Did a newly-constructed home inspection today. In the master bath, the only outlet is in the middle of the mirror, behind the 2-sink countertop. For some reason, something sticks in my mind about outlets in the mirror... anyone ?
|
| Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
There are rules regarding the location of outlets in relation to the sinks. But nothing prohibits their location in a mirror. It's fairly common.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
||||
|
||||
|
Yep, as long as that Receptacle is within 3' of the basin, GFCI Protected and 20A then no worries.
Paul W. Abernathy,CMI,CEI,CEPE NEC® Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#4
|
|||
|
|||
|
Thanks.
|
![]() |