Default Back-up Generator Installation

I wrote up three "double-taps" the other day on a home that had a whole house back-up generator. There were two 15amp and one 20amp circuit breakers that were double tapped.

My question is this: Are these double taps allowed if the second circuit is tied to the back-up generator circuit breaker panel?

Kevin
Reply With Quote
  #2  
Old 10/12/07, 12:17 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,606
Default Re: Back-up Generator Installation

Kevin,
Was there a transfer switch installed?



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 10/12/07, 12:22 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Back-up Generator Installation

Quote:
Originally Posted by bgraham
Kevin,
Was there a transfer switch installed?
Yes, there was a transfer switch, but I am not certian if is was an automatic or manual switch.
Attached Thumbnails
back-up-generator-installation-cimg1749.jpg  
Reply With Quote
  #4  
Old 10/12/07, 12:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Back-up Generator Installation

Remember...unless the "terminal" is listed for more than a single conductor ( ie: QO or CH Brands of 30A or less ) then it is simply incorrect.

Now lets say it is a generac system with its own seperate panel and it connections via the conduit with the massive WAD of conductors....the proper method would be to splice conductors....NOT double up on breakers...

I wont go deeper than that....if you would like to know more details on generators......we can talk...but the main issue where I gather in your question is is it allowed to double tap a breaker......Not unless the terminal is listed for it.......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 10/12/07, 12:32 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,361
Default Re: Back-up Generator Installation

If what I am understanding is they are really using the breaker as a junction box, if the generator comes on automatically if there is a power loss, it could be a problem. But it is not a double load, as we are used to seeing but rather a double line.
Reply With Quote
  #6  
Old 10/12/07, 12:51 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Back-up Generator Installation

Quote:
Originally Posted by pabernathy
Remember...unless the "terminal" is listed for more than a single conductor ( ie: QO or CH Brands of 30A or less ) then it is simply incorrect.

Now lets say it is a generac system with its own seperate panel and it connections via the conduit with the massive WAD of conductors....the proper method would be to splice conductors....NOT double up on breakers...

I wont go deeper than that....if you would like to know more details on generators......we can talk...but the main issue where I gather in your question is is it allowed to double tap a breaker......Not unless the terminal is listed for it.......
Thanks, Paul!

That answers my question.

Kevin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CMI imposter? jbraun CMI/MICB Discussion 118 11/26/07 5:55 PM
SERVARE Online Back UP-Preferred NACHI Pricing dvondrak Misc. Discussion 0 6/13/06 10:48 AM


All times are GMT -4. The time now is 2:48 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts