  #16  
Old 3/4/06, 12:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Probably because I cant SPELL for crap James....yes it is Romex which is really just a brand name....thanks for pointing out I failed spelling in school.....Also I am only about 30 miles from West Virginia if that tells you anything...

I probably should just call it what it is...Non-Metallic Sheathed Cable....as it is safer..thehee

Will.......I FIGHT it every day brother.....I walk into a house giving an electrical quote and my INSPECTOR vibes start going off.....and visa versa.....when on an inspection...I struggle with NOT going too far all the time..

But it really is fun.......having LOTS of knowledge and trying to figure out what to do with it can be both fun and nerve racking at the same time.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #17  
Old 3/4/06, 1:28 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Piping 101....Good To Know !

I knew there was an explanation. Yeah, the Romex name is what 99% of non elecricians know NMC by. In fact, in my reports if I refer to it as non-metallic sheathed cable or as NMC I usually put (Romex) after the first reference just in case they don't know.
Reply With Quote
  #18  
Old 3/4/06, 1:31 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Maybe it is I am southern...lol.....Maybe it sounds like ROMAX when it comes out of us southern folks mouth....lol....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #19  
Old 3/4/06, 1:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Piping 101....Good To Know !

Romex is the registered trademark of the Rome wire and cable company (now Southwire). The real name is type NM-b.
NMC is another product, I doubt most of you have ever seen. It is damp location NM with a plastic inner wrapper where the kraft paper is now. When I look it up, the major cable companies refer you to type UF. I am guessing nobody makes it for the US market. Maybe that is different in the Great White North.
Reply With Quote
  #20  
Old 3/4/06, 2:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Yeppers...and they even name NMS now....

NM- The overall coating SHALL BE flame retardant and moisture resistant.

NMC- The overall coating SHALL BE flame retardant, moisture resistant, fungus resistant and corrosion resistant.

NMS - The overall coatin SHALL BE flame retardant and moisture resistant. The sheath SHALL BE applied so as to seperate the power connectors from the communications and signaling conductors. The signaling conductors SHALL BE permitted to be shielded. An optional outer jacket SHALL BE permitted.

Now the NMS I can safely say I have never used that I am aware of...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #21  
Old 3/4/06, 3:01 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Piping 101....Good To Know !

Right you are Greg. I guess I got used to saying NMC as an abbreviation for non-metallic sheathed cable as a whole.
Reply With Quote
  #22  
Old 3/4/06, 11:24 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: Bonding Piping 101....Good To Know !

Quote:
Originally Posted by jclark1
Right you are Greg. I guess I got used to saying NMC as an abbreviation for non-metallic sheathed cable as a whole.
We call it Rope in the west......
Reply With Quote
  #23  
Old 3/5/06, 10:36 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

You all say.....Howdy Their Partner......Git Y'r soldrin Ironz and Maker uz a Rope....< sound of Dale spitting in a spitoon >



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #24  
Old 3/5/06, 5:01 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Bonding Piping 101....Good To Know !

Just using the term "sheathed cable" to describe type NM wire works for me and clients too ...

P.S. Perhaps the question could be worded ... "Should Gas Piping Within Dwellings Get Bonded?" (couldn't resist ... lol).

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #25  
Old 3/6/06, 2:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

lol....Robert.....Notice my second post after the original...lol.....I realized once I made the thing it was not something I could change...lol..lessoned learned...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #26  
Old 3/6/06, 9:24 PM
eschwartz's Avatar
eschwartz eschwartz is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Seattle, WA
Posts: 33
Default Re: Bonding Piping 101....Good To Know !

Paul,
regarding your initial post....thanks for the gooood info. The point you make about the appliance providing the ground (or not)for the pipe (in some circumstances) is good to be aware of. Thanks
Ed
Reply With Quote
  #27  
Old 3/7/06, 6:21 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Thanks Ed,

Thats what I am here for......Feel free to hollar at me anytime.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #28  
Old 3/19/06, 9:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Wow...only 69% got this one.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #29  
Old 5/24/06, 11:12 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding Piping 101....Good To Know !

Bump.....Good Info



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #30  
Old 5/24/06, 4:44 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Piping 101....Good To Know !

Bonding is good.

G2411.1 (310.1) ICC IRC to see the full text. The gas lines are bonded if the egc of the circuit supplying the equipment is used.--My words.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding both hot and hold supply pipes kshepard Plumbing Inspections 22 5/4/08 9:00 AM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 2:10 AM
Grounding -V- Bonding Article (Good Read) pdoane Electrical Inspections 0 10/12/06 5:31 PM