Here's an academic question. I know there are better ways (GFCI, etc) but is a bootleg ground safer than no ground at all. Why, why not.
|
|
#2
|
|||
|
|||
|
The grounded conductor is a current carrying conductor. If you connect the grounding conductor to it, it can energize anything that is or can be connected to the grounding conductor.
|
|
#3
|
|||
|
|||
|
Quote:
|
|
#4
|
|||
|
|||
|
Please Note:
tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#5
|
|||
|
|||
|
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bad "trick".
It can really trick you into killing yourself. Think about this. What happens when you have a polarity reversal up stream and someone hooks up a bootleg ground? You hooked the white to the ground, polarity is reversed, what voltage did you just put on the case of that fridge? Hope you don't touch the stove or sink while you have the fridge handle in your hand. That bad part is your 3 light tester will say everything is fine. |
|
#7
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Life is to short do it once and do it right. Roy Cooke sr |
|
#8
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
I thought a bootleg ground was an added grounding conductor rather than a grounded conductor.
Or gounding the receptacle to a metal box, isn't that a bootleg ground? What about adding a third grounding conductor that runs back to a grounding bus bar? That's actually a true ground isn't it? |
|
#10
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
If your electrical panel is grounded to plumbing, then couldn't you attatch a separate ground wire from an outlet straight to the plumbing.
Would this not give the same affect? Legal? Safe? |
|
#11
|
|||
|
|||
|
You are not supposed to ground electrical systems using plumbing. You bond the plumbing so that it does not become energized, but you don't use plumbing as a "ground rod." So, no, you should not run a wire from the ground screw of a receptacle to any copper plumbing piping.
Mike Morgan Central Texas Home Inspections mike@centraltexashomeinspections.com www.centraltexashomeinspections.com |
|
#12
|
||||
|
||||
|
Quote:
Depends on where you live and the jurisdiction. In Chicago that is very common... Cold water pipes are "GEC's"...Yep check with the local jurisdiction. One near by suburb does not use grounding rods!! Paul A. has posted a great "grounding" article . Earth ground around the world and who uses what system.. Read that and then pull your hair out... |
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The idea of using a cold water pipe dates back to the days before plastic pipe when a cold water pipe was soldered copper or threaded steel, all the way back to the main on the street. These days it would be rare to have a solid metal pipe without some kind of water filter, softener or simply a section of plastic pipe. It is just not a relaible ground these days.
|
|
#14
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
As long as your jurisdiction says it's ok to ground the panel the same.? |
|
#15
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I think you know just about enough about electricity to get into trouble. You should hire an electrician to do the job correctly Roy Cooke Sr |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| False Ground / Bootleg Ground | mmorris | Electrical | 12 | 5/17/07 1:11 PM |
| Ground Wires Inside a Panel | mveitenhans | Electrical | 13 | 10/29/06 12:39 PM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical | 5 | 3/21/06 9:48 AM |