Default Black copper wire

I did an inspection yesterday and the copper wire in the outside panels ws dark black. At first glance I though the ground wires were insulated. On closer examination, there had all turned black. This was seen in both the service panel and the pool electrical panel. The copper in the inside panel was normal as was the copper on the air conditioner coils.

The home was built in 1997 so before most reports of Chinese drywall and if that were involved, I would have expected the copper inside the home to be affected.

Does anyone have an idea what might cause this and if there is a problem that I should report?

The first photo is the outside panel and the second is the inside panel.
Attached Thumbnails
black-copper-wire-img_5011.jpg   black-copper-wire-img_5048.jpg  



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #2  
Old 11/22/09, 1:13 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 4,868
Default Re: Black copper wire

Lightning? That is strange, at first looks like Chinese Drywall issue, but with the inside panel looking clean makes me believe there was an electrical problem with the box. Did you see ANY wiring issues such as melted sheathing or loose wiring? Has the house undergone a major refurb? Maybe it was a Chinese drywall house that has been retrofitted. We did a house built in 1990 with Chinese Drywall issues. Hurricane Charley almost destroyed the house, so it was rebuilt with Chinese Drywall, so the age is not always the tell tale sign. Did you check wiring at outlets, refrig coils, ac coils?
Reply With Quote
  #3  
Old 11/22/09, 1:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Black copper wire

Sulfer, chemical compounds and high moisture environments are possibilities:

http://www.nachi.org/forum/f19/blackened-grounds-27945/




InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 11/22/09, 1:53 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Black copper wire

Thanks for the replies. When I opened the panel, I thought "OH crap", Chinese drywall. The home was in good condition and had the original roof so I do not suspect any major renovations. Besides, as was mentioned in the other posts, if it were Chinese drywall, there would most likely be some indication inside.

I didn't see any indication of overheating or loose wires. I typically check a few wires at random for tightness and all I checked were nice and tight. The only thing I saw was the color of the bare portions of the copper. It seemed to be most prevelant on the neutrals and grounds but there was some on the hot wires also. Inside the house, nice and clean.

BTW Larry, thanks for the link to the other posts. I am impressed with how some of you guys find these things so easily. For some reason when I search for things like this, I have to wade through a lot of unrelated posts and have a hard time finding ones that are relevant.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #5  
Old 11/22/09, 1:55 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Black copper wire

Was the panel in close proximity to the pool / chemical equipment?



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #6  
Old 11/22/09, 2:02 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Black copper wire

Doug,

The pool panel was around the corner from the pool and about 20 to 25 feet away. The main panel was about 30 feet down the side wall from the pool panel. I could possibly consider some affect from the pool on the pool panel but I think it would be a stretch to associate that with the main panel.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #7  
Old 11/22/09, 2:12 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Black copper wire

Just asking. We have chemical plants near here and with the prevailing winds out of the west, I find homes to the East and close by with 3 and 4 yr old air conditioners where the coil fins on the outside units just crumble from corrosion. Something around that area is causing the copper to turn black. If you don't know the exact cause, best thing to do is report it, recommend an electrician investigate it for any compromise to the system and move on. What about the copper tubing on the HvAC outside?



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #8  
Old 11/22/09, 2:25 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Black copper wire

Please don't misunderstand me Doug, I am looking for answers and appreciate your response. I was just saying that I could not under the circumstances attribute the discoloration in the service panel to the pool. As to your question about the A/C copper, the copper there was dark, which is what I am accustomed to seeing, but not the same black as I saw in the electrical panel.

It is not unusual to find some minor discoloration on the copper in the exterior panels but this is the first time I have seen this. I don't even see this on homes that are much older than this house was. I have also done inspections on homes within a few miles of this one but did not see the same thing.

I'm not sure there is a problem but I will report it.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #9  
Old 11/22/09, 6:16 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 544
Send a message via Skype™ to gwells
Default Re: Black copper wire

Quote:
Originally Posted by rsole View Post
I did an inspection yesterday and the copper wire in the outside panels ws dark black.
Possiblities include Sulfer, Hydrogen Sulfide, and atmospheric oxygen. Are there any open sewers or other sources of sewer gas close to the panel? In areas of high humidity, it is more likely to be atmospheric oxygen; which is not too great a concern. I would (as an electrician, not as an inspector) coat the conductors with an oxide inhibitor and make sure all the connections are properly torqued. I'd also put a sticker in the box (like an oil change reminder) with a recommendation to service the panel at a future date. Here in Michigan, I would say five years but in Florida, it might be better to make it less than five years.



Licensed Electrical Contractor
Master Electrician
BS Electrical Engineering
Certified Master Inspector

B
estInspectors.Net

License Prep and Continuing Education
Home and Commercial Building Inspection - Electrical
Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm
Fire and Explosion Investigation - Commercial Sign
Installation - Real Estate (Agent and Broker) - Appraisal

Inspection Report Software for
Windows - iOS - Mac - Android - Linux



est. 1992
Reply With Quote
  #10  
Old 11/22/09, 6:35 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Black copper wire

Possible loose neutral.
Reply With Quote
  #11  
Old 11/22/09, 8:23 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Black copper wire

I appreciate all the responses. I recommended that they have an electrician inspect the panel and ensure that it would not cause a problem. The sewer is located at the front of the home so I doubt that that is the issue. As to loose connections, I checked a few and every one I checked was good and tight.

Maybe an electrician will find something I didn't.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #12  
Old 11/29/09, 7:54 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Black copper wire

Did you check the ground wires at the outlet connections through-out the house? Even though the home was built in 1997 they may have done some repairs with imported drywall. I read it only take 3 boards to cause problem. How did the copper AC high and low pressure lines at the air handler unit connection look? Just a thought.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Light Switch Near Shower vsantos Electrical Inspections 199 9/18/09 10:56 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM


All times are GMT -4. The time now is 7:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts