This is a question for someone above my paygrade. New construction mega homes. Arc fault protection on all outlets in bedrooms EXCEPT for the GFI protected outlets at the wet bar. It is definitely considered a bedroom outlet, but not arc fault protected.
I have not contacted the county yet, all the home in this development are wired like this. Any thoughts??? Anatol |
In some open floor plan homes, it can be hard to tell when one "room" stops and another "room" starts. This is normally delineated during plan review. That said, this doesn't seem to be the case in your situation. You have a wet bar in a master bedroom, which is a reasonably common feature in the luxury home. If that wet bar is clearly IN the master bedroom, and not in some sort of pub room of its own, it certainly needs AFCI protection in addition to the GFCI protection that you say already exists.
This also comes up when you have bathroom type setups in bedrooms. You AFCI the branch circuit and GFCI the sink counter receptacles on that circuit.
And once a door is introduced this would then be considered a separate room, we refer to them as bathrooms and NO AFCI required, yet, at least around here. ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
I agree that if the bathroom is in a seperate room that is accessed off the bedroom only, that it does not require AFCI protection. The notable exception is Washington State. |
The "bathroom" is really the "basin" with any other qualifying fixtures. If you had a tub and a sink you have a bathroom. The toilet is usually in a separate "water closet" in these big homes, even if it is in the giant bathroom, separate from the bedroom.
The question starts when you just have the makeup counter with a sink and no other "bathroom fixture". Since it is not really defined it will be up to the AHJ whether this is a "wet bar". I say any counter top with a sink is a wet bar |
In 2008 it is a distinction without a difference. The requirments still add
I am waiting for an answer from AA county. I'll post the response.
Thanks for the discussion. Anatol |
The official word from AA County is:
>>> Carmine Cianchetta 4/2/2007 8:00 AM >>> All outlets in a bedroom are to be AFCI protected. This would include the GFCI protected outlets at or within 6' of a wetbar. Anatol |
rshuey is a non-member guest and is in no way affiliated with InterNACHI or its members.
AA county is getting ready for 2008, thats what it will read in the NEC then, "all branch circuits feeding the outlets in bedrooms" remember, they say outlets, not receptacles...
Actually....Russell if you are speaking of the 2008 NEC in regards to 210.12, the it will read this as it stands right now.
210.12 Arc-Fault Circuit-Interrupter Protection. (A) Definition: Arc-Fault Circuit Interrupter (AFCI). An arc-fault circuit interrupter is a device intended to provide protection from the effects of arc faults by recognizing characteristics unique to arcing and by functioning to deenergize the circuit when an arc fault is detected. [ROP 2–119] (B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits installed in dwelling units shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit. [ROP 2–105, 2–142, 2–111] FPN No. 1: For information on types of arc-fault circuit interrupters, see UL 1699-1999, Standard for Arc-Fault Circuit Interrupters. FPN No. 2: See 11.6.3(5) of NFPA 72®-2007, National Fire Alarm Code® for information related to secondary power supply requirements for smoke alarms installed in dwelling units. [ROP 2–118a] FPN No. 3: See 760.41 and 760.121 for power supply requirements for fire alarm systems. [ROP 2–143] Exception: The location of the arc-fault circuit interrupter shall be permitted to be at other than the origination of the branch circuit where the arc-fault circuit interrupter is installed within 1.8 m (6 ft) of the branch circuit overcurrent device as measured along the branch circuit conductors. [ROP 2–147, 2–137] Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| Arc Fault Breakers | pdoane | Electrical Inspections | 21 | 6/24/07 10:08 PM |
| Can an AFCI offer GFCI protection | gbeaumont | Electrical Inspections | 19 | 7/7/06 12:45 AM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical Inspections | 5 | 3/21/06 9:48 AM |