Default Bond at Panel

I recently did an inspection on a 2 family home. One electrical service line, 2 meters, 2 main panels. There is a ground connection and a bond between the neutral bar and the panel at one of the panels. The second panel did not have either. I believe a single ground connection is okay, but am wondering if this panel should be bonded. Any thoughts?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/14/10, 10:25 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bond at Panel

Both panels (as service equipment) must be mechanically connected (bonded) to each other and to the grounding electrode.

The grounded (neutral) conductors at the service equipment must also be bonded to the GE.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/14/10, 10:48 AM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Bond at Panel

Thanks Jeff. I'm going with that.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #4  
Old 10/15/10, 3:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bond at Panel

Quote:
Originally Posted by jpope View Post
Both panels (as service equipment) must be mechanically connected (bonded) to each other and to the grounding electrode.

Why do the two panels need to be mechanically connected to each other?
Reply With Quote
  #5  
Old 10/15/10, 4:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bond at Panel

Grouped disconnects on a single drop should be bonded, no?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 10/15/10, 4:49 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bond at Panel

Quote:
Originally Posted by jpope View Post
Grouped disconnects on a single drop should be bonded, no?

Yes, you're correct. In my mind I took mechanically connecting the two disconnects as requiring some sort of raceway connection between them. They could simply be bonded by having a bonding jumper from each disconnect to the GEC or some other bonding arrangement where there is no direct connection between the two.
Reply With Quote
  #7  
Old 10/15/10, 5:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bond at Panel

I was trying to help differentiate bonded (the mechanical "connection" between components) and grounded (the connection to earth).

Many inspectors have a difficult time with these terms.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 10/15/10, 5:46 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Bond at Panel

John-

Was the house in Staten Island? BX throughout? Were the panels connected by conduit with bonding jumpers?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Does Anyone See A Panel Bond Here? pdickerson Electrical Inspections 14 10/24/07 11:40 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts