Default Is this bonded?

Looked at this panel tonight, everything looked good except I could not find the bonding screw. It's a Square D panel, no screw or strap that I could see. Unable to tell if the grounding bar on left was metal to metal. Not the best pictures but if you see it let me know, thanks.
Mark T
Attached Thumbnails
bonded-img_1997.jpg   bonded-img_1998.jpg  
Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #2  
Old 8/5/09, 11:04 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Is this bonded?

Looks like a sub panel, it has a 4-wire feed and the grounds are on the left hidden bus which is mounted direct to the metal box. The two neutral bars are isolated from ground as they should be if it is in fact a sub panel.

Did you see a 200 amp disconnect (main panel) by the meter?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 8/5/09, 11:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this bonded?

Mark,

Before I comment I have to ask you a few questions.

1.) Is this the Main Service Disconnect? Forget the fact it has a main breaker....is this the Main Service Disconnect?

2.) Since it appears to be 4 conductors, is their any disconnect ahead of it.....anywhere ahead of it?

3.) I really can't tell.....does an GEC land on the grounding terminal bar on the left?

4.) Is their a GEC in this panel?.....an important question that helps answer questions above as well.

let us know......and ye shall receive!



Paul W. Abernathy
Reply With Quote
  #4  
Old 8/5/09, 11:24 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Is this bonded?

Man, I'm embarrassed, I totally dropped the ball on this one. It never occurred to me that this wasn't the main. I'll have to go back tomorrow and check under the meter and look in that mystery box below it. thanks again, Mark T
Attached Thumbnails
bonded-img_1946.jpg  
Reply With Quote
  #5  
Old 8/5/09, 11:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this bonded?

Quote:
Originally Posted by mthiltgen View Post
Man, I'm embarrassed, I totally dropped the ball on this one. It never occurred to me that this wasn't the main. I'll have to go back tomorrow and check under the meter and look in that mystery box below it. thanks again, Mark T
lol.....I knew asking you the questions would JAR the memory. It's ok fella...the great thing about this type of thing is i can bet it will never happen again....so you gained something from it. Never be embarrassed about it fella....it's all good.



Paul W. Abernathy
Reply With Quote
  #6  
Old 8/5/09, 11:35 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Is this bonded?

Quote:
Originally Posted by pabernathy View Post
lol.....I knew asking you the questions would JAR the memory. It's ok fella...the great thing about this type of thing is i can bet it will never happen again....so you gained something from it. Never be embarrassed about it fella....it's all good.
Another great thing is, that you showed your integrity by admitting you may have made a mistake, and not trying to BS your way out of it. That goes a long way around here.
Reply With Quote
  #7  
Old 8/5/09, 11:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this bonded?

Quote:
Originally Posted by jjonas View Post
Another great thing is, that you showed your integrity by admitting you may have made a mistake, and not trying to BS your way out of it. That goes a long way around here.
I agree 100%.........He is a class act. It is not always about the inspections the HI's get right...it is about the ones they might get wrong and that the little BUG in the back of the mind that make's you think enough to ask others.....Just sorry you have to go back out , but you did show class in admitting it and your client is lucky to have you care enough to dig deeper.



Paul W. Abernathy
Reply With Quote
  #8  
Old 8/5/09, 11:48 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Is this bonded?

Paul,
Wouldn't the colors of the SEC be a hint/clue? In the two states I've inspected in (MN & WA), I have only seen black. Is it common in other areas to see black, red, white?
Jeff
Reply With Quote
  #9  
Old 8/5/09, 11:50 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Is this bonded?

I allways appreciate the info you guys give back when there's a question posted. Who know's maybe I'll be talking to you tomorrow!
p.s. don't tell my wife I'm not perfect! sssshhhhhhh
Reply With Quote
  #10  
Old 8/5/09, 11:51 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Is this bonded?

Quote:
Originally Posted by mthiltgen View Post
I allways appreciate the info you guys give back when there's a question posted. Who know's maybe I'll be talking to you tomorrow!
p.s. don't tell my wife I'm not perfect! sssshhhhhhh
Mark, trust me, she already knows
Reply With Quote
  #11  
Old 8/5/09, 11:56 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Is this bonded?

Good use of the available expertise.

My clients always seem to like it when I tell them "I'm going to go confer with a couple of my colleagues about the matter this evening. I'll let you know what our consensus is in the morning."

Sure beats the "Idunno" response.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #12  
Old 8/6/09, 12:00 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is this bonded?

Quote:
Originally Posted by jjonas View Post
Paul,
Wouldn't the colors of the SEC be a hint/clue? In the two states I've inspected in (MN & WA), I have only seen black. Is it common in other areas to see black, red, white?
Jeff
It might . But you can't teach someone anything by always providing the answer without knowing hidden facts only present to the first hand account. Assumptions always cause problems. In regards to the colors, their is no real standard other than High-leg markings, grounded and grounding markings and so on but yes, that is generally the color scheme for SER type of cable.

Over my many years in this business I have seen one manufacturer use Red,Black,White and Bare and another use Black, Black, Black with White and Bare.......depends on the manufacturer really.

The key for me is when I see 4 conductors.....start looking for a service disconnect somewhere else. Also since this appears to be a fairly new installation and the the lack of GEC's would spark a furthur look as well.

The key in education is let the person evolve the answer and retain the rewards from examination....just as mark did.



Paul W. Abernathy
Reply With Quote
  #13  
Old 8/6/09, 12:03 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Is this bonded?

Quote:
Originally Posted by pabernathy View Post
It might . But you can't teach someone anything by always providing the answer without knowing hidden facts only present to the first hand account. Assumptions always cause problems. In regards to the colors, their is no real standard other than High-leg markings, grounded and grounding markings and so on but yes, that is generally the color scheme for SER type of cable.

Over my many years in this business I have seen one manufacturer use Red,Black,White and Bare and another use Black, Black, Black with White and Bare.......depends on the manufacturer really.

The key for me is when I see 4 conductors.....start looking for a service disconnect somewhere else. Also since this appears to be a fairly new installation and the the lack of GEC's would spark a furthur look as well.

The key in education is let the person evolve the answer and retain the rewards from examination....just as mark did.
Thanks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 11:50 AM
Is this subpanel bonded correctly? jboni General Inspection Discussion 12 4/3/09 10:40 AM
Are these buses bonded? jfunderburk Electrical Inspections 3 6/16/06 10:27 AM
Bonded to panel? cobarr Electrical Inspections 8 4/14/06 12:09 AM
bonded sub. Jay Moge Electrical Inspections 2 3/5/06 10:54 PM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts