Default Bedroom w/o grounded outlets

My daugther has a rental where the tennets are looking for some sort of aid for paying rent and the agency that handles that does a inspection of the house. The house was about 90% rewired one of the bedrooms has 2 outlets that are 3 prong but the ground is not there,i checked the the service panel and found the bedroom has the old two wire system to the breakers. What would be the easyist way to correct this problem?
Reply With Quote
Find an InterNACHI certified Maine Home Inspector (and anywhere else in North America)
  #2  
Old 11/18/09, 5:11 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Bedroom w/o grounded outlets

Replace the three prong with two prong receptacles.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 11/18/09, 5:12 PM
rbero rbero is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Green Bay Wi 54304
Posts: 160
Send a message via Yahoo to rbero
Default Re: Bedroom w/o grounded outlets

That was my thought also
Reply With Quote
  #4  
Old 11/18/09, 5:14 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: Bedroom w/o grounded outlets

Fill the receptacle ground with epoxy.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 11/18/09, 5:16 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Bedroom w/o grounded outlets

Quote:
Originally Posted by rbero View Post
My daugther has a rental where the tennets are looking for some sort of aid for paying rent and the agency that handles that does a inspection of the house. The house was about 90% rewired one of the bedrooms has 2 outlets that are 3 prong but the ground is not there,i checked the the service panel and found the bedroom has the old two wire system to the breakers. What would be the easyist way to correct this problem?
The easiest thing (2 prong receptacles are harder to find and expensive.) may be to put a GFCI on the first receptacle on the circuit and label the others "no equipment ground".



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 11/18/09, 5:18 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Bedroom w/o grounded outlets

Quote:
Originally Posted by lkage View Post
The easiest thing (2 prong receptacles are harder to find and expensive.) may be to put a GFCI on the first receptacle on the circuit and label the others "no equipment ground".
Agree, the two prongs are very hard to find.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #7  
Old 11/18/09, 7:40 PM
rbero rbero is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Green Bay Wi 54304
Posts: 160
Send a message via Yahoo to rbero
Default Re: Bedroom w/o grounded outlets

thanks guys i found some 2 pronged outlets at home depot for 1.48 i will install them in the morning
Reply With Quote
  #8  
Old 11/18/09, 8:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bedroom w/o grounded outlets

Why do people think (2) prong plugs are hard to find. I see them all the time in Home Depot, Lowes and most normal hardware stores. Anyway, if it was MY daughters dwelling or apartment then I would simply meet the code section below which is designed to be a practical safeguard and install the GFCI and label the downstream receptacles as "No Equipment Ground" and "GFCI Protected".

(3) Non–Grounding-Type Receptacles.
Where attachment
to an equipment grounding conductor does not exist
in the receptacle enclosure, the installation shall comply
with (D)(3)(a), (D)(3)(b), or (D)(3)(c).

(a) A non–grounding-type receptacle(s) shall be permitted
to be replaced with another non–grounding-type receptacle(s).

(b) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a ground-fault circuit interrupter type
of receptacle(s). These receptacles shall be marked
"No Equipment Ground." An equipment grounding conductor
shall not be connected from the ground-fault circuit interrupter-
type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a grounding-type receptacle(s)
where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the ground fault
circuit interrupter shall be marked "GFCI Protected"
and "No Equipment Ground." An equipment grounding
conductor shall not be connected between the grounding type
receptacles.




Paul W. Abernathy
Reply With Quote
  #9  
Old 11/18/09, 8:35 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Bedroom w/o grounded outlets

Quote:
Originally Posted by pabernathy View Post
Why do people think (2) prong plugs are hard to find. I see them all the time in Home Depot, Lowes and most normal hardware stores.

D'oh! I tried to help a friend find some not long ago and did the searching online. Next time I'll actually go into a store



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #10  
Old 11/18/09, 8:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bedroom w/o grounded outlets

lol......man those big box stores have everything today....



Paul W. Abernathy
Reply With Quote
  #11  
Old 11/19/09, 12:06 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Bedroom w/o grounded outlets

If all else fails, go to a wholesaler.
They do sell to the public.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 1/9/10, 10:58 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bedroom w/o grounded outlets

Paul
By just adding a GFCI outlet with no equipment ground, isn't that still a false sense of security? I have run into situations in kitchen areas where GFCI'S are present without a equipment ground and the outlet will not trip properly, please advise.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #13  
Old 1/9/10, 11:01 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Bedroom w/o grounded outlets

Quote:
Originally Posted by nbhi View Post
Paul
By just adding a GFCI outlet with no equipment ground, isn't that still a false sense of security? I have run into situations in kitchen areas where GFCI'S are present without a equipment ground and the outlet will not trip properly, please advise.
If yo uare trying to test a GFCI that is not connected to ground with a 3 light tester, it wont work.

Use the test button on the outlet.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/9/10, 11:25 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bedroom w/o grounded outlets

I am using my sure tester that simulates a load that should trip, but they never do. I would think in order to function properly, a equipment ground needs to be installed.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #15  
Old 1/9/10, 11:39 AM
ecolclasure ecolclasure is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Hibbing Mn
Posts: 26
Default Re: Bedroom w/o grounded outlets

Just because your tester doesn't trip doesn't mean that the outlet is bad, all it means is your test failed. Your tester won't work in this situation because you are trying to ground fault the outlet to the ground in the box that does not exist. If you were to actually ground fault to ground it would trip. use the button.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
opinions on GFCI outlets for non grounded oputlets jmerritt1 Electrical Inspections 23 5/11/06 7:22 PM