Thanks for the comments on gutters. Here is the other half. Texas Standards state:
report as in need of repair appliances and electrical gutters that do not have proper bonding; I presume they speak of installed appliances that will convey. I am not aware of appliances that are bonded. I thought they were grounded. Am I missing something? TY |
|
#2
|
||||
|
||||
|
Quote:
Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#3
|
|||
|
|||
|
Quote:
|
|
#4
|
||||
|
||||
|
Fred & Brian wrote it...make them tell us how to comply
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Could be as simple as sticking one meter prong in the hot slot of a receptacle, and sticking the other meter lead on the metal of the appliance (range, dishwasher, etc.) and see if you read 120V or not. This test isn't fool-proof, of course, but would be a good start. This simple test alone is surely beyond the scope of a typical home inspection, and any more conclusive testing is way-way, way beyond the scope of a regular home inspection.
|
|
#6
|
|||
|
|||
|
Quote:
I did ask on behalf of the new guy and here is the reply: The best suggestion that I can give you is to go back to your education provider and have them teach you how to comply with all provisions of the standards of practice. |
|
#7
|
|||
|
|||
|
City of Frisco requires bonding of all Type B, chimney flues, metal air ducts and kitchen range vents. Not sure if they amended Fuel Gas code. I do not have a copy. I'll dig up some photos. Band clamps on Type B and chimney with bare # 8 to the panel. Looks weird.
New SoP say bond ALL metal pipe. So I guess we write up all of above plus cast iron vent pipes? |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Your "out" there is "likely to become energized". This means different things to different people. Additionally, if the appliance connected to a certain duct or vent is already bonded, then the duct or vent is also bonded.
|
|
#10
|
|||
|
|||
|
Quote:
|
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Quote:
|
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bonding may not be specified as being lightning protection but if everything was bonded the chance of being injured by lightning in your home is virtually eliminated.
When Mythbusters did their series of lightning experiments (shower, phone etc) in the PG&E test house the first thing they had to do to get any result was lift the connection to the grounding electrode. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Neutral bus bar failed inspection | Greg Moritz | Electrical | 18 | 1/19/08 2:53 PM |
| Bonding Piping 101....Good To Know ! | pabernathy | Electrical | 37 | 4/28/07 12:25 PM |
| Demystify Grounding & Bonding Class | pabernathy | Education | 5 | 12/24/06 2:10 AM |
| Another reason to recommend CO testers | rnewman1 | Interior | 2 | 10/12/06 8:47 AM |