has 10' or more in contact with the earth then it must be used as a grounding electrode and the connection point of the grounding electrode conductor (GEC) must be within 5' of where it enters the building. Unless there is something that cannot be seen from the photo's it seems like the installation is code compliant.
Reply With Quote
  #3  
Old 3/8/10, 8:04 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Anything wrong with this grounding connection?

Is that a Ground, or is it a Bond????
Reply With Quote
  #4  
Old 3/8/10, 8:19 PM
mbenerowski mbenerowski is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Toronto, On
Posts: 59
Default Re: Anything wrong with this grounding connection?

Its the ground. I traced it to the panel.



The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Reply With Quote
  #5  
Old 3/10/10, 3:52 PM
Tim Larsen Tim Larsen is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Central Vermont
Posts: 139
Default Re: Anything wrong with this grounding connection?

Wouldn't there be a dialetric union between the lead and copper?
Shouldn't the GEC hit the lead pipe?

Tim
Reply With Quote
  #6  
Old 3/11/10, 7:31 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Anything wrong with this grounding connection?

Quote:
Originally Posted by tlarsen View Post
Wouldn't there be a dieletric union between the lead and copper?
Shouldn't the GEC hit the lead pipe?

Tim

If there is, then I agree with you. I haven't seen a lead pipe is a long time. Is a dielectric union always used between the two different metal pipes?
Reply With Quote
  #7  
Old 3/11/10, 11:38 AM
Tim Larsen Tim Larsen is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Central Vermont
Posts: 139
Default Re: Anything wrong with this grounding connection?

To be honest I haven't run into lead either and don't know how it affects copper; however, galv to copper, yup.

Tim
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
Panelboard neutral and grounding conductor terminations. jtedesco1 Electrical Inspections 0 1/16/08 3:16 AM
Bathroom fixtures protected by GFCI mthomas2 Electrical Inspections 7 8/10/07 12:39 PM
Branch circuit grounding wires in panel Michael Martin Electrical Inspections 4 5/31/07 9:44 AM


All times are GMT -4. The time now is 2:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts