Default Bonding

Since the water lines are plastic Pex, in the electrical panel it states, "this panel is not bonded due to plastic pipes".

So my question is, what protects these houses and is it as good as a copper pipe system.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 6/20/06, 10:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Bonding

The label is actually a warning that the piping system cannot be used as a means to electrically bond other equipment to the GEC (such as satellite systems or other components that would normally be bonded to the system). Without that warning, other trades may think that any exposed metallic piping could be used to bond their equipment (like an exterior spigot).

It has nothing to do with the "quality" or integrity of the bonding of the system or its components.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 6/20/06 at 10:45 PM..
Reply With Quote
  #3  
Old 6/21/06, 1:37 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Bonding

Very Nice Jeff.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #4  
Old 6/21/06, 1:49 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

They are starting to make the Ufer ground the electrode of choice since copper plumbing is getting more rare.
Reply With Quote
  #5  
Old 6/21/06, 10:11 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,699
Default Re: Bonding

When the GEC enters the meter box (which is not accessible) and no bonding wire enters the service panel, and... plastic conduit connects the meter/service panel, and... PEX water pipe is installed (house on slab). How do you know the system is grounded outside the grounding to the transformer?
Reply With Quote
  #6  
Old 6/21/06, 10:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bonding

David,

The GE System has to be installed in one fashion or another. Be this Ground Rod, Plate or etc.....If the GEC is visible at the meter can outside to a GE....the NEC allows the Grounded Conductor to play that role into the dwelling to the actual panel....

So even if their is not a Water Pipe Option....the NEC gives us other options and requirements that must be done, again the NEC allows the GEC to connect at the Meter Can, Panel or believe it or not the Messenger connection point at the service head....

The main thing to keep in mind is that IF no waterpipe is available the dwelling has to provide the other available options...as Greg said the UFER is getting more and more popular and in fact I have that in my house....tehehe...My Choice...

Always look for the other signs for the GEC....as you stated if it enters the Meter Box...then it is fine...just be sure it is sized right and that is about all you can do on that end......the NEC allows it as it is more a POCO choice I have seen.

Hope this helps....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 6/21/06, 12:31 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

There is actually a good reason to have that GEC land in the meter base. If lightning strikes it has a path to ground without actually entering the house.
That may actually make yoiur surge protection more effective.
In SW Florida the power company likes to see the GEC in their meter base. If I, as an electrical inspector, want to see it, it is only a phone call away. I call the PoCo and tell them I am cutting the seal, they say OK and send someone out to fix it later.
Reply With Quote
  #8  
Old 6/21/06, 12:36 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,699
Default Re: Bonding

That make sense. However access to the meter can prevents verification. The use of plastic electrical conduit prevents a bond. Around here, service panel's attach directly to the meter can. The messenger wire is the only connection "sight unseen" to a potential ground. I guess we have to depend on the AHJ for that inspection
Reply With Quote
  #9  
Old 6/21/06, 3:23 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: Bonding

Quote:
Originally Posted by Greg Fretwell
They are starting to make the Ufer ground the electrode of choice since copper plumbing is getting more rare.
It became quite popualr here in the 1950's
http://www.psihq.com/iread/ufergrnd.htm



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 6/21/06, 7:22 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,222
Default Re: Bonding

The reason ground rods will remain popular is the fact that the location of the lateral service to the meter can change during construction without splicing the GEC.
Reply With Quote
  #11  
Old 6/22/06, 2:33 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

That is one reason why I like the "turned up rebar" type Ufer where the GEC connection remains accessible. You can replace it with a longer one if the service location changes.
You could always shoot a CadWeld but that may be beyond some resi electricians.
Reply With Quote
  #12  
Old 6/22/06, 2:36 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

David there are 6 or 7 connections in the typical meter base, they are all important so in most places a licensed electrican can cut a seal with a phone call to the PoCo.
Reply With Quote
  #13  
Old 6/22/06, 2:42 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bonding

Hey Greg,

In my area......we are not allowed to cut a seal at all without POCO being at the location. As well as even if the NEC allows us to bring this GEC to (3) possibly locations......the POCO can simply say they do not want the connection to take place in their meter can ...which we run into alot with Harrisonburg Electric so it has to take place in the panel in our cases.

I guess the lesson in that is remember it can take place at multiple potential locations and be aware of the fact this can happen.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 6/22/06, 11:21 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding

In Collier county the PoCo wants the GEC in the meter can. I guess your mileage may vary on seals based on the amount of fraud they have. Some places have locking rings on meters. When I did my service upgrade they left my meter unsealed for a couple weeks. Then one day I noticed a seal on it.
Reply With Quote
  #15  
Old 6/23/06, 9:44 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Bonding

lol...NOW that is a TRUSTING community...lol......in our are they SIT and wait to re-seal it...lol....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding Piping 101....Good To Know ! pabernathy Electrical 37 4/28/07 12:25 PM
Nat Gas water heater electr. bonding lfreeze Electrical 14 1/15/07 11:16 PM
What Is Bonding...... pabernathy Electrical 46 1/1/07 2:17 PM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 2:08 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts