Default Arc-Fault breaker

I recently wired a bedroom addition which is being fed from an arc-fault breaker (square d). The breaker trips every three of four days. Checked all connections made sure they were tight. Checked to see if any neutrals were in contact with a ground or box (apparently that will make an arc-fault trip intermittently).
Called Schnieder electric to find out if breaker was faulty it wasn't (was a recall for breakers back in 2004) they didn't have any suggestions. Finally changed breaker. Still trips. I am wondering if this remote control skylight window that opens and has a blind inside of the window has anything to do with it. It has a transformer inside of it.
As well there is a ceiling fan that is remote control. Would the frequencies from these controllers set it off even when they are not operating. The arc-fault has tripped in the middle of the night twice know with nothing on. Just wondering if anybody had any suggestions. Thanks in advance for your help.
Reply With Quote
  #2  
Old 1/29/09, 12:49 PM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 55
Default Re: Arc-Fault breaker

Mark,
I would try to isolate the problem. Disconnect half the circuit at the midway receptacle and see if it trips if it doesn't trip you will know its after the disconnected receptacle If it does trip its before. Then keep doing the same thing until you isolate the area. If had to guess I would think a damaged wire such as a staple driven to hard. Just a guess.
Reply With Quote
  #3  
Old 1/29/09, 10:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Arc-Fault breaker

Could very well be a problem in the WALL that you can't see as that is the reason for the expanded growth of the AFCI technology. If you have tried multiple AFCI's and still have the problem then I can say without a doubt it is either in your wiring or problem in the wall and not the AFCI breaker.

If you happen to own a SureTest their are thing you can do to see if you are having an issue. Since it is your property and afforded the time to check it I guess I would say remove your devices and leave the luminaries....see if that solves it then you narrow it to the receptacles....if they still trip remove on luminaire at a time and see if that solves it.......

Yes....Case to neutral connections in boxes will cause the AFCI to trip but usually much faster than HOURS.....at all else contact a local electrician to come and do some trouble shooting.



Paul W. Abernathy
Reply With Quote
  #4  
Old 1/30/09, 12:17 AM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Arc-Fault breaker

Paul, I'm curious...

Our local AHJ says that luminaires or ceiling fans cannot be wired into the AFCIs. Therefore, only the receptacles. They claim the fans cause them to trip. Any truth to that?



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #5  
Old 1/30/09, 12:28 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Arc-Fault breaker

Quote:
Originally Posted by bthompson1 View Post
Paul, I'm curious...

Our local AHJ says that luminaires or ceiling fans cannot be wired into the AFCIs. Therefore, only the receptacles. They claim the fans cause them to trip. Any truth to that?
Your AHJ is disregarding the NEC and voiding the entire reason for AFCIs.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 1/30/09, 12:53 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Arc-Fault breaker

I agree with Joe's opinion here. The NEC says the following ( 2005 NEC Version )


(B) Dwelling Unit Bedrooms.
All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed
in dwelling unit bedrooms shall be protected by a
listed arc-fault circuit interrupter, combination type installed
to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to
meet the requirements of 210.12(B) until January 1, 2008.

Definition of outlets:

Outlet.


A point on the wiring system at which current is
taken to supply utilization equipment.

Definition of utilization equipment :

Utilization Equipment.


Equipment that utilizes electric
energy for electronic, electromechanical, chemical, heating,
lighting, or similar purposes.

So.....clearly the local AHJ is incorrect an ruling on their own beliefs. I believe quite a few AHJ's believe this and I happen to disagree with them as to me one life possibly saves is very important.

While their is a history of some AFCI's having issues on some motor loads, I dont believe it is wide spread and usually has some underlining issue to which is always blamed on something....fact is AFCI's are better today than they are just a year ago.

I encourage those AHJ's who know of the known issues of maybe a certain fan or product to contact the manufacturers like eaton or schneider so they can add the waveform issue into the programing....but it does not discount the value of AFCI's.




Paul W. Abernathy
Reply With Quote
  #7  
Old 1/30/09, 8:56 AM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc-Fault breaker

Thank you for the input. I will start isolating devices and see what happens.

Mark
Reply With Quote
  #8  
Old 1/30/09, 5:12 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc-Fault breaker

If the AFCI trips, it did its job. It can often be unclear to the lay person what the reason was. A megohm meter normally makes short work of rooting out the trouble.
Reply With Quote
  #9  
Old 1/30/09, 7:28 PM
jallcroft jallcroft is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Springfield, VA
Posts: 65
Default Re: Arc-Fault breaker

Here’s some info…
First…
http://www.thecircuitdetective.com/afci_circuit_breakers.htm
Which then links to…
http://www.thecircuitdetective.com/treeshort.htm
Reply With Quote
  #10  
Old 2/4/09, 8:06 PM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc-Fault breaker

Hello

Replaced with new afci breaker hasn't tripped for 5 days now.

So I guess it was the breaker all along.

Thanks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Breaker Question rsole Electrical Inspections 6 11/23/08 9:57 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM