Old 3/8/10, 8:26 PM
mbenerowski mbenerowski is offline
Default Anything wrong with this grounding connection?
Lead main piping connected to a copper section 8ft and then connected to Pex piping.
Thanks.
anything-wrong-grounding-connection-p1040659.jpg   anything-wrong-grounding-connection-p1040660.jpg
The Inspection Consultant Inc.
www.gtahomeinspector.com
info@theinspectionconsultant.com
tel: 416-843-7080
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 3/8/10, 8:57 PM
Robert Meier's Avatar
Default Re: Anything wrong with this grounding connection?
Here's the NEC requirement for using a water pipe as a grounding electrode:
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe. A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductors. Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
If the pipe in question has 10' or more in contact with the earth then it must be used as a grounding electrode and the connection point of the grounding electrode conductor (GEC) must be within 5' of where it enters the building. Unless there is something that cannot be seen from the photo's it seems like the installation is code compliant.
Old 3/8/10, 9:04 PM
Brian E. Kelly's Avatar
Is that a Ground, or is it a Bond????
Old 3/8/10, 9:19 PM
Its the ground. I traced it to the panel.
tel: 416-843-7080
Old 3/10/10, 4:52 PM
Tim Larsen Tim Larsen is online now
Wouldn't there be a dialetric union between the lead and copper?
Shouldn't the GEC hit the lead pipe?
Tim
Old 3/11/10, 8:31 AM
Originally Posted by tlarsen View Post
Wouldn't there be a dieletric union between the lead and copper?
Tim
If there is, then I agree with you. I haven't seen a lead pipe is a long time. Is a dielectric union always used between the two different metal pipes?
Old 3/11/10, 12:38 PM
To be honest I haven't run into lead either and don't know how it affects copper; however, galv to copper, yup.
Tim
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 10:02 PM
Panelboard neutral and grounding conductor terminations. jtedesco1 Electrical Inspections 0 1/16/08 4:16 AM
Bathroom fixtures protected by GFCI mthomas2 Electrical Inspections 7 8/10/07 1:39 PM
Branch circuit grounding wires in panel Michael Martin Electrical Inspections 4 5/31/07 10:44 AM