Default Appliances connected to GFCI

Both of these situations are a first for me (haven't seen this in 9 years).
The propane gas stove in the kitchen is wired to (connected to) the GFCI electrical receptacles in the kitchen.
The garage door opener (in the same house) is wired to (connected to) the GFCI electrical receptacles in the garage.
If these GFCI's trip, no cooking and no automated garage door opener.
Has anyone seen either of these conditions before.
I noted both in the report, but of course this is a bank owned property (which was actually in very good condition).
By the way the dishwasher was wired to a wall switch; if switch is off no power to the dishwasher.



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/10/12, 11:26 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

Everything that you've described is NEC compliant.
Reply With Quote
  #3  
Old 2/10/12, 11:45 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

As long as GFCI can be located easily.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #4  
Old 2/10/12, 11:47 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

The switch for the DW is there to serve as a service disconnect in case someone is working on the unit. The NEC requires a means of disconnect and this is one option.

Under the latest NEC all receptacles in the garage need GFI protection including the ceiling mounted one.

The small appliance circuits are allowed to service the receptacle for a gas stove.
Reply With Quote
  #5  
Old 2/10/12, 11:56 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

Yes but the reset should not be on the ceiling only the outlet, according to common sense. I have seen GFCI protection at the source for garage door openers on the 12 foot high garage ceiling.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 2/10/12, 12:03 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

Quote:
Originally Posted by kwood View Post
Yes but the reset should not be on the ceiling only the outlet, according to common sense. I have seen GFCI protection at the source for garage door openers on the 12 foot high garage ceiling.
That is no longer permitted under the 2011 NEC since they need to be readily accessible for testing purposes.
Reply With Quote
  #7  
Old 2/10/12, 12:49 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

Nice to here that change in the NEC.
Also the application of GFCI is not needed on freezer or fridge,
another common sense area.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 2/10/12, 1:00 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Appliances connected to GFCI

Quote:
Originally Posted by kwood View Post
Nice to here that change in the NEC.
Also the application of GFCI is not needed on freezer or fridge,
another common sense area.
If it is in the garage or basement they are required to be GFCI protected and this is a good common sense move.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #9  
Old 2/10/12, 1:09 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Appliances connected to GFCI

Stand by for ( unless things change ) there could be many changes to the Ontario electric Code example a Car charging unit in all Garages two car garage two charging units .
Now this I think is not a good idea if only 10% of the cars went electric we will have huge problems .
Not enough power to run the system .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #10  
Old 2/10/12, 1:31 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

Kevin, I see you are under the CEC, but the NEC has removed the exemptions for GFI protection for appliances in garages.
Reply With Quote
  #11  
Old 2/10/12, 1:50 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

Remember whether it is removed or not we only are concerned about what is in place at the time of the Home we are inspecting. Thus the common sense comment applies.
Look at comment #4
Attached Files
File Type: pdf _GFCI_requirement_page-2008[1].pdf (14.1 KB, 44 views)



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 2/10/12 at 1:53 PM..
Reply With Quote
  #12  
Old 2/10/12, 2:21 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

Kevin, the way I took your comment was it is good to see that the GFI protection is not required as if there was an issue with having the GFI protection.


A properly operating appliance should not be tripping a GFI, whether it is required or not.
Reply With Quote
  #13  
Old 2/10/12, 2:38 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

Very true and you are right. Problem is it can be shut off by anyone and then your Freezer goes off or Fridge. Even if there is a problem with the GFCI there is no guarantee that people will now it is supplying power to the Freezer or Fridge or that it has tripped.
Even a HI can trip the GFCI and be responsible for all the freezer meat. If it is required for Freezers or the Fridge I would question this with AHJ.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/10/12, 2:55 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Appliances connected to GFCI

Has there been anyone killed by Freezer?
Has there been any fires by Freezer or fridge not on GFCI?
What is the statistics for those that have lost food because of GFCI plugged into Freezer or Fridge.
They should also have small warning beeps installed when not functioning properly just like a smoke detectors.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 2/10/12 at 3:02 PM..
Reply With Quote
  #15  
Old 2/10/12, 3:36 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Appliances connected to GFCI

The codes are not about the safety of a freezer of meat or a fridge worth of leftovers. It is about life safety. I don't know the statistics about the fires, shocks etc.

There are GFIs with power loss alarms built-in.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two appliances connected into single vent mpulka Inspecting HVAC Systems 8 2/17/10 6:18 AM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM