Default Beam me up Scotty

We have a problem house built in 2008 in the country no AHJ inspection total electrical 5 ton heat pump with 4 15 KW strip heat, 2 electrical cook stoves remote cook top 2 whirlpool tubs a private well for water and Aerobic septic system 3 bathroom exhaust fans with electric heaters and one 50 gallon electrical water heater.
My write up was a little different than what was on the Realtor sheet.

The main panel was 200 amp and had a 100 amp sub feeding the additional panel side by side. As you can see I exceeded the 80% a bit.

I find this a lot but always on a home that has been added on to one or more times and the electrical was not updated. This was my first for a new home the electricians were so proud of their work they signed and dated the inside of the panel. 218 amps sure makes for nice thermal images
Attached Thumbnails
beam-me-up-scotty-28-old-post-rd-enid-3-15-11-033.jpg   beam-me-up-scotty-28-old-post-rd-enid-3-15-11-034.jpg   beam-me-up-scotty-28-old-post-rd-enid-3-15-11-035.jpg   beam-me-up-scotty-28-old-post-rd-enid-3-15-11-036.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/18/11, 4:44 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Wow. How did you manage to get the 218 amp reading, did you turn everything on at once? Looks like the service is too small. I wonder what a load calculation would say about the connected load.
Reply With Quote
  #3  
Old 3/18/11, 7:43 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Beam me up Scotty

I was wondering the same thing.

Charley, did you turn everything on to see that load.?
I think they need a bigger panel Eh!
Reply With Quote
  #4  
Old 3/18/11, 7:47 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Beam me up Scotty

Nice work. I am just starting toread more and understand electrical systems in the residential home.
Good work.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #5  
Old 3/18/11, 7:50 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Beam me up Scotty

Good morning Robert and Ole Charley knows his thingy.
Reply With Quote
  #6  
Old 3/18/11, 8:08 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Are there neutrals going to the ground buss in the subpanel?
Reply With Quote
  #7  
Old 3/18/11, 8:10 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Beam me up Scotty

They are all puting there stickers on the panels. Yes they do make mistakes because business pushes them to the limit. I always have to laugh when I watch "Mike Homes and his teem" rip out and gut the whole basement just because they found something wrong with the panel. He would have fun here. I have found so many wrong problems with new reno's I am just about to explode.
Attached Thumbnails
beam-me-up-scotty-129-taskar-dr-may-17-201043.jpg  



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 3/18/11, 8:12 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by Robert Meier View Post
Wow. How did you manage to get the 218 amp reading, did you turn everything on at once? Looks like the service is too small. I wonder what a load calculation would say about the connected load.

I always use the inhouse appliances and what ever else is available to get a load as I scan thermally all electrical panels. This house just happen to be total electrical got 218 amps without the dishwasher or a dryer the home was vacant



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 3/18/11, 8:16 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by Jim Port View Post
Are there neutrals going to the ground buss in the subpanel?
Nope



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 3/18/11, 8:34 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by Jim Port View Post
Are there neutrals going to the ground buss in the subpanel?
Sorry I answered to quick yes there were neutrals on the ground buss in the sub but not in the main



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 3/18/11, 9:19 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Quote:
Originally Posted by cbottger View Post
Sorry I answered to quick yes there were neutrals on the ground buss in the sub but not in the main
Thanks for the correction. I thought I saw two that are just above the top breakers on the left side. One looks like it comes from the yellow NM with the long sheath at the bottom of the panel.
Reply With Quote
  #12  
Old 3/18/11, 9:21 AM
Marc-Andre Beauchemin's Avatar
Marc-Andre Beauchemin Marc-Andre Beauchemin is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: BROSSARD,Quebec Canada
Posts: 298
Default Re: Beam me up Scotty

Hey Charley,

"218 amps sure makes for nice thermal images"!

Do you have any thermal images of this to show us?

Thank you!

Beauchemin,Marc-Andre
BMAinspection.com
Brossard, Quebec, Canada
Reply With Quote
  #13  
Old 3/18/11, 1:34 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Beam me up Scotty

Morning to you to Marcel. Well afternoon now.
Yes it is very interesting. I find it a help to follow this electrical system chatter.
HVAC AND ELECTRICAL. That's my week areas.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/18/11, 3:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by mbeauchemin View Post
Hey Charley,

"218 amps sure makes for nice thermal images"!

Do you have any thermal images of this to show us?

Thank you!

Beauchemin,Marc-Andre
BMAinspection.com
Brossard, Quebec, Canada
Yes I have will post them later have a report to get out



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 3/18/11, 4:44 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Quote:
Originally Posted by cbottger View Post
I always use the inhouse appliances and what ever else is available to get a load as I scan thermally all electrical panels. This house just happen to be total electrical got 218 amps without the dishwasher or a dryer the home was vacant
So the question is, is the panel a violation or not with a load of 218 amps?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deflected Cantelevered Beam pdickerson Structural Inspections 4 4/3/08 10:16 AM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 10:40 PM
Steel beam bearing 1 1/2" scosta Structural Inspections 17 6/12/06 9:01 PM