Question ARC Faults versus GFCI

I inspected a house today that had 2 water feature pumps (full size pool pumps) wired to ARC fault circuit breakers in the service panel. There were no GFCI's at the pump control timers and, of course, the pumps were not bonded. The pumps/filters/piping is 30' from the nearest water feature. Can ARC's be used in this situation?
Reply With Quote
Need a home inspection in Texas? Check out InterNACHI's listing of Texas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/9/10, 5:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: ARC Faults versus GFCI

NO way unless they happen to be combo devices and I don't know if they are available yet.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 2/9/10, 7:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: ARC Faults versus GFCI

Quote:
Originally Posted by jhaubrich View Post
I inspected a house today that had 2 water feature pumps (full size pool pumps) wired to ARC fault circuit breakers in the service panel. There were no GFCI's at the pump control timers and, of course, the pumps were not bonded. The pumps/filters/piping is 30' from the nearest water feature. Can ARC's be used in this situation?
Hate to ask, but are you sure they were AFCI ?
Reply With Quote
  #4  
Old 2/9/10, 7:08 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: ARC Faults versus GFCI

Were they hardwired or plugged into receptacles? If they were plugged in, did you test the receptacles?

My pond pumps and fountains are hardwired and run off a GFCI breaker in the panel.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #5  
Old 2/12/10, 5:42 PM
Rick Marton Rick Marton is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Paramus, New Jersey
Posts: 58
Default Re: ARC Faults versus GFCI

There should be no arc faults in any outdoor location. Only GFI's are used for outdoor locations. Rick
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 5:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts