Default Bonding of plumbing

I generally call out lack of a visible bond of the plumbing supply to the main panel no matter what age the home is. I often find many older homes lack this applications. Just curious what other document when delaing with this.

Thanks in advance.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/13/12, 9:25 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of plumbing

Do you mean the metallic hot and cold water pipes? Are you using the NEC to require that the plumbing piping be bonded to the electrical system?
Reply With Quote
  #3  
Old 1/13/12, 11:00 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Bonding of plumbing

Yes hot and cold supply.
Not necessarily the NEC but general rules of practice for most homes in the area here. and yes as required by the NEC as well.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net

Last edited by sfogarty; 1/13/12 at 11:12 PM..
Reply With Quote
  #4  
Old 1/13/12, 11:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bonding of plumbing

I always attempt to verify the bond if the interior piping is metallic, regardless of the age of the home.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/13/12, 11:18 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Bonding of plumbing

Quote:
Originally Posted by jpope View Post
I always attempt to verify the bond if the interior piping is metallic, regardless of the age of the home.
Do you recommend it is found or corrected if you cannot verify?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 1/13/12, 11:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bonding of plumbing

Yep. I recommend that it is verified or established by a qualified electrician.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/13/12, 11:47 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Bonding of plumbing

We are required to verify bonding of appliances as part of our state's SOP. A fellow inspector created an appliance bonding tester for it. Can the bonding for the plumbing be established in the same way using this tester which establishes continuity?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #8  
Old 1/13/12, 11:57 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Bonding of plumbing

Richard, that tester (which I'm familiar with ) really just tells us that the appliance chassis (or whatever is being tested) is connected to the EGC. It doesn't tell you how, in other words, to know for sure how the bonding is accomplished you would have to visually observe the wire and it connection. So, no...do not use the tester to confirm water lines are properly bonded.
Reply With Quote
  #9  
Old 1/14/12, 8:38 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Bonding of plumbing

Quote:
Originally Posted by sfogarty View Post
Yes hot and cold supply.
Not necessarily the NEC but general rules of practice for most homes in the area here. and yes as required by the NEC as well.
The NEC does not require a bond from cold to hot. It only requires that the potable water be bonded in an assessable location and then only if it is a complete metal water system. Should repairs be done and nonmetallic parts used then the equipment grounding conductor that supplies the circuit that is likely to energize is all that is required.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #10  
Old 1/14/12, 3:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Bonding of plumbing

Bonding connection confirmed....
Attached Thumbnails
bonding-plumbing-20120114_04.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 1/14/12, 4:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Bonding of plumbing

Jeff, why would they install that bonding ground at the exterior like that in lieu of the interior so aesthetically, that spigot would look a little better.?
Reply With Quote
  #12  
Old 1/14/12, 6:17 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,567
Default Re: Bonding of plumbing

it's California Marcel...they are a little different over there.......just sayin...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #13  
Old 1/14/12, 6:22 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Bonding of plumbing

Different is right Jim.
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/14/12, 7:17 PM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: Bonding of plumbing

Done the same way here in AZ too Marcel, but our brains are baked in the summer.



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #15  
Old 1/14/12, 7:33 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Bonding of plumbing

Hi Jeff, hope all is good down in Arizona. I am sure it is better than the 8 degrees up here right now.

Yup, up here the bonding is made at the water meter in the basement.
Then of course we got the frostless spicots on the outside instead of those old boiler drains or toggle bibbs.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
A few useful posts - I forget from whom jmichalski Plumbing Inspections 12 3/30/06 9:06 PM


All times are GMT -4. The time now is 5:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts