two sub panels same house. one strap cut one in place?
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
| Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Mark, I don't understand your question.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since they're both sub-panels then the neutral and EGC buses must be separated from each other. Seems that they attempted to do this in one panel but still installed the green bonding screw in the neutral bus.
|
|
#4
|
||||
|
||||
|
it looks like the copper strap is cut out of the sub in pics 1 and 2 and the silver flat strap is in place in the sub in pic 3?
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
|
#5
|
||||
|
||||
|
As Robert pointed out, panel #1 is still wrong. The bonding screw is in place, which has bonded the neutral terminal to the cabinet. In addition, the egc's are not bonded to the cabinet, which is required.
In the second panel, it appears that the neutrals are properly isolated (the silver strap connects both terminals together, but does not bond the terminals to the cabinet), while the egc's are properly bonded to the cabinet. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
thank you
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Ground | pnarron | Electrical Inspections | 2 | 11/16/10 4:08 PM |
| Pool and spa bonding | gfitzgerald | Electrical Inspections | 13 | 5/26/10 12:45 PM |
| Neutral bus bar failed inspection | Greg Moritz | Electrical Inspections | 18 | 1/19/08 1:53 PM |
| Demystify Grounding & Bonding Class | pabernathy | Inspection Education & Training | 5 | 12/24/06 1:10 AM |