Default Best way to protect a dedicated exterior circuit

What is the the best way to protect this motor for the septic? It is not GFCI.

It is a dedicated circuit (which it should be) but should it also be GFCI protected?
Attached Thumbnails
best-way-protect-dedicated-exterior-circuit-well-dude-008.jpg  



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #2  
Old 9/19/08, 10:26 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by fmagdefrau View Post
What is the the best way to protect this motor for the septic? It is not GFCI.

It is a dedicated circuit (which it should be) but should it also be GFCI protected?
All outdoor recepticales must be GFCI protected .

If that is a plug , it can be pulled and looks accessible, so there should be no exception.
Reply With Quote
  #3  
Old 9/19/08, 10:39 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,397
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by relliott View Post
All outdoor recepticales must be GFCI protected .

If that is a plug , it can be pulled and looks accessible, so there should be no exception.
I understand that but how should it be GFCI procted? If this motor trips out then the toilets will back up and there will be a big mess.

So should the gfci breaker be installed in the main panel. I know if an outlet type gfci is installed at the box then it will trip out all the time.

Again what is the best way?



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #4  
Old 9/19/08, 10:49 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by fmagdefrau View Post
I understand that but how should it be GFCI procted? If this motor trips out then the toilets will back up and there will be a big mess.

So should the gfci breaker be installed in the main panel. I know if an outlet type gfci is installed at the box then it will trip out all the time.

Again what is the best way?
Frank, if that is a dedicated circuit, then it doesn't have to be GFCI, however, if it were GFCI it still should have an audible alarm tied to a float switch to denote the fact that it is failing to start.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 9/19/08, 11:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Best way to protect a dedicated exterior circuit

A weather proof cover would be a good start as well (the plastic bubble type), and doesn't look "dedicated" to me - it looks like a duplex. Also, the conduit (hopefully type UF) should be protected where it exits the ground.

It doesn't matter where the GFCI protection is located unless the concern is walking through the "sludge" to reset it at the receptacle, but Gerry's point was best, there should be an audible alarm to warn when/if power is cut.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 9/20/08, 12:20 AM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,397
Default Re: Best way to protect a dedicated exterior circuit

Thanks guys. I should have done a better job on this one. I will go back to the property in the morning and re-inspect it. Its a new home, vacant and the garage is open so I can check it out better.

I knew it should not be GFCI protected and I do think it is a dedicated circuit, I agree about the plastic bubble, the unprotected conduit and the alarm. If it is not a dedicated circuit I will recommend a GFCI. However It should be a dedicated circuit because a pump is used.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #7  
Old 9/20/08, 11:00 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best way to protect a dedicated exterior circuit

That receptacle is also currently required to have a "weatherproof while in use" cover, also known as a "bubble cover" for slang.
Reply With Quote
  #8  
Old 9/20/08, 11:57 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by Marc D. Shunk View Post
That receptacle is also currently required to have a "weatherproof while in use" cover, also known as a "bubble cover" for slang.
Mark , in this situation ,wouldn't you normally find it hardwired, much like an condenser unit .

Never see them on a pullable plug.
Reply With Quote
  #9  
Old 9/20/08, 12:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by relliott View Post
Mark , in this situation ,wouldn't you normally find it hardwired, much like an condenser unit .

Never see them on a pullable plug.
Could be either way. Those air sparger pumps are normally cord and plug connected, in my observation. The come that way, right out of the box. Cutting off a factory cord cap to hardwire it would actually enhance the nature of the violation, ie- make things worse.
Reply With Quote
  #10  
Old 9/20/08, 12:16 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by Marc D. Shunk View Post
Could be either way. Those air sparger pumps are normally cord and plug connected, in my observation. The come that way, right out of the box. Cutting off a factory cord cap to hardwire it would actually enhance the nature of the violation, ie- make things worse.
Thanks,I never see them in my neck of the woods.
Reply With Quote
  #11  
Old 9/20/08, 12:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by relliott View Post
Thanks,I never see them in my neck of the woods.
They're a more obscure system. I'm not sure what brand that sparger pump is, but it looks like maybe a Medo. They almost never even need a dedicated circuit, since most of them draw barely over 2 amps. I put in a pretty big Gast pump for an apartment building's air injection pump, and it was only 4.7 amps. No need to dedicate a circuit for any sparger pump I've ever seen.

http://www.septicsolutions.net/store/SepAerator.htm

In fact, if you see a sparger pump in a resi system, an inspector might have to doubt if they weren't having problems with the septic, or if they're trying to be cutting-edge and avoid problems. It's only one of the two reasons.... a system on its last leg, or a high-class system.
Reply With Quote
  #12  
Old 9/20/08, 1:27 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by Marc D. Shunk View Post
They're a more obscure system. I'm not sure what brand that sparger pump is, but it looks like maybe a Medo. They almost never even need a dedicated circuit, since most of them draw barely over 2 amps. I put in a pretty big Gast pump for an apartment building's air injection pump, and it was only 4.7 amps. No need to dedicate a circuit for any sparger pump I've ever seen.

http://www.septicsolutions.net/store/SepAerator.htm

In fact, if you see a sparger pump in a resi system, an inspector might have to doubt if they weren't having problems with the septic, or if they're trying to be cutting-edge and avoid problems. It's only one of the two reasons.... a system on its last leg, or a high-class system.
Yeah not much, unless initial draw is high.

2 amps is something like a couple incandescent bulbs or 200 watts.
Reply With Quote
  #13  
Old 9/21/08, 10:48 AM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,397
Default Re: Best way to protect a dedicated exterior circuit

Quote:
Originally Posted by Marc D. Shunk View Post
That receptacle is also currently required to have a "weatherproof while in use" cover, also known as a "bubble cover" for slang.
I covered that in my report, thanks.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
To protect or not to protect. jlybolt Plumbing Inspections 2 7/23/07 11:53 PM
Missouri Passes New Law to Protect Consumers....from RE Agents jbushart Legislation, Licensing & Legal Issues for Inspectors 0 7/17/07 7:38 PM
Missouri Passes New Law to Protect Consumers....from RE Agents jbushart Legislation, Licensing & Legal Issues for Inspectors 0 7/17/07 7:38 PM
New web site dedicated to marketing for small businesses rray Miscellaneous Discussion for Inspectors 1 2/14/07 10:31 AM
Dedicated circuit required? Frank Nihei Electrical Inspections 6 9/19/06 2:32 PM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts