  #1  
Old 3/24/07, 6:38 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Arc Fault combo

This is a question for someone above my paygrade. New construction mega homes. Arc fault protection on all outlets in bedrooms EXCEPT for the GFI protected outlets at the wet bar. It is definitely considered a bedroom outlet, but not arc fault protected.
I have not contacted the county yet, all the home in this development are wired like this. Any thoughts???

Anatol
Reply With Quote
  #2  
Old 3/24/07, 7:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

In some open floor plan homes, it can be hard to tell when one "room" stops and another "room" starts. This is normally delineated during plan review. That said, this doesn't seem to be the case in your situation. You have a wet bar in a master bedroom, which is a reasonably common feature in the luxury home. If that wet bar is clearly IN the master bedroom, and not in some sort of pub room of its own, it certainly needs AFCI protection in addition to the GFCI protection that you say already exists.
Reply With Quote
  #3  
Old 3/25/07, 3:39 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

This also comes up when you have bathroom type setups in bedrooms. You AFCI the branch circuit and GFCI the sink counter receptacles on that circuit.
Reply With Quote
  #4  
Old 3/25/07, 9:25 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Arc Fault combo

Quote:
Originally Posted by Greg Fretwell
This also comes up when you have bathroom type setups in bedrooms. You AFCI the branch circuit and GFCI the sink counter receptacles on that circuit.
I was OK with the wet bar in MB but the vision from my bed of the girls from the night before doing their morning "duty" is a little much. I hope they have doors on these set-ups.

And once a door is introduced this would then be considered a separate room, we refer to them as bathrooms and NO AFCI required, yet, at least around here.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #5  
Old 3/25/07, 10:49 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Arc Fault combo

Quote:
Originally Posted by badair
And once a door is introduced this would then be considered a separate room, we refer to them as bathrooms and NO AFCI required, yet, at least around here.
It is the same here.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #6  
Old 3/25/07, 11:10 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

Quote:
Originally Posted by badair
I was OK with the wet bar in MB but the vision from my bed of the girls from the night before doing their morning "duty" is a little much. I hope they have doors on these set-ups.

And once a door is introduced this would then be considered a separate room, we refer to them as bathrooms and NO AFCI required, yet, at least around here.
What he's referring to is some of these master suites that have a vanity/makeup area in the actual bedroom that includes a sink. I can clearly picture a few that have had the whirlpool tub in either a raised or sunken area of the master suite. When such bathroomesque type fixtures are located in the master bedroom, the toilet is nearly always in a seperate "toilet room" by itself, or behind a half wall of sorts.

I agree that if the bathroom is in a seperate room that is accessed off the bedroom only, that it does not require AFCI protection. The notable exception is Washington State.
Reply With Quote
  #7  
Old 3/25/07, 1:59 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

The "bathroom" is really the "basin" with any other qualifying fixtures. If you had a tub and a sink you have a bathroom. The toilet is usually in a separate "water closet" in these big homes, even if it is in the giant bathroom, separate from the bedroom.
The question starts when you just have the makeup counter with a sink and no other "bathroom fixture". Since it is not really defined it will be up to the AHJ whether this is a "wet bar". I say any counter top with a sink is a wet bar
Reply With Quote
  #8  
Old 3/25/07, 2:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

Quote:
Originally Posted by Greg Fretwell
The question starts when you just have the makeup counter with a sink and no other "bathroom fixture". Since it is not really defined it will be up to the AHJ whether this is a "wet bar". I say any counter top with a sink is a wet bar
I guess, but making that determination is what causes you to GFCI protect or not. The thread is about AFCI protection. Any 120 volt stuff in the bedroom needs AFCI protection, without regard to how strange, weird, or obscure that stuff might be.
Reply With Quote
  #9  
Old 3/25/07, 7:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

In 2008 it is a distinction without a difference. The requirments still add

Last edited by Greg Fretwell; 3/25/07 at 8:00 PM..
Reply With Quote
  #10  
Old 3/26/07, 9:11 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

I am waiting for an answer from AA county. I'll post the response.
Thanks for the discussion.

Anatol
Reply With Quote
  #11  
Old 4/2/07, 1:57 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

The official word from AA County is:


>>> Carmine Cianchetta 4/2/2007 8:00 AM >>>
All outlets in a bedroom are to be AFCI protected. This would include the GFCI protected outlets at or within 6' of a wetbar.

Anatol
Reply With Quote
  #12  
Old 4/2/07, 7:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

Quote:
Originally Posted by apolillo
The official word from AA County is:


>>> Carmine Cianchetta 4/2/2007 8:00 AM >>>
All outlets in a bedroom are to be AFCI protected. This would include the GFCI protected outlets at or within 6' of a wetbar.

Anatol
I absolutely agree with that ruling from Anne Arundel County. .
Reply With Quote
  #13  
Old 4/3/07, 11:10 PM
rshuey rshuey is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Mar 2007
Posts: 199
Please Note: rshuey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Arc Fault combo

AA county is getting ready for 2008, thats what it will read in the NEC then, "all branch circuits feeding the outlets in bedrooms" remember, they say outlets, not receptacles...
Reply With Quote
  #14  
Old 4/4/07, 9:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Arc Fault combo

Actually....Russell if you are speaking of the 2008 NEC in regards to 210.12, the it will read this as it stands right now.


210.12 Arc-Fault Circuit-Interrupter Protection.

(A) Definition: Arc-Fault Circuit Interrupter (AFCI).


An arc-fault circuit interrupter is a device intended to provide
protection from the effects of arc faults by recognizing
characteristics unique to arcing and by functioning to deenergize
the circuit when an arc fault is detected.
[ROP
2–119]
(B) Dwelling Units.
All 120-volt, single phase, 15- and
20-ampere branch circuits installed in dwelling units shall
be protected by a listed arc-fault circuit interrupter, combination
type installed to provide protection of the branch
circuit.
[ROP 2–105, 2–142, 2–111]


FPN No. 1: For information on types of arc-fault circuit
interrupters, see UL 1699-1999,
Standard for Arc-Fault
Circuit Interrupters
.
FPN No. 2: See 11.6.3(5) of
NFPA 72®-2007, National
Fire Alarm Code
® for information related to secondary
power supply requirements for smoke alarms installed in
dwelling units.
[ROP 2–118a]


FPN No. 3: See 760.41 and 760.121 for power supply
requirements for fire alarm systems.
[ROP 2–143]


Exception: The location of the arc-fault circuit interrupter

shall be permitted to be at other than the origination of the
branch circuit where the arc-fault circuit interrupter is installed
within 1.8 m (6 ft) of the branch circuit overcurrent
device as measured along the branch circuit conductors.


[ROP 2–147, 2–137]




Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Arc Fault Breakers pdoane Electrical 21 6/24/07 10:08 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
Can an AFCI offer GFCI protection gbeaumont Electrical 19 7/7/06 12:45 AM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 8:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts