Default Blackened Grounds

I know this has been discussed here, but I'm not sure we've ever come to a concensus as to the issue that causes it.

The house has been vacant/unoccupied for nearly one year, built in 2005.

All grounding conductors are black. Some show signs that they may have been heated with a blueish tint.

Most of the ungrounded conductors (neutrals) were also black.

None of the ungrounded conductors were black.

Interior receptacles show no abnormal voltage-drop, and there was no discoloration at the conductors inside the home. The panel wiring showed no abnormal heat ranges with thermal imaging.

What say you?
Attached Thumbnails
blackened-grounds-p4180004.jpg   blackened-grounds-p4180005.jpg   blackened-grounds-p4180007.jpg   blackened-grounds-p4180009.jpg   blackened-grounds-p4180010.jpg  




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #2  
Old 4/18/08, 10:30 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blackened Grounds

Ever see a copper roof?
Reply With Quote
  #3  
Old 4/18/08, 10:30 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blackened Grounds

It's you left-coast-outdoor-panel guys.






Quote:
Originally Posted by jpope
The house has been vacant/unoccupied for nearly one year, built in 2005.
WOW! Is the market that bad out there?
Reply With Quote
  #4  
Old 4/18/08, 10:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Blackened Grounds

Quote:
Originally Posted by Mike Whitt
Ever see a copper roof?
If it were really that simple, shouldn't we expect that the ungrounded conductors be blackened as well?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 4/18/08, 10:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Blackened Grounds

Quote:
Originally Posted by Speedy Petey
WOW! Is the market that bad out there?
How is that bad? Foreclosures are "hot." Bank will try and hold out for a good price, but eventually they get realistic and reduce them to maket rates.

This one is in the desert, 3200 sq ft for $289k.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 4/18/08, 11:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blackened Grounds

Well water? Sulfer? Maybe an aeriator
I know that turns copper black.
Reply With Quote
  #7  
Old 4/18/08, 11:34 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Blackened Grounds

Quote:
Originally Posted by jpope
None of the ungrounded conductors were black.
Aren't these ungrounded & darkened as well?
blackened-grounds-p4180005.jpg
Reply With Quote
  #8  
Old 4/19/08, 12:01 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blackened Grounds

Read the replies: http://forums.mikeholt.com/showthread.php?t=93357
Reply With Quote
  #9  
Old 4/19/08, 12:10 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Blackened Grounds

Jeff

The copper and the black has nothing to do with the fact that one is hot and one is at ground level

Look at it this way if the breaker is closed both are at the same level

Copper changes color based on what is in the air and on what is on the wire

Why some of the "HOT" wires were not black I can not answer

Something is not known

I do not see a reportable issue without additional information

I do not think that a good electician could help without additional information

rlb
Reply With Quote
  #10  
Old 4/19/08, 12:15 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Blackened Grounds

Joe your post did not help

rlb
Reply With Quote
  #11  
Old 4/19/08, 12:42 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Blackened Grounds

Quote:
Originally Posted by mboyett
Aren't these ungrounded & darkened as well?
Attachment 20486
Yep. Didn't notice those at the time. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #12  
Old 4/19/08, 2:12 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Blackened Grounds

Could the presence of excessive harmonics within the system attract airborne particles?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #13  
Old 4/19/08, 9:00 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Arrow Re: Blackened Grounds

Quote:
Originally Posted by rbennett
Joe your post did not help

rlb
Read through the replies they do discuss the issue and show that there is a problem, leaving the job and inspection that a HI was hired to do without mention on a report, is likely to come back to the frost and heat the argument, again READ the replies!!

LOOK HERE TO search

Last edited by jtedesco1; 4/19/08 at 9:51 AM..
Reply With Quote
  #14  
Old 4/19/08, 9:55 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Blackened Grounds

We have no information to suggest there is a problem other than cosmetic.

I would still "observe and report" what is present and also report the fact that no factual information has been located that explains the darkened copper.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #15  
Old 4/19/08, 5:11 PM
Jeff Allcroft Jeff Allcroft is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Springfield, VA
Posts: 64
Default Re: Blackened Grounds

Hey all, my first post - I am new to the board and really appreciate the serious stuff, the code specific items and the funnies too!

Boaters here http://continuouswave.com/ubb/Forum6/HTML/001067.html seem to think the black copper is due to salt.

Jeff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Netural & grounds tie together ksitzes Electrical 7 1/13/08 6:38 AM
Neutrals and Grounds ekartal6 Electrical 9 10/8/07 12:42 PM
Multiple grounds gmathias Electrical 11 4/30/07 2:49 PM
Double tapped grounds. gheller Electrical 10 4/17/07 9:14 PM
grounds and neutrals nbhi Electrical 4 4/5/06 12:14 AM


All times are GMT -4. The time now is 12:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts