Exclamation bad panel location

how close can a main panel be to a pressurized water source? The panel is where the service comes in but it is behind the dryer unit which is if cource next to the washer unit.
Reply With Quote
  #2  
Old 9/29/07, 12:23 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: bad panel location

Patrick,

there is no restriction as to proximity to the water main, however any service panel should have unrestricted access in an area 30 inches wide 6'8" of headroom and 36' of clear working space in front.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 9/29/07, 11:16 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: bad panel location

perhaps this will help
Attached Thumbnails
bad-panel-location-electrical-228-.jpg.JPG
Views:	47
Size:	21.6 KB
ID:	14816  
Reply With Quote
  #4  
Old 9/30/07, 9:34 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bad panel location

That's a nice drawing William.
Remember, the 30" wide space does not have to be centered on the panel. The panel can be anywhere in that 30" space.

And has been said, there are NO restrictions with regard to plumbing and piping other than standard clearances to anything else.
Water has nothing to do with it.
Reply With Quote
  #5  
Old 9/30/07, 12:46 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bad panel location

The piping just can't be in dedicated space or above the dedicated space ... "foreign systems".
I also understand that in old houses this is a lot easier said than done. It is a fairly new rule and in the olden days plumbers encroached on working space all the time.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Main Panel location dmacy Electrical 5 12/6/06 7:32 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 12:47 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts