Looking for the nec rules on bathroom gfci's
The issue at hand is two baths plus the laundry, bedroom, and some of the living room is tied togeather.. Almost 30 outlets all togeather.. Some clairty please. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
What is the vintage? The rules concerning bathroom receptacle circuits not being shared started in the 90's.
|
|
#3
|
||||
|
||||
|
Sean, Code says you have 2 choices for bathrooms.
#1: You can run a single 20amp circuit to feed the outlets (and only the outlets) in all bathrooms. In this case you could use 1 gfci in the first location, and protect the other outlets from it. The downfall to this is that if you trip a gfci in the downstairs, and you are in the upstairs bathroom, you have to run downstair to reset it. #2: You can run a single 20amp circuit to feed everything in one bathroom only (outlets, lights, fans etc...), and not use that circuit in any other room. Since there is alot more hair dryers, curling irons etc being used these days, it makes more sense to run 1 circuit for each bathroom, and install a gfci in each required location, next to the basin. Maryland Home Inspection Services Inc. www.MarylandHomeInspectionServices.com State of Maryland License# 31141 Virginia License#3380 000468 National Association Of Certified Home Inspectors ID: NACHI10101807 International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919 Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C. Last edited by jkeilson; 2/2/11 at 4:21 PM.. |
|
#4
|
||||
|
||||
|
House is 2 years old.
James, where in the nec??? Thanks btw Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Right here:
Quote:
|
|
#6
|
||||
|
||||
|
I was looking at 210.8..
Once again thank you Robert!! Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is a mention of bathrooms in 210.8 since that the section that covers GFCI protection. |
|
#8
|
||||
|
||||
|
But not the specific bathroom rule, which is what I was looking for...
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#9
|
||||
|
||||
|
IRC code and commentary below.
2009 IRC E3703.3 Laundry circuit. A minimum of one 20-ampere-rated branch circuit shall be provided for receptacles located in the laundry area and shall serve only receptacle outlets located in the laundry area. Commentary A dedicated branch circuit is required for the laundry area. This circuit can serve receptacles that, for example, are used for ironing, clothes washers and gas dryers. E3703.4 Bathroom branch circuits. A minimum of one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets. Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with Section E3702. Commentary This section requires a dedicated branch circuit for the bathroom receptacle outlet(s). Section E3901.6 provides rules for the location of the receptacle(s). Two choices are available for the branch circuit serving the bathroom(s) in the house. 1. One 20-ampere-rated circuit may serve the requiredThe bathroom receptacle must be Ground Fault Interrupters (GFCI) protected, but lighting and other equipment is not required to be GFCI protected unless otherwise stated as a condition of the listing of a fixture or equipment. Some electricians supply the luminaires and fans in a bathroom from a GFCI protected circuit to provide additional safety for the occupants who come in contact with the luminaires, fans and switches. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Quick electrical question. Need fast! | wdecker | Electrical Inspections | 6 | 3/21/10 10:13 PM |
| Heat pump & electrical question | pjones1 | Inspecting HVAC Systems | 1 | 1/19/09 4:01 PM |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical Inspections | 5 | 9/14/08 3:58 PM |