I inspected a house with a subpanel. The feeds from the main panel come off of a double pole 60amp breaker. I did not find a bond in the main panel, but the subpanel is bonded. I know the sub panel should not be bonded if the main panel is bonded, but since the main is not bonded, is this configuration OK?
Michael Merino Merino's Home Inspection & Education Inc. "Not just an Inspection, an Education"SM Phone/Fax 708~535~6057
|
| Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Quote:
The sub panel must be bonded to the service panel. The equipment grounding conductors (egc's) must be bonded to (and at) each panel. The neutrals must be bonded to (and at) the service panel. The neutrals must not be grounded at, nor bonded to the sub panel. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
The sub panel must be bonded to the service panel. It appears to be bonded with conduit from main panel to the sub panel
The equipment grounding conductors (egc's) must be bonded to (and at) each panel. This is present in both panels. The neutrals must be bonded to (and at) the service panel. NOPE-did not see it present. The neutrals must not be grounded at, nor bonded to the sub panel. YES, as seen in the picture, the green screw. Maybe I should have said bonding screw or strap. Michael Merino Merino's Home Inspection & Education Inc. "Not just an Inspection, an Education"SM Phone/Fax 708~535~6057
|
|
#4
|
||||
|
||||
|
The sub panel wiring is improper. The bonding screw needs to be removed, and the egc's should be removed from the neutral bus, and attached to the (empty) grounding bus, which is bonded to the enclosure as required.
There must be a bonding screw/strap/conductor at the service equipment that bonds both the egc's and the neutrals to the service panel enclosure. The bonding between panels (via conduit) is acceptable, depending on the code-cycle your area follows. The panels have obviously been installed and/or modified by "less than a professional." The service panel is also being used as a raceway, which can be indicative of non-professional workmanship. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Thanks, Jeff. As always, you have the answers!! The question answer format was very helpful.
Michael Merino Merino's Home Inspection & Education Inc. "Not just an Inspection, an Education"SM Phone/Fax 708~535~6057
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical | 44 | 4/18/08 12:43 AM |
| Neutral bus bar failed inspection | Greg Moritz | Electrical | 18 | 1/19/08 2:53 PM |
| Panel Inspection Safety | roconnor | Electrical | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |