Default Bare bulbs in the attic ??

Around here is is very common to see a bare-bulb pull chain fixture in the attic. I usually identify it as a hazard and recommend replacement. I know such fixtures are not allowed in closets, but is there a specific prohibition against them in the attic?
Attached Images
File Type: jpg ECI 030.jpg (40.0 KB, 46 views)



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #2  
Old 10/3/08, 12:55 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,797
Dale Duffy .
Default Re: Bare bulbs in the attic ??

They are in every attic I have inspected (homes built probably within the last 10 years), as a matter of fact, required here for new construction, and a receptacle present also if the Air Handler is in the attic.
Reply With Quote
  #3  
Old 10/3/08, 1:01 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,647
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: Bare bulbs in the attic ??

that's all I ever see Frank....and if it's on a pull chain i usually manage to break it....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 10/3/08, 1:18 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: Bare bulbs in the attic ??

Quote:
Originally Posted by dduffy View Post
They are in every attic I have inspected (homes built probably within the last 10 years), as a matter of fact, required here for new construction, and a receptacle present also if the Air Handler is in the attic.
How long has the receptacle requirement been in effect? I see them sometimes, but not always (usually without a cover !!)



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 10/3/08, 1:24 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,797
Dale Duffy .
Default Re: Bare bulbs in the attic ??

Quote:
Originally Posted by fnewman View Post
How long has the receptacle requirement been in effect? I see them sometimes, but not always (usually without a cover !!)
Depends on what version of the building codes your municipality uses, I would need to start my other computer where my codes are downloaded, perhaps someone else could chime in Frank.

But if there is an Air Handler in the attic, it really makes no difference about code whether there is a receptacle and light present, simply recommend they have one installed if the house has the Air Handler in the attic, if not, there really isn't a need for a light or receptacle.
Reply With Quote
  #6  
Old 10/3/08, 1:51 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 6,408
Robert E. Elliott .
Default Re: Bare bulbs in the attic ??

I always recommend (no metal pull chains)
They conduct electricity.
Reply With Quote
  #7  
Old 10/3/08, 1:55 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,322
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Bare bulbs in the attic ??




"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 10/3/08, 2:24 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: Bare bulbs in the attic ??

Never thought about the isolating link, but most around here just have a string below the fixture chain.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #9  
Old 10/3/08, 4:22 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,152
Barry Adair .
Default Re: Bare bulbs in the attic ??

we like to use dinosaurs
Attached Images
File Type: jpg DSC00001.JPG (131.7 KB, 45 views)



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #10  
Old 10/3/08, 5:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bare bulbs in the attic ??

I am not aware of anything that would prohibit the keyless within the attic space.

I guess as an HI the largest concern really needs to be the placment of the bulb itself. If the bulb is in a location that is really...well....subject to someone hitting it when they enter the attic or in a position that makes it really subject to being damaged then I can see where it would make the report as a suggestion. Most certainly.

Now CODE wise I can only think of the following which may reference something for you.

410.5 Luminaires (Fixtures) Near Combustible Material.
Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).

* So a specific location in an attic may come into play.....

410.6 Luminaires (Fixtures) Over Combustible Material.
Lampholders installed over highly combustible material
shall be of the unswitched type. Unless an individual
switch is provided for each luminaire (fixture), lampholders
shall be located at least 2.5 m (8 ft) above the floor or shall
be located or guarded so that the lamps cannot be readily
removed or damaged.

But other than that...I am not aware of anything but if it looks unsafe atleast report it and make them aware of it....then it's there call.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #11  
Old 10/3/08, 5:46 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 6,408
Robert E. Elliott .
Default Re: Bare bulbs in the attic ??

Article 410 Luminaries (Lighting Fixture), Lampholders, and Lamps

Article 410.8 (B) Luminaries (Fixture) Types Permitted. Listed. The following types of light fixtures shall be permitted to be installed in a closet. Closets (Clothes and storage) eight ( square feet (0.74 m²) or larger one of the following type of light fixtures shall be installed:

1. A recessed incandescent fixture with a completely enclosed lamp operated by a wall switch.

2. A surface mounted or recessed fluorescent fixture with a completely enclosed tube(s) operated by a wall switch.

410.8 (C) Luminaries (Fixture) Types Not Permitted. The following fixtures are not permitted:

1. Surface mounted incandescent fixture with enclosed, partially enclosed or open bulbs.
2. Pendant Style
3. Lampholders

Exception:
Walk-in closets of larger area where no storage exists within forty (40) inches (1016 mm) in any direction of a vertical line extending from the floor to ceiling, away from the wall, incandescent fixtures with totally enclosed bulb(s) may be used. Said light fixtures shall be operated by a wall switch.

OOps for closets (but good to read anyway

Last edited by relliott; 10/3/08 at 5:50 PM. Reason: oops
Reply With Quote
  #12  
Old 10/3/08, 7:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,890
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare bulbs in the attic ??

The hazard of a keyless in an attic, if one exists, is the physical placement of the fixture and requisite lamp. If it's right above a scuttle hole, such as you would bump it when you boost yourself up and in, then it's in a bad spot. If it's right in front of your face, or right behind your head at the place you'd normally stand to service an air handler, then it's in a bad spot. I've smashed out a few attic lamps with my head before, and it's never a pleasant situation. It necessarily involves a little bit of scorched hair. Placement of the fixture is the only thing I worry about; ie- whether it's likely to get bumped with someone's head.

Having said that, if you're in an attic that has boxes piled up close to the bare lamp fixture, then you're also looking at a present hazard.
Reply With Quote
  #13  
Old 10/3/08, 8:48 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pace (Pensacola), FL
Posts: 2,971
Doug Edwards,  CMI .
Default Re: Bare bulbs in the attic ??

The Sparkies' already identified the only issue I have with the keyless fixtures. Often, with all the space inside an attic one can place a light fixture someone will place it right at the top of the ladder or hide it behind a truss so the bulb is very close to the roof sheathing. I had such a one in my own house when we bought it so I moved it so it would cast more light and got it out of the way so I would quit breaking the bulbs trying to go in and out of the attic. I got real tired of the piss ant string too so I added a switch just inside the hatch.



Doug Edwards, CMI


"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

John Stuart Mill






Reply With Quote
  #14  
Old 10/3/08, 9:19 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: Bare bulbs in the attic ??

Since most attics I visit don't even have room for a fairly short person to stand up without hitting your head on a rafter, etc., and given that you can purchase a perfectly good enclosed fixture for a few dollars, I will probably continue to recommend replacement without indicating that any specific requirement exists. Thanks to all.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #15  
Old 10/5/08, 10:11 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 566
jkogel is well trusted jkogel is well trusted jkogel is well trusted
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare bulbs in the attic ??

This guy thought the attic was a handy place for a breaker panel. No light. Talk about bumping your head in the dark.

John Kogel
www.allsafehome.ca
Attached Images
File Type: jpg atticpanel.jpg (60.8 KB, 19 views)
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources