Default Bond at Distribution Panel

Hey Guys-

This home had a service disconnect on the exterior with correct bonding of the ground and neutral. However, the interior distribution panel was also bonded. Usually it seems there is a way to remove the bonding strap to separate them but this one looked to be permanently connected. Either way its incorrect right? Is this panel made to be a service panel only and not a distribution panel or am I missing how the two can be separated? Thanks.

Kenny
Attached Thumbnails
bond-distribution-panel-gedc4026b.jpg   bond-distribution-panel-gedc4142b.jpg   bond-distribution-panel-gedc4146.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/7/11, 9:15 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bond at Distribution Panel

There should have been an auxillary ground bar kit installed and all the grounding conductors moved over to it.

The green bond screw has not been installed on this panel.
Reply With Quote
  #3  
Old 3/7/11, 11:16 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bond at Distribution Panel

Quote:
Originally Posted by Jim Port View Post
The green bond screw has not been installed on this panel.
Which means that the sub panel is NOT bonded. The neutrals and egc's are bonded (which is improper in this case), but the panel is not.

At all panels, the egc's should be bonded to the enclosure. At sub (distribution) panels, the neutrals should be isolated from the enclosure.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 3/7/11, 11:21 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Bond at Distribution Panel

I think I see a double-tapped neutral on the right bus.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 3/7/11, 4:09 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bond at Distribution Panel

Someone didn't have much of a clue when they put the neutral and feeder EGC in parallel. The panel would be grounded if the feeder is contained in a metallic raceway. There is no bonding locknut or bonding bushing on the nipple that contains the service entrance condcutors (although it could be in the meter). There is no visible GEC connection.
Reply With Quote
  #6  
Old 3/7/11, 4:29 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Bond at Distribution Panel

Thanks guys. I didn't consider an auxiliary ground bar kit or the difference between the bonding of the egc's/neutrals and the actual bonding of the panel.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #7  
Old 3/8/11, 10:52 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bond at Distribution Panel

Quote:
Originally Posted by krigler View Post
Thanks guys. I didn't consider an auxiliary ground bar kit or the difference between the bonding of the egc's/neutrals and the actual bonding of the panel.
I assumed that based on your post.

All metal boxes within the electrical system (panel boxes, j-boxes, switch boxes, etc.) should be "grounded," i.e. bonded to the grounding electrode system. This is generally accomplished through bonding of the egc's to the boxes.

The neutrals (grounded conductors) should only be bonded to the GES at the service equipment. Connecting/bonding the neutrals to the egc's anywhere else in the system can create a parallel path for current to "travel" on exposed metallic components within the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Sub distribution panel 'over qualified' ? lfoster Electrical Inspections 7 4/12/09 7:56 AM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts