  #1  
Old 4/13/11, 8:48 AM
Michael LaCroix Michael LaCroix is offline
New User
 
Join Date: Apr 2011
Posts: 1
Please Note: Michael LaCroix is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Arc fault circuit interrupters

Do arc fault circuit interrupter cause interferance with electronic equipment?
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/15/11, 9:41 AM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by Michael LaCroix View Post
Do arc fault circuit interrupter cause interferance with electronic equipment?
No they do not.

It is also worth noting that under the current NEC newly constructed homes will be required too have arc fault protection at all outlets that are within 60" of the floor and that are not required to be GFCI protected



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #3  
Old 4/15/11, 3:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by mtyson View Post
No they do not.

It is also worth noting that under the current NEC newly constructed homes will be required too have arc fault protection at all outlets that are within 60" of the floor and that are not required to be GFCI protected
Where are you getting this information? This is not in the NEC.
Reply With Quote
  #4  
Old 4/15/11, 3:58 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc fault circuit interrupters

I think that is just a very poor paraphrase of the 210 requirements. It also does not follow the NEC definition of outlets. Using the 5' distance no ceiling lighting or smokes would need to be AFCI protected.
Reply With Quote
  #5  
Old 4/15/11, 5:24 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by Robert Meier View Post
Where are you getting this information? This is not in the NEC.
As of January 2008 only "combination type" AFCIs will meet the NEC requirement. The 2008 NEC requires the installation of combination-type AFCIs in all 15 and 20 ampere residential circuits with the exception of laundries, kitchens, bathrooms, garages and unfinished basements.



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #6  
Old 4/15/11, 5:47 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by Jim Port View Post
I think that is just a very poor paraphrase of the 210 requirements. It also does not follow the NEC definition of outlets. Using the 5' distance no ceiling lighting or smokes would need to be AFCI protected.
Your are correct a poor paraphrase. I should have said outlets that are 60" above the floor need not be a combination AFCI (tamper proof), but are still required too be AFCI protected



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #7  
Old 4/15/11, 6:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc fault circuit interrupters

Tamper proof receptacles have a shutter mechanism to prevent items like keys or pins from being inserted into the device and preventing shocks. Tamper proof has nothing to do with AFCI protection and can be used on regular circuits without AFCI protection.

It would also help if you would review the NEC definition of outlet and receptacle. They are not interchangeable.
Reply With Quote
  #8  
Old 4/15/11, 7:54 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by mtyson View Post
Your are correct a poor paraphrase. I should have said outlets that are 60" above the floor need not be a combination AFCI (tamper proof), but are still required too be AFCI protected
The tamper resistant changes in the 2011 NEC affect receptacles above 66" not 60".

Quote:
406.12 Tamper-Resistant Receptacles in Dwelling Units.
In all areas specified in 210.52, all nonlocking-type
125-volt, 15- and 20-ampere receptacles shall be listed
tamper-resistant receptacles.
Exception: Receptacles in the following locations shall
not be required to be tamper-resistant:
(1) Receptacles located more than 1.7 m (5 1⁄2 ft) above the
floor.
Informational Note Figure 406.10(B)(4) One Example of a
Symbol Used to Identify the Termination Point for an Equipment
Grounding Conductor.
(2) Receptacles that are part of a luminaire or appliance.
(3) A single receptacle or a duplex receptacle for two appliances
located within dedicated space for each appliance
that, in normal use, is not easily moved from one
place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(.
(4) Nongrounding receptacles used
Reply With Quote
  #9  
Old 4/15/11, 11:16 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Arc fault circuit interrupters

http://www.nachi.org/arc-fault-circuit-interrupters.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #10  
Old 4/16/11, 7:58 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc fault circuit interrupters

Quote:
Originally Posted by gromicko View Post
Nice Article. I would re-examine a few things in this paragraph:

Quote:
Arc Faults vs. Ground Faults

It is important to distinguish AFCI devices from Ground Fault Circuit Interrupter (GFCI) devices. GFCIs detect ground faults, which occur when current leaks from a hot (ungrounded) conductor to a grounded object as a result of a short-circuit. This situation can be hazardous when a person unintentionally becomes the current’s path to the ground. GFCIs function by constantly monitoring the current flow between hot and neutral (grounding) conductors, and activate when they sense a difference of 5 milliamps or more. Thus, GFCIs are intended to prevent personal injury due to electric shock, while AFCIs prevent personal injury and property damage due to structure fires.
The words short-circuit should be replaced with ground fault. The NEC has added a definition in the 2011 to clarify the difference.

The word (grounding) should be replaced with grounded.


Quote:
Article 100:
Ground Fault. An unintentional, electrically conducting
connection between an ungrounded conductor of an electrical
circuit and the normally non–current-carrying conductors,
metallic enclosures, metallic raceways, metallic equipment,
or earth.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM


All times are GMT -4. The time now is 5:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts