Default Is this an approved installation?

Main lugs jumpered and receptacle installed on side of panel (non-GFCI in unfinished basement...)
approved-installation-pict2044.jpg

approved-installation-pict2046.jpg

approved-installation-pict2049.jpg




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #2  
Old 5/18/07, 10:41 PM
Jay Schwartz's Avatar
Jay Schwartz Jay Schwartz is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pembroke Pines, FL
Posts: 593
Default Re: Is this an approved installation?

William:

Based on the color of the receptacle cover, it appears this may have been done back in the 70's. It was a common practice that is no longer allowed. Recommend a repair be made by a licensed qualified electrical contractor.



Jay Schwartz

Coast To Coast Home Services, Inc
Your Florida Home Inspection Company TM
Corporate Office: 954-673-3479
Naples Office: 239-298-4396
1-877-79-Windstorm

www.CoastToCoastHomeServices.com
www.SaveOnWindStorm.com

South Florida Home Inspectors Association

Southeast Florida NACHI Chapter - VP
Reply With Quote
  #3  
Old 5/19/07, 10:11 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Looks like a 3 phase panel being used on a single phase system.
Reply With Quote
  #4  
Old 5/19/07, 10:29 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by jschwartz1
Based on the color of the receptacle cover, it appears this may have been done back in the 70's. It was a common practice that is no longer allowed.
What do you base that statement on? It's less commonly done nowadays, but you'd be hard-pressed to find a prohibition against it.

With regard to the pictures in total, it is a 3-phase panel, with a couple phases jumpered to make it a single phase panel. Non conventional, but okay. The mechanical lug reducing adaptors used on the jumper are properly employed. The installer did have his head in the game on that one. The double tap appears to be old type TW insulated wire (really fat insulation), so the wire gauge may be okay for double tapping a square d breaker. You'd have to double check that. The backfed main doesn't appear to have a hold-down clip, but this may have been installed when that was not a requirement.

Last edited by Marc D. Shunk; 5/19/07 at 10:34 AM..
Reply With Quote
  #5  
Old 5/19/07, 10:40 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Is this an approved installation?

Is that jumper large enough?

These are items I don't normally see (back fed main) and just appeared odd to me...

Thanks for your reply Marc




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #6  
Old 5/19/07, 10:47 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by wwarner
Is that jumper large enough?
I don't know. You havn't given any information about the jumper yet, or the service size. The service entrance conductors appear to be aluminium with XHHW or RHH insulation, and the jumper appears to be coppery with THHN or THW insulation, so that would account for some disparity in size. Got any more information for a more educated guess about the jumper?

It's probably not a shame for you to call this all out, since it is a weird install that you're likely to never see again. Probably okay, but weird just the same.
Reply With Quote
  #7  
Old 5/19/07, 10:48 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Is this an approved installation?

It would be proper to recommend GFCI protection for that recepatcle when the panel is located hanging from a joist in an unfinished basement. Correct?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #8  
Old 5/19/07, 10:53 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Is this an approved installation?

Quote:
Originally Posted by Marc D. Shunk
I don't know. You havn't given any information about the jumper yet, or the service size. The service entrance conductors appear to be aluminium with XHHW or RHH insulation, and the jumper appears to be coppery with THHN or THW insulation, so that would account for some disparity in size. Got any more information for a more educated guess about the jumper?

It's probably not a shame for you to call this all out, since it is a weird install that you're likely to never see again. Probably okay, but weird just the same.
200A meter box, 100 amp SEC (from meter), 100A main breaker, ... jumper appeared to be 6 gauge copper




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #9  
Old 5/19/07, 10:53 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Is this an approved installation?

Marc,

This does look to be a 3-phase panel "converted" for 120/240 use.
It looks like the left hand phase A lug has been removed and the 3 polebreaker is feeding bus A and C with bus B fed by the white jumper.

Is this a permitted application?
Reply With Quote
  #10  
Old 5/19/07, 10:55 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by mlarson
Is this a permitted application?
It's not prohibited, and that's all you can say. The jumper size may be an issue, now that we know it's probably 6 gauge copper.
Reply With Quote
  #11  
Old 5/19/07, 11:05 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by wwarner
200A meter box, 100 amp SEC (from meter), 100A main breaker, ... jumper appeared to be 6 gauge copper
Is it definitely a 200A meter pan, or just a 200CL meter?





I must say, I have seen this done (3-phase jumped to single phase) a few times but I do not like it. Someone went through some work to convert an old 3-phase panel when they could have gone out and gotten the correct single phase main breaker panel and done a MUCH neater job.
This is what happens when your brother in-law gives you old surplus material he got from the plant.

As marc said though, there is nothing specifically prohibiting it.
Reply With Quote
  #12  
Old 5/19/07, 11:15 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by Speedy Petey
This is what happens when your brother in-law gives you old surplus material he got from the plant.
.
Yes, I think it would be fair to say that this is probably along the lines of what happened here.
Reply With Quote
  #13  
Old 5/19/07, 11:45 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Is this an approved installation?

Quote:
Originally Posted by Speedy Petey
Is it definitely a 200A meter pan, or just a 200CL meter?





I must say, I have seen this done (3-phase jumped to single phase) a few times but I do not like it. Someone went through some work to convert an old 3-phase panel when they could have gone out and gotten the correct single phase main breaker panel and done a MUCH neater job.
This is what happens when your brother in-law gives you old surplus material he got from the plant.

As marc said though, there is nothing specifically prohibiting it.
Yes it was definately a 200A meter pan (older)

I figured it was a friend of a friend or relative install since there were no approval tags and the house is 107 years old. That's what threw me since it was an odd install (and I didn't much like it either) but nothing really glaring about being wrong except the bonded sub in the garage and the possible size of that jumper.

Thanks for all your input.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...

Last edited by wwarner; 5/19/07 at 11:49 AM..
Reply With Quote
  #14  
Old 5/19/07, 11:54 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Is this an approved installation?

Quote:
Originally Posted by jschwartz1
William:

Based on the color of the receptacle cover, it appears this may have been done back in the 70's. It was a common practice that is no longer allowed. Recommend a repair be made by a licensed qualified electrical contractor.
I can still find some of those brown bakolite (sp?) covers around here at hardware stores. So although yes it may indicate an older install, I wouldn't put my money on it based on the receptacle cover.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #15  
Old 5/19/07, 12:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this an approved installation?

Quote:
Originally Posted by wwarner
I figured it was a friend of a friend or relative install since there were no approval tags and the house is 107 years old. That's what threw me since it was an odd install (and I didn't much like it either) but nothing really glaring about being wrong except the bonded sub in the garage and the possible size of that jumper.
It sounds like your gut feelings were correct. Good job.

I'm an electrician who often gets charged with fixing items that home inspectors find that need correction. I wouldn't hold it against any home inspector who flagged a really weird installation for evaluation by an electrician. In fact, I'd encourage you to do so in really odd cases, such as this one is. I just tire of the HI's who constantly flag things that are absolutely proper in anyone's book, such as double taps on Square D 15, 20 and 30 amp QO breakers. There's one inspector in my area that suggests an electrician evaluate every 2-prong receptacle he comes across. That's costing a lot of people a lot of money.

Last edited by Marc D. Shunk; 5/19/07 at 12:35 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
6 Hours Home Inspection CE Credit New York Approved bmerrell Inspection Education & Training 0 9/20/07 7:13 PM
NYS Requires Modules, Not Sections bmerrell Inspection Education & Training 14 2/7/07 11:21 AM


All times are GMT -4. The time now is 5:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts