I just inspected a 4 y.o. house and found some black staining on 3 outlets. They were in different rooms and not all on outside walls. The staining is like a fine powder which wipes off easily. Any thoughts?
|
|
#2
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
|||
|
|||
|
That happens often here in Colorado, the Power Company sends out a high test signal, and here we have the black carbon dust electrical backflow preventers, it they aren't working then the black carbon dust spills out onto the outlets and they know they need to replace those black carbon electrical backflow preventors on that part of the grid.
I may be wrong though,, Ask Mark or Paul,, they are the Guru's,, |
|
#4
|
||||
|
||||
|
Please Note:
Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul's the Guru. I just twist wires together.
This was just discussed a few days ago anyhow. http://www.nachi.org/forum/showthrea...ighlight=glade |
|
#6
|
|||
|
|||
|
Thanks Marc. Just went over there and looked at it. Must have missed it earlier.
|
|
#7
|
||||
|
||||
|
I believe it is DUST from air probably around the openings and possibly back drafting...I would suspect Glades Plugs.....or something similar in the outlets.
Other than that.....if it was from arcing you would be able to smell it and get the smell of charing...or burning from the plastic...the fact it wipes off tells me I don't believe it has anything to do with arcing...but thats just my OP. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| ungrounded outlets! | gmaher | Electrical Inspections | 29 | 6/10/07 11:58 PM |
| Properly Testing GFCI Outlets | tchristopher | Electrical Inspections | 17 | 3/17/07 12:19 PM |
| Replacing 2-prong outlets with GFCI outlets | kshepard | Electrical Inspections | 7 | 6/24/06 7:58 AM |
| 20 amp with 15 amp outlets | abishop | Electrical Inspections | 32 | 1/31/06 5:21 PM |