Do these look like material approved for outdoor conduit?

I haven't seen them before. They are made out of some sort of blue plastic.

Thanks in advance.
Attached Thumbnails
blue-conduit-conduit.jpg  
Reply With Quote
  #2  
Old 4/4/08, 3:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Blue Conduit?

Smurf tube is corrugated PVC flexible tubing used to provide an easy method of upgrading structured wiring systems. The tube is run from the distribution panel to each outlet during the prewiring construction phase. Retrofit wiring can easily be pulled through the tubes without painstaking cable snaking. The most common type, Flex-Plus Blue ENT, is manufactured by Carlon, Cleveland, Ohio. Workers nicknamed it “smurf tube” because of its distinctive blue color.

Why can’t ENT be installed outdoors?
ENT was designed as an in-building product (see Article 362 of 2002 NEC). Since ENT does not have ultraviolet (UV) inhibitors added to the PVC compound such as our rigid PVC conduit, it is more affected by the ultraviolet rays from the sun. We know from experience that unprotected outside storage of ENT may result in brittleness in a 3 to 4 month period. ENT from the factory is stored with a white plastic wrap for storage and shipping to protect the product from the sun.

Carlon Website



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector


Last edited by mlarson; 4/4/08 at 4:08 PM..
Reply With Quote
  #3  
Old 4/4/08, 4:04 PM
chunt1's Avatar
chunt1 chunt1 is offline
Active Poster
 
Join Date: Sep 2006
Location: Lake Dallas, TX
Posts: 511
Please Note: chunt1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Try here
Reply With Quote
  #4  
Old 4/4/08, 4:22 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Thanks, great answers. Now I know why I haven't seen this outdoors!
Reply With Quote
  #5  
Old 4/4/08, 6:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Carlon may be overstating the UV damage aspect but it is listed indoor only so that is what you have to go by. I am using a piece of 3/4" smurf to sleeve the steering cable on my boat and it is doing fine 10 years later. I also have a short piece of smurf on the condensate line of my A/C that my wife moves around to water the plants, still OK.
Reply With Quote
  #6  
Old 4/4/08, 6:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Be advised also that ENT is not rated for protection against physical damage. Sometimes people will sleeve romex in ENT for "armor", which is just silly. In the eyes of the code, ENT offers no enhancement with regard to physical protection.
Reply With Quote
  #7  
Old 4/4/08, 9:05 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

I agree Marc, they do have similar language in regard to damage but our AHJ seems to like it more than exposed Romex. (garages and utility spaces)
This whole physical damage issue is so subjective it is hard to trust a ruling from day to day, AHJ to AHJ. There is really no hard and fast rule of what is subject to physical damage and when that potential damage is "severe".
It is just one of those, "the AHJ knows it when he sees it" things.
Some places like Romex on running boards everywhere, others want it above 5' or so, some always want it concealed and others don't really like Romex at all. (I'm talking about you Will )
Usually where we see smurf in new construction is roughing in garage "coach lights" that get installed in grouted cells since it is listed for direct concrete encasement. You can also use it to sleeve through a tie beam or come through a floor slab into an island if it is in the pour.
They are supposed to dig it out a little deeper where the smurf goes to still maintain the 4" slab and keep the smurf in the concrete. YMMV
Reply With Quote
  #8  
Old 4/4/08, 9:27 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Marc, correct me if I am wrong, but I believe when you put Smurf in concrete you are required to use PVC fittings instead of Smurf fittings, as Smurf fittings are not concrete tight.
Reply With Quote
  #9  
Old 4/4/08, 9:59 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Not true. Smurf fittings are listed for concrete if they snap twice when installing. They are suprisingly tight if the end of the tube was cut in the groove.
Reply With Quote
  #10  
Old 4/5/08, 2:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Quote:
Originally Posted by brian winkle
Marc, correct me if I am wrong, but I believe when you put Smurf in concrete you are required to use PVC fittings instead of Smurf fittings, as Smurf fittings are not concrete tight.
Don't know. I don't use the stuff. Good practice dictates that any mechanical connection that will be covered in concrete get taped anyhow.
Reply With Quote
  #11  
Old 4/5/08, 4:05 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Blue Conduit?

Hi. Mark;

Around here, the only place on commercial jobs that the blue smurf tube is used is by the control people for thermostats, low voltage, and hard to get places, add ons by the electrician to run additional conductors.

What is up with running in concrete in lieu of running pvc conduit buried in the ground away from all the abuse of pouring the concrete?

Never seen this stuff actually run and cast in concrete. Even though it might be approved.

Curious.

Marcel
Reply With Quote
  #12  
Old 4/5/08, 4:14 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Quote:
Originally Posted by mcyr
What is up with running in concrete in lieu of running pvc conduit buried in the ground away from all the abuse of pouring the concrete?
It's fast and cheap. That's about all I can think of.

I think you'd also have about a 90% chance of the flatwork guys stepping on it or running their mud buggies over it and having many places smashed flat. Sounds like a bad installation practice, to me, even if it is approved.

I said that I don't run the stuff, but I guess that's not true. I remember running it at least twice. Each time it was in metal studs, where the schedule got all messed up. I was in a hurry, and just left a stub of ENT stick out of the top of the wall, above the suspended ceiling line, from each switch and outlet location so that the rockers could get to work. Made more work for me later, but kept the schedule on track. Took a few days work and turned it into 6 hours. Of course, when I had to do the above ceiling work, that took way more time, but there was more wiggle room in the construction schedule at that point. I don't want to be the guy responsible for taking a project off the critical path. That usually means you will not get any more work from that GC after the project is done.
Reply With Quote
  #13  
Old 4/5/08, 4:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Blue Conduit?

Thanks Mark.

Fast and cheap, yes sir, seems like everything is being based on that today.

Problem here is cheap, in order for it to be material cheap, it also allows to be labor cheap.
Now you do not need electrians that know how to bend EMT and the lesser skills mean lesser pay, Unless in the Union.

One of these days, good skilled craftsmen will be a thing of the past.

Marcel
Reply With Quote
  #14  
Old 4/5/08, 6:25 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Fast and cheap, sounds like what Will says about Romex. He is right. That IS why Marc doesn't run EMT in residential.

ENT is listed concrete tight, without tape. I can say, if the ends are dressed cleanly and "double clicked" into the connectors they are damn near water tight . Certainly better than traditional EMT compression connectors. (dunno about the "rain tight" ones).
Reply With Quote
  #15  
Old 4/6/08, 2:58 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blue Conduit?

Quote:
Originally Posted by Greg Fretwell
ENT is listed concrete tight, without tape. I can say, if the ends are dressed cleanly and "double clicked" into the connectors they are damn near water tight . Certainly better than traditional EMT compression connectors. (dunno about the "rain tight" ones).
You say this from all your years of experience installing electrical goods?

Give me a break.

More old guys rambling on, pretending to still be relevant.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
One Common Ancestor Behind Blue Eyes ccurrins Miscellaneous Discussion for Inspectors 13 2/10/08 11:55 AM
Dwelling and Commercial Electrical Equipment jtedesco1 Electrical Inspections 4 1/10/08 7:46 AM
Blue pvc glue kgerhauser Plumbing Inspections 10 1/26/07 4:47 PM
Should this be in conduit kblair1 Electrical Inspections 18 12/26/06 5:50 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Inspection Education & Training 5 8/11/06 5:46 PM


All times are GMT -4. The time now is 3:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts