Should I report an incorrect bonding screw? I found a new upgraded panel with what looks like a sheet metal screw used as the bonding screw. The green bonding screw with tag was laying in the bottom of the panel. Ken
|
|
#2
|
||||
|
||||
|
In this case, a bond is properly installed. Even if an improper screw was utilized, the bond is still going to be effective. IMO...I wouldn't call it out.
|
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
From a code standpoint that is quite illegal and NOT acceptable.
|
|
#4
|
||||
|
||||
|
Quote:
I had no idea that a green screw is so different from a regular screw. |
|
#5
|
||||
|
||||
|
1. per NEC - "Sheet metal screws shall not be used to connect grounding conductors to enclosures. "
and 2. Manufacturer's supplied screw(or similar) might be the only ones used during testing. So read the card attached to the green screw, sine MI could be violated. L&L issue. tom PS, now if it's a drywall screw, that might be ok per #1. However still a L&L issue. |
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
||||
|
||||
|
Quote:
|
|
#8
|
||||
|
||||
|
Quote:
|
|
#9
|
||||
|
||||
|
Quote:
BTW, I still do electrical work, for free, and carry a green sharpie too. |
|
#10
|
||||
|
||||
|
Quote:
![]()
|
|
#11
|
||||
|
||||
|
Quote:
I guess, I have to agree with David on this one, some things just don't seem to make any common sense, even though it is code. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#12
|
||||
|
||||
|
Quote:
![]() It's a patented (by the manufacturer - me) two in one screw. Use it in the panel as a bonding screw (after using the green sharpie on the head of it) and then go on the opposite side of the wall and you've got yourself a handy dandy coat hanger. |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I believe that Home Inspector's should rely on the comments made by those here with many years of experience and listen to them. THE SHEET METAL SCREW IS A VIOLATION! |
|
#14
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
David:
What size in AWG is this screw? What if the service entrance conductors were 3/0 AWG copper, would it be large enough? What is the purpose of the MBJ? |
|
#15
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Neutral bus bar failed inspection | Greg Moritz | Electrical | 18 | 1/19/08 2:53 PM |
| Subpanel Bonding Screw | away | Electrical | 24 | 1/9/08 3:46 PM |
| Demystify Grounding & Bonding Class | pabernathy | Education | 5 | 12/24/06 2:10 AM |
| Is the there a 'bonding' screw that I don't see. | mgault | Electrical | 9 | 10/13/06 11:31 AM |