Default Bathroom electrical question

Looking for the nec rules on bathroom gfci's

The issue at hand is two baths plus the laundry, bedroom, and some of the living room is tied togeather.. Almost 30 outlets all togeather..

Some clairty please.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/2/11, 4:14 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom electrical question

What is the vintage? The rules concerning bathroom receptacle circuits not being shared started in the 90's.
Reply With Quote
  #3  
Old 2/2/11, 4:15 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Bathroom electrical question

Sean, Code says you have 2 choices for bathrooms.

#1: You can run a single 20amp circuit to feed the outlets (and only the outlets) in all bathrooms. In this case you could use 1 gfci in the first location, and protect the other outlets from it. The downfall to this is that if you trip a gfci in the downstairs, and you are in the upstairs bathroom, you have to run downstair to reset it.

#2: You can run a single 20amp circuit to feed everything in one bathroom only (outlets, lights, fans etc...), and not use that circuit in any other room. Since there is alot more hair dryers, curling irons etc being used these days, it makes more sense to run 1 circuit for each bathroom, and install a gfci in each required location, next to the basin.




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.

Last edited by jkeilson; 2/2/11 at 4:21 PM..
Reply With Quote
  #4  
Old 2/2/11, 4:28 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Bathroom electrical question

House is 2 years old.

James, where in the nec???

Thanks btw




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #5  
Old 2/2/11, 4:45 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom electrical question

Right here:

Quote:
210.11 Branch Circuits Required.
Branch circuits for lighting and for appliances, including motor-operated appliances, shall be provided to supply the loads calculated in accordance with 220.10. In addition, branch circuits shall be provided for specific loads not covered by 220.10 where required elsewhere in this Code and for dwelling unit loads as specified in 210.11(C).
(A) Number of Branch Circuits. The minimum number of branch circuits shall be determined from the total calculated load and the size or rating of the circuits used. In all installations, the number of circuits shall be sufficient to supply the load served. In no case shall the load on any circuit exceed the maximum specified by 220.18.
(B) Load Evenly Proportioned Among Branch Circuits. Where the load is calculated on the basis of volt-amperes per square meter or per square foot, the wiring system up to and including the branch-circuit panelboard(s) shall be provided to serve not less than the calculated load. This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s). Branch-circuit overcurrent devices and circuits shall be required to be installed only to serve the connected load.
(C) Dwelling Units.
(1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
(3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
Reply With Quote
  #6  
Old 2/2/11, 4:51 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Bathroom electrical question

I was looking at 210.8..
Once again thank you Robert!!




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #7  
Old 2/2/11, 4:53 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom electrical question

Quote:
Originally Posted by sfogarty View Post
I was looking at 210.8..
Once again thank you Robert!!

There is a mention of bathrooms in 210.8 since that the section that covers GFCI protection.
Reply With Quote
  #8  
Old 2/2/11, 4:55 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Bathroom electrical question

Quote:
Originally Posted by Robert Meier View Post
There is a mention of bathrooms in 210.8 since that the section that covers GFCI protection.
But not the specific bathroom rule, which is what I was looking for...




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #9  
Old 2/2/11, 5:35 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Bathroom electrical question

IRC code and commentary below.

2009 IRC E3703.3 Laundry circuit. A minimum of one 20-ampere-rated
branch circuit shall be provided for receptacles located in the
laundry area and shall serve only receptacle outlets located in the
laundry area.

Commentary A dedicated branch circuit is required for the laundry
area. This circuit can serve receptacles that, for example,
are used for ironing, clothes washers and gas
dryers.

E3703.4 Bathroom branch circuits. A minimum of one
20-ampere branch circuit shall be provided to supply bathroom
receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single
bathroom, outlets for other equipment within the same bathroom
shall be permitted to be supplied in accordance with
Section E3702.

Commentary This section requires a dedicated branch circuit for the
bathroom receptacle outlet(s). Section E3901.6 provides
rules for the location of the receptacle(s). Two
choices are available for the branch circuit serving the
bathroom(s) in the house.
1. One 20-ampere-rated circuit may serve the required
receptacle(s) in all the bathrooms in the
house. In this case, no other outlets may be
served by this circuit. The bathroom lighting and
any fan or heat lamps would be served by a distinct
general purpose branch circuit.

2. A 20-ampere circuit may serve only one bathroom.
For additional bathrooms in the house,
additional separate circuits would be run. The
one circuit for the single bathroom supplies the
required receptacle(s) and is also permitted to
serve lighting and equipment in the bathroom
such as an exhaust fan and/or heat lamp. Because
this circuit is subject to the provisions of
Section E3702, the load of the other equipment
can be a maximum of 50 percent of the rating of
the branch circuit.
The bathroom receptacle must be Ground Fault Interrupters
(GFCI) protected, but lighting and other
equipment is not required to be GFCI protected unless
otherwise stated as a condition of the listing of a
fixture or equipment. Some electricians supply the
luminaires and fans in a bathroom from a GFCI protected
circuit to provide additional safety for the occupants
who come in contact with the luminaires, fans
and switches.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Quick electrical question. Need fast! wdecker Electrical Inspections 6 3/21/10 10:13 PM
Heat pump & electrical question pjones1 Inspecting HVAC Systems 1 1/19/09 4:01 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM


All times are GMT -4. The time now is 5:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts