Default Bonding of Service Panel

Hey Guys-

This home had an overhead service to the meter then directly into the home via the attic to the service panel. No service disconnect on the exterior. Since this is the panel with the main disconnect, shouldn't the neutral and ground bus bars be bonded?

The meter had a grounding electrode and it appears that they ran a grounding conductor off the ground bus bar below somewhere...possibly to the copper water lines in the crawlspace, but I was not able to locate it.

Thoughts?

Thanks...Kenny.
Attached Thumbnails
bonding-service-panel-img_3932.jpg   bonding-service-panel-img_3933.jpg   bonding-service-panel-img_3934.jpg   bonding-service-panel-img_3935.jpg   bonding-service-panel-img_3936.jpg  




Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/3/10, 10:03 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

You appear to have a couple of issues. The lack of the bond screw, improper fitting used to connect NM cables to the panel and the length of unfused cable inside the attic.

Unfused SE conductors are required to be "as short as practical". From the description it does not sound like this install would meet that requirement. If the unfused conductors cannot meet the above then a disconnect is installed to provide overcurrent protection and then the cable length does not matter. However, this would now require a 4 wire feeder from the disconnect to the panel where the grounds would be isolated from the neutrals.
Reply With Quote
  #3  
Old 3/3/10, 10:10 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Bonding of Service Panel

Kenny,

What is the BRAND name of this panel?



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #4  
Old 3/3/10, 10:33 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Bonding of Service Panel

Quote:
Originally Posted by bhartley View Post
Kenny,

What is the BRAND name of this panel?
Buck, it's a Square D.
Attached Thumbnails
bonding-service-panel-img_3931.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #5  
Old 3/3/10, 11:05 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

This this is the QO Square D line.
Reply With Quote
  #6  
Old 3/3/10, 3:48 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Bonding of Service Panel

Kenny,

The only reason I ask about the BRAND is that I only saw Square D breakers in lower part of the panel. Thought maybee it was a different panel. Refer the panel to a qualified electrician, when in doubt



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #7  
Old 3/3/10, 5:08 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Bonding of Service Panel

Quote:
Originally Posted by Jim Port View Post
You appear to have a couple of issues. The lack of the bond screw, improper fitting used to connect NM cables to the panel and the length of unfused cable inside the attic.

Unfused SE conductors are required to be "as short as practical". From the description it does not sound like this install would meet that requirement. If the unfused conductors cannot meet the above then a disconnect is installed to provide overcurrent protection and then the cable length does not matter. However, this would now require a 4 wire feeder from the disconnect to the panel where the grounds would be isolated from the neutrals.
Thanks Jim. What problem does the lack of a bonding screw create in this situation...for my educational purposes. In reference to the SE conductor, what does unfused refer to?

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #8  
Old 3/3/10, 6:21 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

Unfused cable is without any overcurrent protection installed. An example would be between the meter and the panel. Once overcurrent protection is installed the length of cable inside is not regulated by the NEC. Overcurrent protection can be a breakered disconnect either immediately inside or on the outside of the house.

Without the bond screw a live conductor could short to the enclosure without tripping the breaker as there would be no fault path. This could also create a shock hazard to anyone that touched the panel.
Reply With Quote
  #9  
Old 3/3/10, 6:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Bonding of Service Panel

There appears to be a bond screw immediately below the neutral of the SE.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #10  
Old 3/3/10, 6:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

There are several issues with the service raceway. For one, judging from the photo and depending on the jurisdiction, it may be too long to be inside of the dwelling. [230.70(A)(1)] The service raceway must be bonded on one end with something other than standard lockmuts, since we can't see into the meter neclosure it may or may not be propoerly bonded. Even though there may be no bonding jumper within the panel from the neutral to the cabinet, the cabinet would be bonded by virtue of it's connection to the service raceway.
Reply With Quote
  #11  
Old 3/3/10, 7:04 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

Quote:
Originally Posted by mlarson View Post
There appears to be a bond screw immediately below the neutral of the SE.
Going to differ with you Michael,

I think that is a screw to hold the neutral bar to the bracket. Also the Square D bond screws are a green color.
Reply With Quote
  #12  
Old 3/3/10, 7:10 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding of Service Panel

Quote:
Originally Posted by Jim Port View Post
Once overcurrent protection is installed the length of cable inside is not regulated by the NEC. Overcurrent protection can be a breakered disconnect either immediately inside or on the outside of the house
Please explain.....You lost me on that one. Are you saying the cable between the meter and the panel OCPD is not regulated by the NEC....or the cable inside on the load side of the OCPD is not regulated by the NEC. Im confused because both are regulated by the NEC.

Please clarify fella......



Paul W. Abernathy
Reply With Quote
  #13  
Old 3/3/10, 7:12 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding of Service Panel

I agree with Jim....their is no bonding screw in this panel. It would usually be upper right and it would indeed be green.



Paul W. Abernathy
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/3/10, 7:15 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

I do not think that panel is feed with a raceway; the neutral is braided like SE cable, not insulated, and that looks like a PVC terminal adapter in the panel.

I don't see how anyone can make a determination on the length of the SE conductors based on those pics.
Reply With Quote
  #15  
Old 3/3/10, 7:16 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding of Service Panel

Quote:
Originally Posted by Robert Meier View Post
There are several issues with the service raceway. For one, judging from the photo and depending on the jurisdiction, it may be too long to be inside of the dwelling. [230.70(A)(1)] The service raceway must be bonded on one end with something other than standard lockmuts, since we can't see into the meter neclosure it may or may not be propoerly bonded. Even though there may be no bonding jumper within the panel from the neutral to the cabinet, the cabinet would be bonded by virtue of it's connection to the service raceway.
Robert, are you using 250.97 regarding the raceway bond? If not what Article are you using?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Panel ground bonding wolejarski Electrical Inspections 2 5/23/08 12:13 AM
Service panel full of paper tags gwilcox Electrical Inspections 5 8/17/07 6:55 AM
Zinsco Service Disconnect Panel pdickerson Electrical Inspections 7 9/16/06 11:59 AM
Service Panel Used As Junction Box mbazzo Electrical Inspections 20 8/12/06 12:09 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts