how close can a main panel be to a pressurized water source? The panel is where the service comes in but it is behind the dryer unit which is if cource next to the washer unit.
|
|
#2
|
||||
|
||||
|
Patrick,
there is no restriction as to proximity to the water main, however any service panel should have unrestricted access in an area 30 inches wide 6'8" of headroom and 36' of clear working space in front. Regards Gerry Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience. Adam Smith (1723-1790) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106
|
|
#3
|
|||
|
|||
|
perhaps this will help
|
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's a nice drawing William.
Remember, the 30" wide space does not have to be centered on the panel. The panel can be anywhere in that 30" space. And has been said, there are NO restrictions with regard to plumbing and piping other than standard clearances to anything else. Water has nothing to do with it. |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The piping just can't be in dedicated space or above the dedicated space ... "foreign systems".
I also understand that in old houses this is a lot easier said than done. It is a fairly new rule and in the olden days plumbers encroached on working space all the time. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical | 44 | 4/18/08 12:43 AM |
| Electrical Safety Foundation International Links | jtedesco1 | Electrical | 5 | 12/8/07 4:10 PM |
| Main Panel location | dmacy | Electrical | 5 | 12/6/06 7:32 PM |
| Panel Inspection Safety | roconnor | Electrical | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |