Default Re: Beam me up Scotty

While that might be handy to help with an IR scan due to the non-typical usage, it does not represent how the service will typically be used or if it is too small. Kind of like adding up all the breaker handle ratings and saying the service is too small.
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 3/18/11, 5:41 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

My understanding and what I have always gone by is its not allowed to exceed 80% of the rating of the panel period. I load the panels up with what is available knowing perfectly well that it would be very unusual for every appliance in the home to be on at the same time but that should make no difference if the appliance are installed the rating of the panel should allow for them all to be on at the same time. Here are a couple images of the panel before I shut the test down once I saw 218 amps the 200 amp main had got up to 115 degrees before I shut down don't know how high it would have got to If had not shut down when I did
Attached Thumbnails
beam-me-up-scotty-28-old-post-rd-enid-3-15-11-104.jpg   beam-me-up-scotty-28-old-post-rd-enid-3-15-11-111.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #18  
Old 3/18/11, 6:25 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Beam me up Scotty

Quote:
I saw 218 amps at the 200 amp main
Shouldn't this cause the *main* breaker to trip.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #19  
Old 3/18/11, 6:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Quote:
Originally Posted by ccurrins View Post
Shouldn't this cause the *main* breaker to trip.

Eventually it will, maybe. That's likely an inverse-time CB which will trip faster based on a larger amount of overload. More overload faster trip. This is based on the manufactures trip curve. For a 10% overload it may take hours to trip.
Reply With Quote
  #20  
Old 3/18/11, 6:35 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Beam me up Scotty

Quote:
Originally Posted by Robert Meier View Post
Eventually it will, maybe. That's likely an inverse-time CB which will trip faster based on a larger amount of overload. More overload faster trip. This is based on the manufactures trip curve. For a 10% overload it may take hours to trip.
Would that be sufficient to protect circuits from overheating? Or normally would individual circuit breakers trip first, or easier?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #21  
Old 3/18/11, 7:10 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Quote:
Originally Posted by ccurrins View Post
Would that be sufficient to protect circuits from overheating? Or normally would individual circuit breakers trip first, or easier?

In general inverse-time CB's are inherently similar. Smaller branch CB's might have slightly different trip curves based on how the manufacturer designs them when comparing them to say the 200 amp main CB in this case.

An example would be to think about an AC unit that runs at 20 amps. Typically the CB protecting that circuit would be rated for about 35 amps. During start up the starting current could be up to 600% of the running current or about 120 amps. That's certainly well above the 35 amp trip setting on the CB but it doesn't trip. That's because it's inverse-time design allows it to pass a large amount of current for a very short duration of time, enough time for the compressor motor to start. If these breaker were not designed this way then large inrush loads such as motors could never start.
Reply With Quote
  #22  
Old 3/18/11, 8:09 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Here is a double pole breaker on a free standing cook stove from today that I did not like the temp differential between the two legs should have been close to the same temp on both legs. Putting it on the repair list to have the breaker and or circuit checked

BTW I find a ton of kitchen stove breakers just like this one
Attached Thumbnails
beam-me-up-scotty-1505-monument-087.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 3/18/11 at 8:12 PM..
Reply With Quote
  #23  
Old 3/18/11, 8:57 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Beam me up Scotty

Big differential in my opinion.. Nice Mr. Bottger. I have to get a IR camera when my company gets more secure and earnings are dictating upgrades are allowed.
I have looked into pricing and education. Very good findings.
Thanks....... Robert the Canuc.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #24  
Old 3/18/11, 9:25 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Beam me up Scotty

Quote:
Originally Posted by cbottger View Post
Here is a double pole breaker on a free standing cook stove from today that I did not like the temp differential between the two legs should have been close to the same temp on both legs. Putting it on the repair list to have the breaker and or circuit checked

BTW I find a ton of kitchen stove breakers just like this one
I agree that they should be closer in temperature if the loads are the same on each leg but what is a normal temperature? Is the lower one normal?
Reply With Quote
  #25  
Old 3/18/11, 10:24 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by Robert Meier View Post
I agree that they should be closer in temperature if the loads are the same on each leg but what is a normal temperature? Is the lower one normal?
I generally see the temps range between 100 F and 110F really depends on How long I am operating the stove and the length of run. I pay more attention to the un-balanced temp than how high it is until it reaches up in the area of 130 F and again that will depend on the ambient temp at the panel lots of considerations to take in when scanning panels



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #26  
Old 3/18/11, 10:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Beam me up Scotty

Quote:
Originally Posted by ryoung7 View Post
Big differential in my opinion.. Nice Mr. Bottger. I have to get a IR camera when my company gets more secure and earnings are dictating upgrades are allowed.
I have looked into pricing and education. Very good findings.
Thanks....... Robert the Canuc.
Mr Bottger died in 1962 they generally call me Charley



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deflected Cantelevered Beam pdickerson Structural Inspections 4 4/3/08 10:16 AM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 10:40 PM
Steel beam bearing 1 1/2" scosta Structural Inspections 17 6/12/06 9:01 PM


All times are GMT -4. The time now is 5:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts