Question Bare wire on old dryer or stove circuit: neutral or ground?

In an old 3-hole stove or clothes dryer outlet that has a wire with 2 hots and a bare, stranded wire wrapped around them, is that stranded wire to be treated as a ground wire or a neutral wire if it is wired to a sub-panel with properly separated ground and neutral lugs?

Is this a fine point or can it be a more significant safety issue (backflow of current, etc.)?
Reply With Quote
  #2  
Old 8/26/06, 6:28 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

ground wire
Reply With Quote
  #3  
Old 8/26/06, 6:32 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Royal Oak, MI
Posts: 126
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

Thanks, Charles. That was quick. And was what I thought. But I wasn't sure on account of the presence of clocks, timers, etc. on stoves, which I figured might require 110-120V.
Reply With Quote
  #4  
Old 8/26/06, 6:41 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

I know what you mean about the clocks etc. That is why it is not allowed anymore.
Reply With Quote
  #5  
Old 8/26/06, 7:13 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Royal Oak, MI
Posts: 126
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

So then do the clocks, timers, etc. cause the bare wire to carry current?
Or do are they designed to run on 220-240V, perhaps via a transformer within the appliance?
Reply With Quote
  #6  
Old 8/26/06, 7:21 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

So then do the clocks, timers, etc. cause the bare wire to carry current?
I would expect so----however small. Again that is why it isn't allowed anymore.
Reply With Quote
  #7  
Old 8/26/06, 11:31 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

Sorry guys but this is all wrong.
The braid on old type SEU cable is most definitely a neutral conductor. These are 120/240v circuits, NOT simply 240v. The braid is the neutral and the case of the applaince (ground) was allowed to be bonded to the neutral in older codes, thus eliminating the need for a separate ground to be run.
There is no mandate to require these circuits to be upgraded as existing circuits which were legal when installed are still legal.
Thing is it was never legal to run these types of circuits from sub-panels. They were required to originate from the service equipment.

ANY conductor that carries current is either and ungrounded (hot) conductor, or a grounded (neutral) conductor. NEITHER is a ground (grounding condcutor).
Reply With Quote
  #8  
Old 8/27/06, 11:46 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

250.60 from the pre-96 code said you could use the "groundED" conductor to ground the frame of ranges and dryers. It required that this circuit originate in the service panel and that except for SE cable, the grounded conductor shall be insulated. That is why you frequently saw 10/3-wg romex feeding the 3 prong receptacles. Typically they landed the bare on the backstrap or box and used the white on the receptacle grounded terminal.
Reply With Quote
  #9  
Old 8/28/06, 12:23 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

I still remember using #8al SEU cable for dryers. Very common back then.
Reply With Quote
  #10  
Old 8/28/06, 2:08 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bare wire on old dryer or stove circuit: neutral or ground?

SE was the exception to an insulated grounded conductor but you still couldn't come from a sub with 3 wires.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical 4 8/1/06 10:44 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
Can an AFCI offer GFCI protection gbeaumont Electrical 19 7/7/06 12:45 AM


All times are GMT -4. The time now is 7:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts