Should I report an incorrect bonding screw? I found a new upgraded panel with what looks like a sheet metal screw used as the bonding screw. The green bonding screw with tag was laying in the bottom of the panel. Ken
Reply With Quote
  #2  
Old 4/6/08, 2:12 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

In this case, a bond is properly installed. Even if an improper screw was utilized, the bond is still going to be effective. IMO...I wouldn't call it out.
Reply With Quote
  #3  
Old 4/6/08, 2:43 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Screw

From a code standpoint that is quite illegal and NOT acceptable.
Reply With Quote
  #4  
Old 4/6/08, 3:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by Speedy Petey
From a code standpoint that is quite illegal and NOT acceptable.
Would you please expand.

I had no idea that a green screw is so different from a regular screw.
Reply With Quote
  #5  
Old 4/6/08, 3:13 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Bonding Screw

1. per NEC - "Sheet metal screws shall not be used to connect grounding conductors to enclosures. "

and

2. Manufacturer's supplied screw(or similar) might be the only ones used during testing. So read the card attached to the green screw, sine MI could be violated. L&L issue.

tom

PS, now if it's a drywall screw, that might be ok per #1. However still a L&L issue.
Reply With Quote
  #6  
Old 4/6/08, 3:14 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by tdietrich1
per NEC - "Sheet metal screws shall not be used to connect grounding conductors to enclosures. "

and

Manufacturer's supplied screw(or similar) might be the only ones used during testing. So read the card attached to the green screw, sine MI could be violated. L&L issue.

tom
So what sort of material is the manufacturers bonding screw?
Reply With Quote
  #7  
Old 4/6/08, 3:15 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Bonding Screw

Quote:
Originally Posted by dvalley
So what sort of material is the manufacturers bonding screw?
Identified and tested materal.

Reply With Quote
  #8  
Old 4/6/08, 3:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by tdietrich1
Identified and tested materal.

Gee, that helps...Thanks
Reply With Quote
  #9  
Old 4/6/08, 3:18 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Bonding Screw

Quote:
Originally Posted by dvalley
Gee, that helps...Thanks

BTW, I still do electrical work, for free, and carry a green sharpie too.

Reply With Quote
  #10  
Old 4/6/08, 3:20 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by tdietrich1
BTW, I still do electrical work, for free, and carry a green sharpie too.

A green sharpie will definitely work on my inspections.
Reply With Quote
  #11  
Old 4/6/08, 3:22 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,371
Default Re: Bonding Screw

Quote:
Originally Posted by dvalley
Gee, that helps...Thanks


I guess, I have to agree with David on this one, some things just don't seem to make any common sense, even though it is code.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #12  
Old 4/6/08, 3:28 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by mcyr


I guess, I have to agree with David on this one, some things just don't seem to make any common sense, even though it is code.

Marcel
Will this work?


It's a patented (by the manufacturer - me) two in one screw.

Use it in the panel as a bonding screw (after using the green sharpie on the head of it) and then go on the opposite side of the wall and you've got yourself a handy dandy coat hanger.
Reply With Quote
  #13  
Old 4/6/08, 3:31 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Screw

Quote:
Originally Posted by mcyr


I guess, I have to agree with David on this one, some things just don't seem to make any common sense, even though it is code.

Marcel
The requirement for the a green MBJ screw goes back to the early 90"s when an Inspector from Portland, OR sent in a proposal, because the existing panelboard neutral bars then had a screw but it was silver like the others, so with that we got the GREEN screws, the sheet metal screw business started during a change made in a later code because the proposal indicated that it was unreliable.

I believe that Home Inspector's should rely on the comments made by those here with many years of experience and listen to them.

THE SHEET METAL SCREW IS A VIOLATION!
Reply With Quote
  #14  
Old 4/6/08, 3:34 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding Screw

David:

What size in AWG is this screw?

What if the service entrance conductors were 3/0 AWG copper, would it be large enough? What is the purpose of the MBJ?
Reply With Quote
  #15  
Old 4/6/08, 3:35 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Bonding Screw

Quote:
Originally Posted by jtedesco1
The requirement for the a green MBJ screw goes back to the early 90"s when an Inspector from Portland, OR sent in a proposal, because the existing panelboard neutral bars then had a screw but it was silver like the others, so with that we got the GREEN screws, the sheet metal screw business started during a change made in a later code because the proposal indicated that it was unreliable.

I believe that Home Inspector's should rely on the comments made by those here with many years of experience and listen to them.

THE SHEET METAL SCREW IS A VIOLATION!
Thank you Joe, but what is this green bonding screw made out of?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Neutral bus bar failed inspection Greg Moritz Electrical 18 1/19/08 2:53 PM
Subpanel Bonding Screw away Electrical 24 1/9/08 3:46 PM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM
Is the there a 'bonding' screw that I don't see. mgault Electrical 9 10/13/06 11:31 AM


All times are GMT -4. The time now is 9:06 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts