Default bonded sub.

this is a 125a sub. about 1' away from the main, for the finished basement. there is only one bus bar, it's bonded to the back of the panel, all the grnds and neutrals are here. shouldn't they be separated?
Attached Thumbnails
bonded-sub-100_0834-small-.jpg.JPG
Views:	78
Size:	52.7 KB
ID:	1803  
Reply With Quote
  #2  
Old 3/5/06, 12:02 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: bonded sub.

Yes.


250.24(A)(5)


Load-Side Grounding Connections.


A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.






IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/5/06 at 12:40 AM..
Reply With Quote
  #3  
Old 3/5/06, 10:54 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bonded sub.

Quote:
Originally Posted by jpope
Yes.



250.24(A)(5)




Load-Side Grounding Connections.



A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.



Thought so, thanx Jeff. seller didn't want me to call it out. he said "yeah but what could happen, realy who cares........" so i told him, " i do, and so should my client." of course he also told me that the counter outlets didn't "have" to be gfci.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical Inspections 11 4/29/09 11:50 AM
35 year old metal roofing, bonded granules, panels molded like shakes kshepard Exterior Inspections 8 9/20/07 4:14 PM
bonded? cbuell Electrical Inspections 8 2/8/07 5:42 PM
Are these buses bonded? jfunderburk Electrical Inspections 3 6/16/06 10:27 AM
Bonded to panel? cobarr Electrical Inspections 8 4/14/06 12:09 AM


All times are GMT -4. The time now is 2:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts