Default Bonding

Could not find a bonding strap or screw. My ? however is, if the SEG is in contact with the panel, isn't that the same as a strap? The SEG is taking any stray electricity that may be hot on the panel back to ground, correct.

Attachment 11353

Attachment 11354

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 8:42 AM..
Reply With Quote
  #2  
Old 5/6/07, 9:54 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Bonding

Hi Gary,

no that would not be acceptable, there must be a proper mechanical connection.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 5/6/07, 10:03 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

In a lot of those older panels the bond was not so obvious. Green screws and external straps/bars were not always used.
The bond could be that straight blade screw right above the phillips head.
Reply With Quote
  #4  
Old 5/6/07, 10:19 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Bonding

Very True, speedy.

Look for a diagram on the inside of the panel, on square-d's I find them on the right. It might not be easy to read, but don't stick any body parts in to read it. Usually there is some verbiage, "bonding where required" and an arrow to a hole on the neutral bar. Often it's a fat, flat head like mentioned before.

tom
Reply With Quote
  #5  
Old 5/6/07, 10:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bonding

Gary, what's the SEG?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 5/6/07, 12:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding

Quote:
Originally Posted by nbhi
The SEG is taking any stray electricity that may be hot on the panel back to ground, correct.
Ahh...I don't have the desire to go into this in detail but do a look up google " stray voltage " and you will see what is going onto the " Grounded " conductor is not considered stray voltage.

The "Neutral" or " Grounded" conductor you are speaking of serves as a return path for electricity, fault current to aid in the faciliation of the OCPD from the panel to the transformer and so on.....any HOT as you say that gets onto the panel is going back via proper bonding methods.....to the source via this SEG which I believe you wanted to say Service Entrance Grounded conductor.

But alas...you get the jist of it.



Paul W. Abernathy
Reply With Quote
  #7  
Old 5/6/07, 2:06 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding

Paul
So, will the Service Entrance Grounded conductor take the stray electricity if the SEGC is in contact with the panel? I know the proper installation is to have a bonding strap or screw.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 5/6/07, 2:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

Quote:
Originally Posted by nbhi
Paul
So, will the Service Entrance Grounded conductor take the stray electricity if the SEGC is in contact with the panel? I know the proper installation is to have a bonding strap or screw.
No, only because there is no such thing as stray electricity. I'm sure you have some sort of good question in there some place, but it's really hard to decode what it is you're trying to ask. Are you talking about fault current? Lightning strikes? Paranormal EMI? Something else?
Reply With Quote
  #9  
Old 5/6/07, 2:42 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding

Marc
If a wire in the panel is nicked and is in contact with the panel, making the panel now hot.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 5/6/07, 2:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

Quote:
Originally Posted by nbhi
Marc
If a wire in the panel is nicked and is in contact with the panel, making the panel now hot.
Okay, you're talking about fault current. Just because the bare service neutral happens to be pressed against the panel is no guarantee that enough current from a nicked conductor in the can (that is also touching the can) will flow to open the overcurrent protective device. A 15 of 20 amp branch breaker... maybe. A 40 or 50 amp breaker... I doubt it very much.

I'm a little puzzled why you seem to be bending over backwards in search of a reason to justify a non-compliant installation. As has been pointed out, you need a solid mechanical connection. 'Loose wires cause fires'.
Reply With Quote
  #11  
Old 5/6/07, 3:04 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding

Marc
I am not bending over backwards, for one think I am not as flexable as I once was. I was just curious, that if the SEGC was in contact with the panel, would that be enough to carry away stray current if a wire was nicked. By the way the panel was in very good condition, no nicked wires.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #12  
Old 5/6/07, 3:12 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

Quote:
Originally Posted by nbhi
I was just curious, that if the SEGC was in contact with the panel, would that be enough to carry away stray current if a wire was nicked.
The qualified answer is "maybe", but there is no assurance, and it is a hazard. Matter of fact, stop using the term 'stray current'. If you use that term around a qualified person or customer who has his head screwed on straight, they'll think you're a clown.
Reply With Quote
  #13  
Old 5/6/07, 3:21 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding

You think I could be a clown? Never thought of it. Thanks for the good tip. I'll be sure to remember, fault current.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 5/6/07 at 3:28 PM..
Reply With Quote
  #14  
Old 5/6/07, 3:57 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Bonding

The wire just touching the inside of the panel is not good enough just due to the painted surface.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #15  
Old 5/6/07, 4:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

Quote:
Originally Posted by bgraham
The wire just touching the inside of the panel is not good enough just due to the painted surface.
Not all panels are painted, but unacceptable just the same.

Example of a resi panel can that is not painted:

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
Nat Gas water heater electr. bonding lfreeze Electrical Inspections 14 1/15/07 10:16 PM
What Is Bonding...... pabernathy Electrical Inspections 46 1/1/07 1:17 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 5:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts