Default Bonding sub panel

I inspected a house with a subpanel. The feeds from the main panel come off of a double pole 60amp breaker. I did not find a bond in the main panel, but the subpanel is bonded. I know the sub panel should not be bonded if the main panel is bonded, but since the main is not bonded, is this configuration OK?
Attached Thumbnails
bonding-sub-panel-pa300027.jpg   bonding-sub-panel-pa300023.jpg  



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #2  
Old 10/30/09, 11:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Bonding sub panel

Quote:
Originally Posted by mmerino View Post
I know the sub panel should not be bonded if the main panel is bonded, but since the main is not bonded, is this configuration OK?
Bonded to what?

The sub panel must be bonded to the service panel.

The equipment grounding conductors (egc's) must be bonded to (and at) each panel.

The neutrals must be bonded to (and at) the service panel.

The neutrals must not be grounded at, nor bonded to the sub panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 10/30/09, 11:39 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 619
Default Re: Bonding sub panel

The sub panel must be bonded to the service panel. It appears to be bonded with conduit from main panel to the sub panel

The equipment grounding conductors (egc's) must be bonded to (and at) each panel. This is present in both panels.

The neutrals must be bonded to (and at) the service panel. NOPE-did not see it present.

The neutrals must not be grounded at, nor bonded to the sub panel. YES, as seen in the picture, the green screw. Maybe I should have said bonding screw or strap.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 10/30/09, 11:47 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Bonding sub panel

The sub panel wiring is improper. The bonding screw needs to be removed, and the egc's should be removed from the neutral bus, and attached to the (empty) grounding bus, which is bonded to the enclosure as required.

There must be a bonding screw/strap/conductor at the service equipment that bonds both the egc's and the neutrals to the service panel enclosure.

The bonding between panels (via conduit) is acceptable, depending on the code-cycle your area follows.

The panels have obviously been installed and/or modified by "less than a professional." The service panel is also being used as a raceway, which can be indicative of non-professional workmanship.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 10/31/09, 12:17 AM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 619
Default Re: Bonding sub panel

Thanks, Jeff. As always, you have the answers!! The question answer format was very helpful.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Neutral bus bar failed inspection Greg Moritz Electrical 18 1/19/08 2:53 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:40 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts